Well fair play to the manufacturers, all but 1 of them I contacted got back to me on this. Interesting to note the diverse replies I received. This is the email I sent out:
Good morning,
I have a technical query regarding your MCBs.
An MCB is subjected to a small overload of short duration (eg. a B32 MCB subjected to 40 A for 10 minutes), but not long enough to operate the MCB. This happens repeatedly, say once or twice a day for 25 years.
Could being used this way eventually damage the MCB?
In what way would the MCB be damaged?
If the MCB did fail as a result of the above, would it fail safe (open circuit) or closed?
Kind regards,
PRETTY MOUTH
And here are the replies:
CHINT:
The situation you are talking about would not cause any long term damage.
In the real world the only real way to damage an MCB is to have a dead short. This can create 1000’s amps of current for a split second until the MCB trips.
This is called the kA rating. Most of our MCBs are either 6 or 10 kA (6000 or 10000). A 6ka rated MCB with survive a 6000A short circuit and still be useable in the future.
HAGER:
Using an MCB in this way would not be a good design practice, and may over time be damaging to the MCB, I can not say if it fails it will fail open or closed.
Importantly you should consider is the circuit correct to carry this extra current, cable size? And possible damage to this cable over time.
This is possibly a shower circuit with an upgrade to a higher wattage shower but using the original breaker and cable.
WYLEX:
Please see below from our test lab.
Although it appears that the mcb is operating satisfactorily without further information it’s not possible to do more than make recommendations.
The 32 A mcb is being subject to an overload which is thermally stressing it and possibly any cable between the mcb and the load. It would be better if the mcb was replaced by a 50 A mcb which would then be operating well within its capabilities.
Could being used this way eventually damage the MCB?
Yes.
In what way would the MCB be damaged?
As the mcb is being thermally stressed the mouldings could be being burnt, when the contacts operate they could be subjected to degradation due to the higher current producing more arcing.
If the MCB did fail as a result of the above, would it fail safe (open circuit) or closed?
The worst outcome would be that the mcb would fail, which could cause a fire. If the mcb is in an insulated consumer unit this could cause a house fire.
BRITISH GENERAL:
The product has been designed to accommodate this load demand for the periods as given in the BS7671 regulations and should not affect the performance in anyway.
It is more prolonged overloading or fault operations that could reduce the products life expectancy as there is a limit as with all manufactures on how many times the product can withstand this before it fails typical.
For the manner the unit would fail we would expect it fail in the off position. But this would depend on the fault that had occurred at the time. This is why now in domestic situations an RCD is required for all circuits.
I have attached a copy of our data sheet which includes the operations switching and mechanical operation values.
The BG data sheet says 'Endurance Operations : Electrical 4000, Mechanical 10000.
Crabtree also got back asking which range I was referring to, and contactum didn't reply.