Had a look at the property the other day.
A number of problems with the PIR.
To start off with, the supply is TN-C-S, not TN-S, there's a sticker on the cut-out, and the head is not sealed, so the neutral/earth link is easily viewed by opening the lid.
The main switch is rated at 240V but the inspector has noted 230V.
The Main fuse, is type II, but the inspector hasn't noted the type, or the Short-circuit capacity.
The circuits on the PIR are numbered backwards, circuit 10 next to the main switch, circuit 1 furthest from the main switch (MK Sentry CU).
On a couple of socket circuits, the number of points served are incorrect, on one circuit it's listed as 7 when there are 9, and on another 6 when there are only 3. No idea where the other socket has appeared from?
The Inspector missed the lack of earth continuity on one of the socket-outlets, a spur which I have disconnected and blanked off.
The unknown circuit is for the combi boiler.
Circuit 9 which has had a code 1 applied because it has an OPD of 32A, and the inspector reccomends 16A, is actually a RFC wired in 2.5mm² T&E, so no code at all.
There is one socket-outlet in the hall by the front door on the ground floor, which is likely to be used for mobile equipment outdoors which I have changed for an RCD socket.
I've stuck some lables on the CU.
No warning lables required for two versions of wiring, as it's all Red and Black, no RCD warning lable required, as there isn't an RCD in the CU.
I've listed the lack of RCD protection for the socket-outlets intended for general use by ordinary persons, the lack of RCD protection for circuits of a location containing a bath or shower and the lack of RCD protection for cables concealed in walls at a depth less than 50mm all as code C3s (decided to do it as an EICR).
Haven't coded the heat detector in the hall, as it's not within the scope of BS7671.
Haven't coded the 0.75mm² flex for the hob ignition, as it's a fixed load, that is unlikely to be subjected to overcurrent.
 
Spin - obviously without exposing the name of the previous PIR "inspector" or his company, can you reveal whether he is an incompetent one man show or belonging to one of these bucket shops turning out PIRs by the hour? Cheers.
 
Had a look at the property the other day.
A number of problems with the PIR.
To start off with, the supply is TN-C-S, not TN-S, there's a sticker on the cut-out, and the head is not sealed, so the neutral/earth link is easily viewed by opening the lid.
The main switch is rated at 240V but the inspector has noted 230V.
The Main fuse, is type II, but the inspector hasn't noted the type, or the Short-circuit capacity.
The circuits on the PIR are numbered backwards, circuit 10 next to the main switch, circuit 1 furthest from the main switch (MK Sentry CU).
On a couple of socket circuits, the number of points served are incorrect, on one circuit it's listed as 7 when there are 9, and on another 6 when there are only 3. No idea where the other socket has appeared from?
The Inspector missed the lack of earth continuity on one of the socket-outlets, a spur which I have disconnected and blanked off.
The unknown circuit is for the combi boiler.
Circuit 9 which has had a code 1 applied because it has an OPD of 32A, and the inspector reccomends 16A, is actually a RFC wired in 2.5mm² T&E, so no code at all.
There is one socket-outlet in the hall by the front door on the ground floor, which is likely to be used for mobile equipment outdoors which I have changed for an RCD socket.
I've stuck some lables on the CU.
No warning lables required for two versions of wiring, as it's all Red and Black, no RCD warning lable required, as there isn't an RCD in the CU.
I've listed the lack of RCD protection for the socket-outlets intended for general use by ordinary persons, the lack of RCD protection for circuits of a location containing a bath or shower and the lack of RCD protection for cables concealed in walls at a depth less than 50mm all as code C3s (decided to do it as an EICR).
Haven't coded the heat detector in the hall, as it's not within the scope of BS7671.
Haven't coded the 0.75mm² flex for the hob ignition, as it's a fixed load, that is unlikely to be subjected to overcurrent.

Nice one Spin, sounds spot on and makes an absolute mockery of the **** that was compiled previously.
 

Reply to Code 1 Problems - Am I being Scammed? in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
669
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
1K
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
2K

Similar threads

  • Question
Thanks for your advice guys. very helpful
Replies
4
Views
1K
  • Article
This is an RSS feed of thread: Two electrical supplies and a single immersion element Content of the thread: Good afternoon, new joiner here with...
Replies
0
Views
205

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top