A quote should not accompany a PIR, get a different person to do the remedial works.
As for the report:
No cpc's on lighting is code 2 (ESC BPG04)
Sockets on a lighting circuit is a code 4 as there is no real risk, the fuse would blow.
Sockets on a 5A fuse - no code at all its not a deviation.
No MPBC code 1 not 2
Shower circuit in 6mm is fine Overload would blow the fuse
Disconnected cable in CU code 3 OK
RCD protection Code 4 unless likely to be used outside Code 2
Fuse board complies No code
Not 100% sure about last 1 they are either labelled or not, what identification to cpc's other than sleeved and in correct order - not rocket science in a House wit T&E
Very strange that ALL the R1+R2+ZE are perfectly equal to ZS - not likely!
Maximum recognised IR value shod be >299
I guess there is no telephone or shaver socket in the house.
No requirement for danger notices - so cannot fail on that.
What choice or protective device setting is required?
What is wrong with VD?
Particular protective measures should be at least a LIM as it is a requirement of the 17th
No light switches I see!
No values for ring continuity - is there a ring circuit?
As for the report:
No cpc's on lighting is code 2 (ESC BPG04)
Sockets on a lighting circuit is a code 4 as there is no real risk, the fuse would blow.
Sockets on a 5A fuse - no code at all its not a deviation.
No MPBC code 1 not 2
Shower circuit in 6mm is fine Overload would blow the fuse
Disconnected cable in CU code 3 OK
RCD protection Code 4 unless likely to be used outside Code 2
Fuse board complies No code
Not 100% sure about last 1 they are either labelled or not, what identification to cpc's other than sleeved and in correct order - not rocket science in a House wit T&E
Very strange that ALL the R1+R2+ZE are perfectly equal to ZS - not likely!
Maximum recognised IR value shod be >299
I guess there is no telephone or shaver socket in the house.
No requirement for danger notices - so cannot fail on that.
What choice or protective device setting is required?
What is wrong with VD?
Particular protective measures should be at least a LIM as it is a requirement of the 17th
No light switches I see!
No values for ring continuity - is there a ring circuit?