Client refusing spd | Page 2 | on ElectriciansForums

Discuss Client refusing spd in the UK Electrical Forum area at ElectriciansForums.net

Joined
May 3, 2018
Messages
32
Reaction score
6
Location
Leicester
Got a customer refusing to pay additional for an spd, its in luton which i believe is known for lightning strikes .
Customer just wants me to install new standard bg board.
Normally, i wouldn't make a fuss, but because its in a lightning zone, im thinking if its mandatory. Or could i put it down as a departure.
 
Surely the cost of the protection is only about ÂŁ70 or under now, a lightning strike can destroy the consumer unit for a start let alone TV, smart phone, computer etc etc. How can you say the cost of protection outweighs the cost of impact?

The way I get round it when a customer asks what an SPD is and do I need it I give them two options...

1. You can pay the ÂŁ70 for the SPD which experts have decided is worth the protection and you can have some piece of mind that you have at least some protection from lightening strikes.

2. I can do a very complicated risk assessment that will often still dictate you need the SPD, to carry out this risk assessment I charge ÂŁ90.

Would you like choice 1 or choice 2?

Any customer who would moan that much about fitting an SPD frankly I dont want as a customer, go find some cowboy to do your electrics.
ÂŁ70 may be nothing to you, but to many it is a significant amount of money, often more than a day's wages. In the vast majority of cases, an SPD is insurance against something that is highly unlikely to happen.

Tradespersons who force their clients to buy unnecessary components because they don't know the regulations could themselves be perceived as cowboys.
 
I include the SPD in the quote and give the client the option to remove it, mainly they keep it in

I also do NOT do a calculation on SPD's as there are too many variables, I just recommend it on every consumer unit change- it is up to the client then

If there is a SPD problem afterwards then the client is liable as they have went against my professional advice
 
ÂŁ70 may be nothing to you, but to many it is a significant amount of money, often more than a day's wages. In the vast majority of cases, an SPD is insurance against something that is highly unlikely to happen.

Tradespersons who force their clients to buy unnecessary components because they don't know the regulations could themselves be perceived as cowboys.
Yeah the difference between a non spd board and an spd board, is literally ÂŁ70-ÂŁ100 difference.
Due to the variables already in the area, i wasn't sure whether its mandatory. I don't want a call saying "i should have fitted an spd" due to xyz, if i customer refuses it, im gonna make sure its a departure and refusal.
Anything that could come back at us, even the tiny possibility, keep our asses covered.
 
Yeah the difference between a non spd board and an spd board, is literally ÂŁ70-ÂŁ100 difference.
Due to the variables already in the area, i wasn't sure whether its mandatory. I don't want a call saying "i should have fitted an spd" due to xyz, if i customer refuses it, im gonna make sure its a departure and refusal.
Anything that could come back at us, even the tiny possibility, keep our asses covered.
What's the departure for? Something else?
 
On your certificate note that it was recommended by you to fit an SPD but the client declined.
 
ÂŁ70 may be nothing to you, but to many it is a significant amount of money, often more than a day's wages. In the vast majority of cases, an SPD is insurance against something that is highly unlikely to happen.

Tradespersons who force their clients to buy unnecessary components because they don't know the regulations could themselves be perceived as cowboys.

Here is what the regs say:

Protection against transient overvoltages shall be provided where the consequence caused by overvoltage could:
  • Result in serious injury to, or loss of, human life, or
  • Result in interruption of public services and/or damage to cultural heritage or
  • Result in interruption of commercial or industrial activity, or
  • Affect a large number of co-located individuals
For all other cases, a risk assessment according to Regulation 443.5 shall be performed in order to determine if protection against transient overvoltages is required.

This is is quite clear that where no protection via an SPD risk assessment must be performed...

My point is to carry out that risk assessment costs time which is money. The only exception being if for a single dwelling where the total value of the installation and equipment does not justify protection. So lets consider what a lightning strike can damage in a best case scenario of a little old ladies house.. The consumer unit, all wiring, all accessories, TV, Microwave, fridge/freezer. So thats a complete rewire, including redecoration, new TV, microwave and fridge/freezer, lets say thats ÂŁ5000 as a cheap estimate..

You are trying to say that a ÂŁ70 SPD is not justified to save ÂŁ5k? The reason that is there is if say you have the incomer in the garage and tails is split into two boards, one for the house one for the garage. The garage has a couple of sockets with nothing plugged in and a light... In that instance then yes you can say the cost of fitting an SPD to the garage is not necessarily justified.

There has been youtube videos where a lady from the IET (cant remember her name but an expert on transient voltages) said for all residential properties the interpretation is that they all need SPD's.

If you are really concerned about cost go fit a BG board with SPD which is currently ÂŁ20 at screwfix, or a fusebox SPD kit which is ÂŁ27. I can understand why we were having this conversation when SPD's were over ÂŁ100 but some are now ÂŁ20... An SPD is generally as necessary as an RCD, if a customer said I dont want to pay for an RCD board would you fit a board with no RCD's?
 
Yeah the difference between a non spd board and an spd board, is literally ÂŁ70-ÂŁ100 difference.
Due to the variables already in the area, i wasn't sure whether its mandatory. I don't want a call saying "i should have fitted an spd" due to xyz, if i customer refuses it, im gonna make sure its a departure and refusal.
Anything that could come back at us, even the tiny possibility, keep our asses covered.

Yep, also tell customers that this may potentially invalidate their insurance in the event of a transient voltage such as a lightning strike causing damage... Usually focuses the mind. If they are concerned about the money that much fit a fusebox board where the SPD is less than ÂŁ30...
 
For all other cases, a risk assessment according to Regulation 443.5 shall be performed in order to determine if protection against transient overvoltages is required.

This is is quite clear that where no protection via an SPD risk assessment must be performed...
If we finish that sentence....
"For all other cases a risk assessment shall be performed etc. If the risk assessment is not performed [you need to install one] except for single dwelling units where the total value of the installation and equipment therein does not justify such protection"
The gives the context for the comments earlier in this thread.

However I do agree with you that I can't think of many houses where spending ÂŁ30 to protect equipment worth thousands isn't justified. My scheme assessor said he wanted either an RA or an SPD, and so they just get fitted as standard now - life's too short!
Much as I don't ask customers what rating RCBO's to fit, I don't ask them if they want an SPD either. They just get one!
 
Here is what the regs say:

Protection against transient overvoltages shall be provided where the consequence caused by overvoltage could:
  • Result in serious injury to, or loss of, human life, or
  • Result in interruption of public services and/or damage to cultural heritage or
  • Result in interruption of commercial or industrial activity, or
  • Affect a large number of co-located individuals
For all other cases, a risk assessment according to Regulation 443.5 shall be performed in order to determine if protection against transient overvoltages is required.

This is is quite clear that where no protection via an SPD risk assessment must be performed...
NO it doesn't!

You stopped reading/copying prior the the part about residential!

Which is different to others, it is very clear the above applies to everything OTHER THAN:

...single dwelling units where the total value of the installation and equipment therein does not justify such protection.

If an end user (residential) says that he does not believe the potential for damage warrants the cost of protection (not that it's less than the cost, just that it doesn't warrant it) then it need not be fitted - this would be completely compliant with the regulations.

It's not a departure!
How would this invalidate insurance? (It is 100% compliant!)

It may be a poor decision, in my/your/our opinion it would be worth fitting but the installation would be correct to the regs.
 
Not this again. Thr calculation is simple.

CRL =fenv/(LpĂ—Ng)
where:

fenv is an environmental factor selected according to Table 443.1
Lp is the risk assessment l
ength in km (see below)

Ng is the lightning ground flash density (flashes per km2
per year) relevant to the location of the power
line and connected structure (see Figure 44.2).

The calculation for Lp is;

LP = 2 Lpal + Lpcl + 0.4 Lpah + 0.2 Lpch

Lpal - Length of LV overhead line in km
Lpcl - Length of LV underground line in km
Lpah - Length of HV overhead line in km
Lpch - Length of HV underground line in km

Thr collective length (Lpal + Lpcl + Lpah + Lpch) is limited to 1km so if you can't calculate then use 1.

So we now have CRL =fenv/(1Ă—Ng)

fenv is an environmental factor selected according to Table 443.1 (85 for countryside, 850 for urban)

CRL =85/(1Ă—Ng)

CRL = 850/(1*Ng)

Ng is the lightning ground flash density (flashes per km2 per year) relevant to the location of the power line and connected structure (see Figure 44.2).

you don't define what you mean by "lightening zone". So we'll use 0.5 and 0.8 respectively.

CRL =85/(1Ă—0.5) = 170
CRL =85/(1Ă—0.8) = 106.25

CRL = 850/(1*0.5) = 1700
CRL = 850/(1*0.8) = 1062.5

Urban environment will almost always need one by calculation.

Another way to do it is ask that customer how much tech thru own; iPads, TVs, computers, consoles etc (chances are you'll easily hit low to mid 1000s), ask if they have insurance and the excess they would have to pay on a claim AND how much that will increase for them next year.

In most cases your SPD will cost less than any excess and so be a no brainer.
 
So lets consider what a lightning strike can damage in a best case scenario of a little old ladies house.. The consumer unit, all wiring, all accessories, TV, Microwave, fridge/freezer. So thats a complete rewire, including redecoration, new TV, microwave and fridge/freezer, lets say thats ÂŁ5000 as a cheap estimate..
Little old lady has lived for 80 years and has never once had the above problem, nor does she know anyone who has. And neither do I. Why? Cos it happens so incredibly rarely that the risk is negligible. Also, little old lady is on state pension, so has very limited funds and does not want to spend unnecessarily, ÂŁ70 is a lot of money to her. She wouldn't like to learn that her electrician was mis-selling her unnecessary items.

SPDs are there to help protect sensitive electronic equipment, I have not heard of them being touted as protection against direct lightning strikes of the magnitude that would destroy fixed wiring. Where are you getting this information from?


You are trying to say that a ÂŁ70 SPD is not justified to save ÂŁ5k?
You're misrepresenting my argument. IF a surge event happens, and the SPD protects ÂŁ5k worth of equipment (which it isn't guaranteed to do BTW), then it was money well spent. However, the odds of it happening are so incredibly slim as to be negligible. And even if they weren't, who am I to make that decision? It's up to my clients.

There has been youtube videos where a lady from the IET (cant remember her name but an expert on transient voltages) said for all residential properties the interpretation is that they all need SPD's.
Without a link to back this comment up, this smells of fertiliser.

If you are really concerned about cost go fit a BG board with SPD which is currently ÂŁ20 at screwfix, or a fusebox SPD kit which is ÂŁ27. I can understand why we were having this conversation when SPD's were over ÂŁ100 but some are now ÂŁ20...
Why? Why should I make my clients spend ÂŁ20 more than they have to, if they don't want to? If ÂŁ20 is nothing to you, then send me ÂŁ20 now.

An SPD is generally as necessary as an RCD, if a customer said I dont want to pay for an RCD board would you fit a board with no RCD's?
This is a truly absurd comment.

Out of interest, before the 18th edition, were you forcing these oh-so incredibly important SPDs on your clients?
 
Little old lady has lived for 80 years and has never once had the above problem, nor does she know anyone who has. And neither do I. Why? Cos it happens so incredibly rarely that the risk is negligible. Also, little old lady is on state pension, so has very limited funds and does not want to spend unnecessarily, ÂŁ70 is a lot of money to her. She wouldn't like to learn that her electrician was mis-selling her unnecessary items.

SPDs are there to help protect sensitive electronic equipment, I have not heard of them being touted as protection against direct lightning strikes of the magnitude that would destroy fixed wiring. Where are you getting this information from?



You're misrepresenting my argument. IF a surge event happens, and the SPD protects ÂŁ5k worth of equipment (which it isn't guaranteed to do BTW), then it was money well spent. However, the odds of it happening are so incredibly slim as to be negligible. And even if they weren't, who am I to make that decision? It's up to my clients.


Without a link to back this comment up, this smells of fertiliser.


Why? Why should I make my clients spend ÂŁ20 more than they have to, if they don't want to? If ÂŁ20 is nothing to you, then send me ÂŁ20 now.


This is a truly absurd comment.

Out of interest, before the 18th edition, were you forcing these oh-so incredibly important SPDs on your clients?
I totally agree with all these arguments made by @Pretty Mouth

There was an article in Connections Magazine a while back, which basically said the decision on whether to install an SPD in a domestic setting, shouldn't be made solely on value of the connected equipment, but also on the likelihood of a surge event happening.

Having said that, as SPDs have come down in price quite a lot, I have taken the decision to fit them as standard in most properties when I change a consumer unit. But I will always try to give the best value for money, especially when the client is not well off financially. Which means that sometimes the SPD gets left out.
 
CRL = 850/(1*0.5) = 1700
CRL = 850/(1*0.8) = 1062.5

Urban environment will almost always need one by calculation.
Sorry, didn't follow. Your examples for Urban work out above 1000, so don't require SPD.
I thought it was Countryside that was more likely to require SPD's? (says me living in the countryside ?)
 
Anyone saying they have never heard of any equipment being damaged by surges - you probably wouldn't even realise. Any faulty device could have been affected by a surge.

Also, sometimes people seem fixated on direct lightning strikes. Of course an SPD won't protect against this, but it may well protect against the induced peaks on the mains caused by such a strike.

A company once tried to cost-down their product by removing some of the lightning/surge protection components. What happened? Well, they started getting more products returned as faulty. Faults caused by surges.
 
Had a powercut at home a few months ago, when the power came back on I had a dead cctv monitor and surround sound system. I can only assume there was a surge of some description at that point. Because they worked before it. Replacing those 2 items cost me ÂŁ600. Power cuts are common out in rural suffolk where I live, who knows if an spd would have saved them, but they literally do now get built into the price of everyjob board replacement i do due to this personal experience.
 

Reply to Client refusing spd in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
373
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
938
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

  • Question
This potential client seems to be making progress in terms of being interested in proper chargers and answering my query questions. I have also...
Replies
13
Views
2K
Problems can arise when you get on too well then they think he won’t mind me doing a bit.
    • Friendly
    • Like
Replies
8
Views
470

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top