K

Kev2632

I was at a job today where there was a central heating comprising of 3port valve, what i couldn't understand was why is there HW off connection to be used in the programmer and also a third connection to be used on the tank stat, also this system also wanted a 2port valve incorporated into the HW pipe feading the coil to the tank ?? Why is that all? Could anybody help me understand this?
 
The 3 port valve doesn't have the spring that a two port valve has. It has an extra connection to 'bring back' back the valve. A two port valve springs back when there is no power supplied.

The cylinder stat has 'call' and 'satisfied' terminals. I.e. normally open and normally closed. This is to operate the 'bring back' the valve when satisfied for heat.

The extra two port is unusual but if its on the pipe going to the coil, then all it will do is shut the water feed off when satisfied. Are you sure that the three port does HW and CH and not two CH zones?
 
The 3 port valve doesn't have the spring that a two port valve has. It has an extra connection to 'bring back' back the valve. A two port valve springs back when there is no power supplied.

The cylinder stat has 'call' and 'satisfied' terminals. I.e. normally open and normally closed. This is to operate the 'bring back' the valve when satisfied for heat.

The extra two port is unusual but if its on the pipe going to the coil, then all it will do is shut the water feed off when satisfied. Are you sure that the three port does HW and CH and not two CH zones?
Thanks for your reply, yea it does the HW and CH and the two port valve was fitted for the feed going into the coil as well? Pretty weird to be honest
 
If it's an unvented cylinder, mains water fed no storage tank (with expansion vessel and Temperature and pressure relief valve) it must have a 2 port valve connected via the Over temperature stat on the cylinder.
The valve comes with the kit supplied by the cylinder manufacturer.
 
If it's an unvented cylinder, mains water fed no storage tank (with expansion vessel and Temperature and pressure relief valve) it must have a 2 port valve connected via the Over temperature stat on the cylinder.
The valve comes with the kit supplied by the cylinder manufacturer.
Yea that's the exact it!! And why is thus 2port valve need exactly???
 
If it's an unvented cylinder, mains water fed no storage tank (with expansion vessel and Temperature and pressure relief valve) it must have a 2 port valve connected via the Over temperature stat on the cylinder.
The valve comes with the kit supplied by the cylinder manufacturer.

What's the idea behind this then. What does it do?
 
What's the idea behind this then. What does it do?

Cuts the heat source off to the cylinder from the boiler under control of the over temperature stat on the cylinder.

If the normal Hot water zone valve failed and the unvented cylinder continued to heat up, it could potentially become a bomb ready to discharge steam when it explodes.

The 2 port valve is part of a package of safety features, associated with unvented cylinders, designed to prevent this.
 
The main reason the additional valve is there is to prevent the hot water from ever going above 100'c. The cylinder stat is the first line of defence followed by the over heat stat which would operate at 85c & would cut of the supply of hot water to the cylinder, hence the extra valve. If the temperature were to go above 90c the temperature & pressure relief valve would start to open & let in more cold water to keep it from going above 100c As the pressure rises in the cylinder so does the temperature as it is above atmospheric pressure. A pressure of 1bar inside the cylinder would result in a temperature of 122c. As the pressure goes up so does the temperature Unless one of these unvented cylinders has not been installed correctly it would vertually be impossible for one of these to explode as there are so many safety features it would have to overcome for that to ever happen. Most modern boilers have overheat devices as well
 
Found a good few of these set ad-hoc or addition of solid fuel input and the big risk is at overheat temperature ANY burst or even leak vents pressure and entire contents above 100c flashes to steam at 1600 times volume,can level like a gas explosion. Vented systems much easier to remain tame...
 

Reply to Central heating 3port valve? in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Sticky
  • Article
Wicked I've just actually looked through it and it's very smart. Some good stuff in it. There's a tile association company that do a magazine...
Replies
2
Views
283
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
273
  • Article
Hi everyone, Another weekend, another sale! Get ready for colder days with Haverland Radiators, combining efficiency with modern design. Keep...
Replies
0
Views
351

Similar threads

glad it was such a simple fix..... And good job the previous owners didnt take it with them
Replies
6
Views
638
I
  • Article
Baxi system boiler and Opentherm Hello Does anyone know if its possible to connect an Opentherm thermostat such as a Nest to a Baxi 800 System...
Replies
0
Views
232
Ian777
I

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top