That report has too many errors throughout it to be worth the paper that it is written on. There is no way on the planet that the Ze + R1+R2 for every circuit magically equals Zs. A 35mA RCD now that says it all.
 
Wingers,

have you actually paid for your reports yet?

Don't think much to his 'quote' either. Cheap on the CU change yet v. expensive on the bonding I'd say. (I notice he doesn't mention what make of CU he'd be using, some 'ccc' no doubt)
 
thats what i thought earthing porvided by the suppliers and an earth rod one or the other i spotted loads of errors 1mm lighting cable with 1 mm cpc when it hasnt got one look at my previouse post to see what i spotted , on the subject some 6mm twe does have a 4mm cpc so it could be
 
Wingers,

have you actually paid for your reports yet?

Don't think much to his 'quote' either. Cheap on the CU change yet v. expensive on the bonding I'd say. (I notice he doesn't mention what make of CU he'd be using, some 'ccc' no doubt)
Not yet, got invoice this morning

Will have to email him and query some of the bits you have all mentioned and ask what make CU he would fit
 
thats what i thought earthing porvided by the suppliers and an earth rod one or the other i spotted loads of errors 1mm lighting cable with 1 mm cpc when it hasnt got one look at my previouse post to see what i spotted , on the subject some 6mm twe does have a 4mm cpc so it could be

You sure about that? I've come across 7/044 - 7/029 imperial cable and can see how it might be mistaken for 6.0/4.0 (actual csa would be 6.9/3.0)
 

Attachments

  • Imperial cable ratings.pdf
    57.1 KB · Views: 26
Last edited by a moderator:
If this installation that has been PIR'd is 40+ years old then none of the cable sizes noted in this report are correct, it would have all been wired in imperial sizes. So those 6 mm T&Es would have been 7.044 with a stranded 3.036 cpc The 2.5mm T&ES 7.029 with a 3.029 cpc.
 
That report has too many errors throughout it to be worth the paper that it is written on. There is no way on the planet that the Ze + R1+R2 for every circuit magically equals Zs. A 35mA RCD now that says it all.

Obviously calculated all ZS's and not took a measurement :D
 
Do feel free to open my rating document and save yourself a copy to use next time you're changing a CU on a house with imperial cable. (post #36)
 
Odd bit of form filling
5419 is an old BS number for a double pole switch,yet it is apparantly a 35m/amp Rcd :confused:
4293 is the old Rcd No
The rating of the Rcds are usually 63 amp not 60 ,something amiss here

Both tick boxes checked for suppliers earth and TT.
If its TT, its one cracker of an earth path, with just 0.22 ohms,yet a low Pfc of just 0.5Ka

I take it that the reading for the rod was taken at the Met without removing the conductor, and a Pme or Tns connection was beeing recorded

Look on the bright side,there is uniform brilliance as far as the insulation resistance of the installation is concerned, :)
 

Reply to Comments advice on report after having Electrical inspection in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
As the holiday season approaches, PCBWay is thrilled to announce their Christmas & New Year Promotions! Whether you’re an engineer or an...
Replies
0
Views
642
  • Article
Bloody Hell! Wishing you a speedy recovery and hope (if) anyone else involved is ok. Ivan
    • Friendly
    • Like
Replies
13
Views
1K
  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
961

Similar threads

Just to add. The plumbing forum has no ads on at all right now as I'm waiting for it to get verified. So you can browse it all nice and quick.
Replies
1
Views
1K
L
  • Article
Have you ever / would you ever; Work for a Plumbing Supplier / Plumbing Wholesaler Have you ever / would you ever; Work for a Plumbing Supplier /...
Replies
0
Views
168
L

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top