Evening..

I am working on a large property at the moment putting in a new bathroom, kitchen etc. The owner has done a fair bit of DIY. One such job entails using a bit of 2 core flex (0.75mm) from a JB under the floorboards, then up the wall in trunking and across the loft where it reaches its position and drops through the ceiling into a pendant.

I have changed the JB to MF and will put a proper ceiling rose on the ceiling, however I can't quite figure out if there is anything wrong with the 2 core flex going up the wall. Basically it's not earthed, his argument is that it is normal for the cable coming from a ceiling rose to be 2 core, and he's right... this is just a very, very long ceiling pendant! ?? PS.. it's a plastic pendant. Plus many older properties don't have earthing to lights. I want to change it for twin and earth but I can't think of any reg that says this has to be done?

Cheers.
 
So he is spending a sh!te load of money on a kitchen and a bathroom but arguing about the cable to the light, as mentioned above the cable should have a CPC as the chance of someone hammering a nail in to 9" of pendant cable is slim but the chances of it getting damaged in the run are a lot higher.

Just tell him you know better.
not very likely someone will nail cable in trunking.
 
not very likely someone will nail cable in trunking.

That's a piece of mini trunking containing a shower cable that I installed a few years earlier. Painted over and a screw inserted!

[ElectriciansForums.net] Comments on this DIY job please?
[ElectriciansForums.net] Comments on this DIY job please?
 
HHD why did he run a supply from under the boards then up through to the loft when there would be a lighting feed in the loft already ? I must be missing something ?
Its a landing light so youre right theres lots of cables in the loft, but the switch is on the ground floor.
 

Reply to Comments on this DIY job please? in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
381
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
959
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

  • Question
I would use the Switch & Load 16A - https://www.quickwire.co.uk/product/switch-load-16a/ Designed to do the same thing as the ceiling rose in...
Replies
5
Views
778
Promised a photo…. Remember, this was working…. And they managed to move in without hitting it…
    • Like
Replies
4
Views
363

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top