Electricians guide to the building regs expands on it -- section 2. Basically the zone on one side extends to the reverse side of the wall ..... provided of course the location of the accessory/safe zone can be determined from the reverse side!

Thst sound very familiar now you say it, My regs book and OSG are 200 miles away at present.
 
Glenn can you point me in the direction that suggests that a safe zone carries through the wall. I was under the impression that it was only contained within the same room? Admittedly I wouldn't drill into a wall directly behind a light switch.

BGB Top of pg 125 (522.6.101.v)

OSG implies it by illustration pg 74
 
Electricians guide to the building regs expands on it -- section 2. Basically the zone on one side extends to the reverse side of the wall ..... provided of course the location of the accessory/safe zone can be determined from the reverse side!


...and provided the wall is 100mm thick or less
 
Personally I don't put cables in the wall using a safe zone on the reverse as it seems wrong and asking for someone to put a nail in a wire that they were not thinking was going to be there.
 
God what a saga!
Who designed the "solution"?
Did you the home owner agree to have fused unit behind a panel?
Who/when are the next connections being made?
Is the sparky a member of a scheme?
Is the equipotential bonding in place and to the regs?
How much are you paying?

and finally this should be in the DIY section.
 
Last edited by a moderator:
Personally I don't put cables in the wall using a safe zone on the reverse as it seems wrong and asking for someone to put a nail in a wire that they were not thinking was going to be there.


Yes but with some modern wall constructs (<100mm) your cables are vulnerable to the other side anyway.
 
As a non-technical question, how much did the 'electrician' charge for the job? My thinking being if you've paid peanuts on one of the trader sites you get monkeys doing the job ......

I am paying £450 for the job. This was meant to include them wiring up the pump etc which they haven't done. I'm not completely familiar with the price of these jobs but that sounds fair were the job done properly.
 
I am paying £450 for the job. This was meant to include them wiring up the pump etc which they haven't done. I'm not completely familiar with the price of these jobs but that sounds fair were the job done properly.

Why have they not wired the pump? Was it not ready for connection on the day?
Why are the fuses removed from the FCUs? Is there further work to be done?

You said your main concern was the FCUs (normal type) installed near the pipes - This is NOT a problem and is totally compliant.
 
God what a saga!
Who designed the "solution"?
Did you the home owner agree to have fused unit behind a panel?
Who/when are the next connections being made?
Is the sparky a member of a scheme?
Is the equipotential bonding in place and to the regs?
How much are you paying?

and finally this should be in the DIY section.

You have NO idea how much of a saga this whole bathroom has been... 6 months since I had a functioning shower in my house... this is just another part of it!

• I designed the room and the placement of the equipment. It was the only way it was going to work, I spent a few weeks doing it on a computer to scale. It wasn't a rush job.
• I spoke to the guy over the phone and he said he was going to locate everything above the mixer, I explained that there would be a panel there but I didn't really think this meant the fused switches in the bathroom, I was thinking he meant the location of junction boxes etc.
• I guess I am going to do the final connection.. wasn't mentioned they were coming back.
• They had a whole load of certifications on their page on the trader website. I also clarified they were Part P certified as this is an ex local property and I HAVE to abide by the councils rules.
• This was mentioned but I will have to wait till I get the invoice to see if they have actually added it.
• £450

Cheers,

Tom.
 
Why have they not wired the pump? Was it not ready for connection on the day?
Why are the fuses removed from the FCUs? Is there further work to be done?

You said your main concern was the FCUs (normal type) installed near the pipes - This is NOT a problem and is totally compliant.

Im not entirely clear why they didn't wire the pump or mixer... both were installed and ready for wiring, there is no water supply at the moment but they can both be dry tested.

The mirror will need adding at a later date as obviously I need to add the panels and tile before it goes up.

Thanks for clarifying about the FCUs. That was indeed my main concern.
 
Im not entirely clear why they didn't wire the pump or mixer... both were installed and ready for wiring, there is no water supply at the moment but they can both be dry tested.

The mirror will need adding at a later date as obviously I need to add the panels and tile before it goes up.

Thanks for clarifying about the FCUs. That was indeed my main concern.


This may be why they have chosen not to wire the pump yet - pump can overheat without water (you say they are coming back re: the mirror).

Have you discussed your concerns with the electrician? If so what does he say?
 
You have NO idea how much of a saga this whole bathroom has been... 6 months since I had a functioning shower in my house... this is just another part of it!

• I designed the room and the placement of the equipment. It was the only way it was going to work, I spent a few weeks doing it on a computer to scale. It wasn't a rush job.
I spoke to the guy over the phone and he said he was going to locate everything above the mixer, I explained that there would be a panel there but I didn't really think this meant the fused switches in the bathroom, I was thinking he meant the location of junction boxes etc.
• I guess I am going to do the final connection.. wasn't mentioned they were coming back.
• They had a whole load of certifications on their page on the trader website. I also clarified they were Part P certified as this is an ex local property and I HAVE to abide by the councils rules.
• This was mentioned but I will have to wait till I get the invoice to see if they have actually added it.
• £450

Cheers,

Tom.
So are you saying he quoted you a price without visiting you? Junction boxes are also not recommended hidden behind panels
 
I am paying £450 for the job. This was meant to include them wiring up the pump etc which they haven't done. I'm not completely familiar with the price of these jobs but that sounds fair were the job done properly.

For a days work, an RCD, a bit of T&E and 3 FCU's you've not paid for monkeys!
 
No I agree with badged. That's a fair bit of money for what looks on paper quite straight forward.
 
For a days work, an RCD, a bit of T&E and 3 FCU's you've not paid for monkeys!

This may also include main & supplementary bonding, a second visit when mirror, water supply etc is ready

The price is difficult to judge without all the facts - the £450 may have been a worse scenario estimate (it was 'over the phone')
 
So are you saying he quoted you a price without visiting you? Junction boxes are also not recommended hidden behind panels

No he visited me to give me a quote. I was stuck in meetings at work so my other half was at home when the job was actually done which is when I spoke to him on the phone.

We hadn't discussed the finer details of where everything was going.

This looks like its my fault really as I didn't spell it out...
 
This may also include main & supplementary bonding, a second visit when mirror, water supply etc is ready

The price is difficult to judge without all the facts - the £450 may have been a worse scenario estimate (it was 'over the phone')

In that case if he's put in supp bonding (with an RCD?) and main bonding (absent? maybe undersized?) along with an additional days visit to wire in a pump and mirror (heck knows what he was doing the first day!) then you may well have a monkey doing the work :biggrin:

Edited ---- just read the above post on visiting to do the quote, so one assumes he knew what work he was quoting for!
 
No he visited me to give me a quote. I was stuck in meetings at work so my other half was at home when the job was actually done which is when I spoke to him on the phone.

We hadn't discussed the finer details of where everything was going.

This looks like its my fault really as I didn't spell it out...


Not really understanding what it is you are not happy with - the pump itself will need access for maintenance etc (designated panel cover) and this is no doubt why the electrician chose to mount the local switchgear in there - there is no problem with mounting electrical equipment in a location that has easy access.
 
In that case if he's put in supp bonding (with an RCD?) and main bonding (absent? maybe undersized?) along with an additional days visit to wire in a pump and mirror (heck knows what he was doing the first day!) then you may well have a monkey doing the work :biggrin:

Edited ---- just read the above post on visiting to do the quote, so one assumes he knew what work he was quoting for!

The RCD was for the RFC he was using to feed the install, the supplementary bonding is relevant if the lighting circuit has no RCD

Also this price probably includes VAT, actual price £375
 
Agree with Hawkmoon, I too cant see a problem with the FCUs within a void, accessable via a removeable panel and therefore outside the bathroom zones.

As for the cable running down the wall, as has been stated, we dont know whats on the otherside of the wall etc and cant be sure if it is outside of the so called "safe zones".

I can see why the cable has been run down the wall and not across to the left safe zone, as the water pipes are in the way, and the cable would need to cross under or over them. Lets be honest here, is this going to be a major hazard in this instance?, cable RCD protected, wooden studwork, not really picture hanging territory and if you were going to hang a towl rail or something else here your more likely to hit a water pipe.....besides, I'd look in the panel first, wouldnt you?

As for the price, why do people get so uptight if it looks like someone might make a profit for a change. The client says he was happy with the price, so what if you would do it cheaper, we all continuously moan about low wages etc but as soon as a price is mentioned on a thread like this, it's ooh that sounds expensive, must be a cowboy, knock some money off cos I'm cheaper blah blah blah.:smile:
 
The RCD was for the RFC he was using to feed the install, the supplementary bonding is relevant if the lighting circuit has no RCD

I got the impression he wasn't touching the lighting circuit, just extending the ring circuit for everything?
 
As for the price, why do people get so uptight if it looks like someone might make a profit for a change.

No problem with the price and a profit! My original thought was they had paid for a cheap job off "the web site" and hence perhaps the job wasn't as good as it should be! If you can get that money for a days work good luck :biggrin:
 
Agree with Hawkmoon, I too cant see a problem with the FCUs within a void, accessable via a removeable panel and therefore outside the bathroom zones.

As for the cable running down the wall, as has been stated, we dont know whats on the otherside of the wall etc and cant be sure if it is outside of the so called "safe zones".

I can see why the cable has been run down the wall and not across to the left safe zone, as the water pipes are in the way, and the cable would need to cross under or over them. Lets be honest here, is this going to be a major hazard in this instance?, cable RCD protected, wooden studwork, not really picture hanging territory and if you were going to hang a towl rail or something else here your more likely to hit a water pipe.....besides, I'd look in the panel first, wouldnt you?

As for the price, why do people get so uptight if it looks like someone might make a profit for a change. The client says he was happy with the price, so what if you would do it cheaper, we all continuously moan about low wages etc but as soon as a price is mentioned on a thread like this, it's ooh that sounds expensive, must be a cowboy, knock some money off cos I'm cheaper blah blah blah.:smile:


Absolutely (if tool needed to access) - no different to under bath as 701.32.3
 
So its all actually ok!? Some seriously mixed messages on this post! :)

Price is for one days work plus parts. No mention of coming back to wire the equipment up.

Cheers,

Tom.
 

Reply to Concerned about bathroom work carried out in the DIY Electrical Advice area at ElectriciansForums.net

Similar Threads

Bit of a sickener they didn't employ you to do the box change aint it? I might, as a disclaimer, point out with that certificate that as the...
Replies
2
Views
479
  • Question
ok cheers for the help lads
Replies
7
Views
574
You can replace a fan in zone 1 with a 230 volt fan with a pull cord, with an IP rating of at least IPX5, as long as the circuit is protected by a...
Replies
1
Views
1K
loz2754
L
  • Question
Rcd protection?
Replies
19
Views
2K
You could also use one of these to do exactly what you suggested with a bit of work rewiring the switch and fan cables. When the switch is turned...
Replies
8
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock    No Thanks