Code 1 Problems - Am I being Scammed? | Page 5 | on ElectriciansForums

Discuss Code 1 Problems - Am I being Scammed? in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

Looks like his maximum Zs for protective devices are incorrect too! he has put down 80% of tabulated values instead of the values quoted in the Regs eg 1.15 for 60898 32a (@80%) / 1.44 in regs.
 
Looks like his maximum Zs for protective devices are incorrect too! he has put down 80% of tabulated values instead of the values quoted in the Regs eg 1.15 for 60898 32a (@80%) / 1.44 in regs.
That's debatable.
I believe the NICEIC require the value quoted in BS7671, wheras NAPIT allow either that or the 80% value.
BS7671 doesn't require any value at all.
Myself, I'd prefer the 80% value, as it's clear to the client then that the measured values are within limits.
 
The schedule of inspections is the usual generic rubbish, I'm amazed that there's no tick in the earth electrode box.

He reports overrated protective devices yet ticks the 'choice & setting' box.

He reports 'no RCDs' yet ticks the 'presence of residual current devices' box.

He reports a flex supplied from a cooker circuit yet ticks the 'selection of conductors for volt drop and current carrying capacity' box.

I wonder by what method he verified voltage drop? (another tick).

Utter rubbish, not unusual for a domestic PIR, usually takes me about 10 seconds to decide, this one took slightly less....
 
The schedule of inspections is the usual generic rubbish, I'm amazed that there's no tick in the earth electrode box.

He reports overrated protective devices yet ticks the 'choice & setting' box.

He reports 'no RCDs' yet ticks the 'presence of residual current devices' box.

He reports a flex supplied from a cooker circuit yet ticks the 'selection of conductors for volt drop and current carrying capacity' box.

I wonder by what method he verified voltage drop? (another tick).

Utter rubbish, not unusual for a domestic PIR, usually takes me about 10 seconds to decide, this one took slightly less....
Are you fence sitting IQ?
 
That's debatable.
I believe the NICEIC require the value quoted in BS7671, wheras NAPIT allow either that or the 80% value.
BS7671 doesn't require any value at all.
Myself, I'd prefer the 80% value, as it's clear to the client then that the measured values are within limits.

Fair enough... I always put the 100% as we use NIC certs
 
First you have to consider whether the Agency will accept a new PIR.

I don't see this being an issue. Once I explain to them that the person they reccomended made a complete bodge job of the report and that I will be getting my own guy to do it they will understand. As mentioned they dont have any affiliation with this electrician, he is just someone who has done some work for them in the past. Its likely they will cease to use this person.

Futhermore if the person I use from this forum comes and does a decent job I could put them forward as a more worthy candidate for for work like this in the future.
 
I don't see this being an issue. Once I explain to them that the person they reccomended made a complete bodge job of the report and that I will be getting my own guy to do it they will understand. As mentioned they dont have any affiliation with this electrician, he is just someone who has done some work for them in the past. Its likely they will cease to use this person.

Futhermore if the person I use from this forum comes and does a decent job I could put them forward as a more worthy candidate for for work like this in the future.
PM sent.
 
View attachment 7649

View attachment 7650

Heres the relevant pages of the report in image format. To be honest I dont mind paying the ÂŁ150 + VAT for the cert but then having to pay additional for stuff that isnt needed is an issue for me.

A few things jump out at me. I haven't read all the previous posts in detail so some or all of them may have already been mentioned.

Test Results

80% values used for Maximum permitted EFLI
R1 + R2 for the two rings don't coincide with the r1 and r2

Inspections


Nominal Voltage U should be N/A for single phase and U[SUB]0[/SUB] should be 230V
Short circuit capacity of BS 88 fuse not entered. This info can be found in the OSG
Choice and setting of protective devices ticked even though he's given one of them a code 1
Presence of RCD ticked although he's said there isn't any
Selection of conductors for current carrying capacity and voltage drop ticked although he's given a code 1 to the hob igniter cable
 
Make sure you keep us informed on the outcome of this please.

Also make sure the observations recorded are understandable and explained to you as the client.
 

Reply to Code 1 Problems - Am I being Scammed? in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
669
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
1K
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
2K

Similar threads

  • Question
Thanks for your advice guys. very helpful
Replies
4
Views
1K
  • Article
This is an RSS feed of thread: Two electrical supplies and a single immersion element Content of the thread: Good afternoon, new joiner here with...
Replies
0
Views
205

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top