I've seen single circuit UFH's with a separate supply for the pump from a fused spur and the pump works off a stat (in the manifold), like midwest is describing and the valve is just used to isolate that circuit, (stop flow).
If there is more than one loop, it needs more control over the pump. That's when you normally see the wiring centres, as I remember.
Unfortunately as this is a stand alone single circuit and the previous sparks didn't put in a dedicated wiring centre which I would normally use which has the ability to setup multiple pumps, I think I need either a different wiring centre or to put in a relay to stop the second pump back feeding the HW/CH pump, however I keep looking at the wiring diagram and can't work out where the back feed is coming from, got them pulling the wireless receiver tonight to see if that solves it!:-( I wouldn't mind but he is plumber by trade, he should be able to do his own wiring!:)

Does the manifold have a stat built in for the pump ?
 
The bodge way is to connect the UFH pump to the brown of the UFH 2 port valve and call for heat from the UFH thermostat. The ideal way is to connect the UFH pump to the coil of a relay along with the orange of the UFH 2 port valve.
 
I've seen single circuit UFH's with a separate supply for the pump from a fused spur and the pump works off a stat (in the manifold), like midwest is describing and the valve is just used to isolate that circuit, (stop flow).
If there is more than one loop, it needs more control over the pump. That's when you normally see the wiring centres, as I remember.


Does the manifold have a stat built in for the pump ?
The manifold doesn't have a stat built in, it is acting like a heating circuit, one zone valve, wireless thermostat/timer.
 
The bodge way is to connect the UFH pump to the brown of the UFH 2 port valve and call for heat from the UFH thermostat. The ideal way is to connect the UFH pump to the coil of a relay along with the orange of the UFH 2 port valve.
I have taken the bodge approach, will
Go back, check wiring and put in a relay! Thanks.
 

Reply to Circulation pump permanently on in the Central Heating Systems area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
275
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
773
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
779

Similar threads

glad it was such a simple fix..... And good job the previous owners didnt take it with them
Replies
6
Views
706
As per Davesparks, it would be helpful to see a picture of the valve etc. If the manifold valve referred to is a common or garden motorised...
Replies
8
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top