Terminator please quote the reg that tells us we have to have an upfront RCD if all circuits have 30mA protection, I'm not saying your wrong but I can't find that reg.
ATB J
Jimmy - I said 'ought to have' because you can never be sure that someone may come along and change or add a circuit just using an MCB - and if the main earthing resistance had deteriorated (TT is notoriously unreliable) you would lose your disconnection times. It does say in the BGB "the preferred protective device is an RCD" 411.5.2. Then Note 1 says "where discrimination between RCDs is necessary refer to Reg 531.2.9. That is about compliance with the Regs for fault protection using two or more RCD,s in series and that discrimination in their operation is necessary to prevent danger.
In this case I think you need an upfront S type RCD to meet disconnection times and downstream RCBO,s to ensure disrimination and to prevent danger by the whole installation being knocked out.