i=p/u

-
Arms
Joined
Dec 9, 2010
Messages
7,520
Reaction score
800
Location
Northern Ireland
A guy asked me to install supply to 3 ph oven, as its few miles away I looked at same kind in another of shops , and it was installed on 32A breaker on 6mm. Anyway I got the rating plate sent to me by photo and I working out 2.5mm on 16A 3ph breaker, am I missing something... I could be but doubt it.
 