That report has too many errors throughout it to be worth the paper that it is written on. There is no way on the planet that the Ze + R1+R2 for every circuit magically equals Zs. A 35mA RCD now that says it all.
Follow along with the video below to see how to install our site as a web app on your home screen.
Note: This feature may not be available in some browsers.
Discuss Comments advice on report after having Electrical inspection in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net
Not yet, got invoice this morningWingers,
have you actually paid for your reports yet?
Don't think much to his 'quote' either. Cheap on the CU change yet v. expensive on the bonding I'd say. (I notice he doesn't mention what make of CU he'd be using, some 'ccc' no doubt)
thats what i thought earthing porvided by the suppliers and an earth rod one or the other i spotted loads of errors 1mm lighting cable with 1 mm cpc when it hasnt got one look at my previouse post to see what i spotted , on the subject some 6mm twe does have a 4mm cpc so it could be
We're in the Norwich area... And as you clearly don't trust your electrician... I don't think I'll bother thanks
That Ze reading needs checking. 0.22?? Really?
That report has too many errors throughout it to be worth the paper that it is written on. There is no way on the planet that the Ze + R1+R2 for every circuit magically equals Zs. A 35mA RCD now that says it all.