An insulated enclosure won't need one no.
But I'm not a big fan of the OSG! After all it's a guide. And wrong in many places as said on many threads.......
 
Agreed..BUT the OP suggested that he wouldn't test HIS RCBO and rely on an RCD ( One by his own admission he can not identify ) to give additional protection, so he either has to falsify the cert or investigate ? Failure to investigate would make him liable sorry

Totally disagree with that.
Inform the customer of your findings in the cert and it is up to them to decide what action to take.
And why do you have to falsify anything ?
Failure to investigate makes him liable ? total crap ! the property owner is always responsible for his own installlation not the spark.
 
Read the OP ! This isn't a EICR it's a new circuit that he is commissioning ! Yes he is liable if he fails to carry out and document his test results for the circuit HE has supplied, he was suggesting that he was going to neglect the RCBO test results in favour of an upfront RCD, by his own admission he doesn't know the characteristics of so what does he put on the cert ..ermmmm ?
 
Well if hes prevented from carrying out certain tests due to reasons outside of his control and records this in the cert - this is not neglect , its a limitation.
And as for the details of the device that needs to recorded , he'll just have to look for the BS number on the main rcd.
And i read the op clearly , smart arse.
Your understanding of the legal obligations is sadly lacking.
 
Well if hes prevented from carrying out certain tests due to reasons outside of his control and records this in the cert - this is not neglect , its a limitation.
And as for the details of the device that needs to recorded , he'll just have to look for the BS number on the main rcd.
And i read the op clearly , smart arse.
Your understanding of the legal obligations is sadly lacking.

There's no need to make childish comments, just because someone doesn't agree with your view,that's point one, point two is, you claim to have read the OP in which he states... no markings on front of RCD but assume must be 30mA non time delay.and then you say " he'll just have to look for the BS number on the main rcd."

Well he can't find it ? so what does he put in the box asking for the BSEN number ?

Keep it civil



 
The way I see it it's simple - If it's an insulated enclosure he don't need an upfront RCD as long as all circuits are protected by RCBO's - This would comply with the requirments of a TT installation and give total discrimination.
Just get rid of the upfront RCD and replace with a main switch.

The only caveat that I would add is (just thought of) - if someone later came along and changed an RCBO for an MCB or added another circuit with one, it would then not comply with TT requirements

So perhaps back to the upfront time delayed RCD as well as RCBO's. They are the only options if you want total discrimination.
 
OK - Now have more time and just read OP properly. As it's 3 phase and TT, it ought to have an up front RCD - and because discrimination is an important consideration. 531.2.4. (selection of to prevent unnecessary tripping) it must be an S type when combined with downstream RCD's.

It would also come under 531.2.9. (where discrimination is necessary to prevent danger when two or more RCD's are in series). Which I read as downstream RCD's/RCBO's must be fitted. Obviously RCBO's would be costly but would be the ultimate solution with discrimination. Which is what the customer wanted.

I don't think cost considerations come into it when the Regs state clearly what is needed for compliance in this case.
 
Terminator please quote the reg that tells us we have to have an upfront RCD if all circuits have 30mA protection, I'm not saying your wrong but I can't find that reg.
ATB J
 
I would agree that an upfront time delayed RCD, unless the tails are mechanically protected, would be required for TT.

However, I had occasion to test a TT installation where a non-delayed 'G' 100mA and 30mA RCD were connected in series.

I ramp tested the 100mA RCD to establish minimum tripping current and then applied the normal auto tests to the 30mA RCD. At 1/2 and 1 IAN you will get results for the 30mA and on 5 IAN will get a result but will loose both RCDs.

I compared the results for the 100mA and 30mA RCDs at 5 IAN and found the results to differ..... So a certain amount of discrimination will be available for excessive leakage currents
 
There's no need to make childish comments, just because someone doesn't agree with your view,that's point one, point two is, you claim to have read the OP in which he states... no markings on front of RCD but assume must be 30mA non time delay.and then you say " he'll just have to look for the BS number on the main rcd."

Well he can't find it ? so what does he put in the box asking for the BSEN number ?

Keep it civil



point 1 - you were being a smart arse with the whole " errmmmm?" and "read the op" comments - dont dish it out if you cant take it.
point 2 - it bothers me not if others have a different opinion to mine.
point 3 - He writes BS 61008 on the cert or anything else he feels is suitable.
But what BS number he writes has not been an issue in this thread until you just brought it up ?
I thought the issue was being unable to complete the rcd tests due to an inappropriate main switch device that he never installed in the first place , which you suggested that he should take responsibilty for ????

Quote " failure to investigate would make him liable"
Again , no it wouldnt.
 
Read the OP ! This isn't a EICR it's a new circuit that he is commissioning ! Yes he is liable if he fails to carry out and document his test results for the circuit HE has supplied, he was suggesting that he was going to neglect the RCBO test results in favour of an upfront RCD, by his own admission he doesn't know the characteristics of so what does he put on the cert ..ermmmm ?

Think I summed up what he shoudl do in post 5:
'Just fudge the cert, cheat, lie, else like plenty of other sparks don't send them the certificate.'
 
So do you think the last electrician that worked on the board wouldn't be investigated and his results and analysed ?, and if it came to light he hadn't carried out the mandatory tests on HIS new circuit you think he wouldn't be (Accused of ) being liable if someone got a belt..Your dreaming.
 
What investigation ????
Whos investigating ??? where are you getting this from lol ??
Mandatory tests ?? mandatory as in law ?? which law ???
The tests he couldnt complete would be recorded with the reasons on the cert , everything above board , no lies.
Please stop digging this hole youre in.
 
What the hell does it matter which RCD trips for the purpose of the cert?....If there is a requirement for RCD protection on the circuit installed and a test operates at least one within the required time jobs a goodun innit?....Whats all this nonsense about falsifying certs and legal action?????????........confused.
 
I would just make a note of what you found, advise customer and leave it at that, however for these purpose I have a plug lead to test rcbo's whilst they asre out of the board, especially useful in off peak installs.
 
What the hell does it matter which RCD trips for the purpose of the cert?....If there is a requirement for RCD protection on the circuit installed and a test operates at least one within the required time jobs a goodun innit?....Whats all this nonsense about falsifying certs and legal action?????????........confused.

Exactly WP!, it is the disconnection time that counts, the only non compliance is that the up-front RCD trips first which should be noted on the cert.
 
Hole ? no hole here sunshine, I believe what I said is true, and I will stick to it, if you have a different opinion that's your entitlement, I can respect others opinions without agreeing with them.
J
 
As you are totally relying on a RCD device for your earth fault protection on a TT system, it makes perfect sense to have an up-front 100mA S type RCD as your ''Additional'' means of protecting against faulty down stream RCD(s). Far better to have a decent back-up, when your TT system is an unstable 200 ohm Ra set-up using a twig as the earth electrode!!... lol!!
 
Terminator please quote the reg that tells us we have to have an upfront RCD if all circuits have 30mA protection, I'm not saying your wrong but I can't find that reg.
ATB J

Jimmy - I said 'ought to have' because you can never be sure that someone may come along and change or add a circuit just using an MCB - and if the main earthing resistance had deteriorated (TT is notoriously unreliable) you would lose your disconnection times. It does say in the BGB "the preferred protective device is an RCD" 411.5.2. Then Note 1 says "where discrimination between RCDs is necessary refer to Reg 531.2.9. That is about compliance with the Regs for fault protection using two or more RCD,s in series and that discrimination in their operation is necessary to prevent danger.

In this case I think you need an upfront S type RCD to meet disconnection times and downstream RCBO,s to ensure disrimination and to prevent danger by the whole installation being knocked out.
 
Last edited:
Jimmy - I said 'ought to have' because you can never be sure that someone may come along and change or add a circuit just using an MCB - and if the main earthing resistance had deteriorated (TT is notoriously unreliable) you would lose your disconnection times. It does say in the BGB "the preferred protective device is an RCD" 411.5.2. Then Note 1 says "where discrimination between RCDs is necessary refer to Reg 531.2.9. That is about compiance with the Regs for fault protection using two or more RCD,s in series and that discrimination in their operation is necessary to prevent danger.

In this case I think you need an upfront RCD to meet disconnection times and downstream RCBO,s to prevent danger by the whole installation being knocked out.

Not sure if i've read this right, ....but an up-front S type RCD won't meet TT disconnection times, (delayed trip time) it's there solely as additional protection to any RCD device that fails, for one reason or another to operate, (they are not the most reliable of protective devices). At the very least, it will trip out a faulty circuit, even if it is slightly outside of the set times of a TT system...
 
Yes, agreed Engineer - A touch of dyslexia - I meant the other way round, RCBO's to meet disconnection and and upfront for backup and discrimination, as you have pointed out. Been a long day.
 
I don't disagree with extra protection I was just curious to see if it was an interpretation of the regs or a reg
Eng 54 could you explain to me how you interpret the regs on protecting tails in to an enclosure on a TT ? if the 100mA RCD is in the board, and not external to it how does/can it protect the tails that are from DNO fuse to incomer on RCD ? Not a trick question just a genuine enquiry fella.

ATB J
 
I don't disagree with extra protection I was just curious to see if it was an interpretation of the regs or a reg
Eng 54 could you explain to me how you interpret the regs on protecting tails in to an enclosure on a TT ? if the 100mA RCD is in the board, and not external to it how does/can it protect the tails that are from DNO fuse to incomer on RCD ? Not a trick question just a genuine enquiry fella.

ATB J

My interpretation of this situation is that the enclosure itself cannot be metallic due to no rcd upstream of the CU main switch - ie. being fully insulated provides that extra level of protection for TT wiring prior to the rcd.
If you get my drift lol.
 

Reply to Can't test RCBO as main RCD trips first - what to do? in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

Similar Threads

Regarding the EV, it’s an Ohme charger which I believe has a type A RCD built in, setup would be: 50A RCBO to feed garage db Garage db has no...
Replies
17
Views
529
Sort of; technically speaking the 10mA is required to hit the 40mS target at 50-149mA, whereas the 30mA device can be happily snoozing along for...
Replies
8
Views
705
  • Question
Assumption is the mother of all major foul-ups! Start with the basics, like IR testing, RCD testing on its own, and checking the leakage as...
Replies
7
Views
637
As per above from Dave. Swap to a 63A outlet and problem goes away. What gets plugged into it is not part of an inspection.
Replies
20
Views
2K
In my opinion replacing the consumer unit and waiting to see which RCBO trips is not a good fault finding technique. If the lighting circuit...
Replies
8
Views
447
davesparks
D

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock    No Thanks