Consumer unit change | Page 2 | on ElectriciansForums
Discuss Consumer unit change in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net
Your profile lists you as an Electrical Apprentice, question is should you be doing this type of work unsupervised? not having a dig but any self respecting Electrician should have tested this installation prior to changing the CU, another question, why the need to change it in the first place, might be a good idea to get access to the trainee section get a bit more help in there, good luck.
I have this situation in my house.
Whoever installed experienced the same issues with tripping.
He did what Telectrix suggested.
I think I have a non destructive solution, can someone please critique ?
Put both circuits on the RCD side in separate MCBS
At the landing switch, wire it as a one way switch terminate cables.
Same with the hall swicth
Then fit a discreet flush mounted pir to operate the landing light. ?
Definitely don't do that. It's a breach of 314.4, and the EAWR too. And you may kill a fellow spark or hapless DIYer.
As Pete has quite rightly pointed out, it should be done under supervision of an electrician as the OP is an apprentice.
just by switching off the MCB ( or pulling the fuse) for upstairs lights and seeing if the landing light stayed on would give you a good indication.
Didn't think that I "spoke down" to the OP, my advice was clearly the right thing to do, I agree with you that Apprentices learn better by doing, rather than being told how to do things, but I stand by what I said, the OP ought to be supervised when doing this sort of work. And as a Mentor I take objection to being accused of not being nice, if you bothered to check any more of my posts to trainees, you will find out how fair I am, if the OP has taken objection to my post, then I will apologize to him/her, there was no malice intended.
Experience gained under the supervision of an experienced electrician, not doing it off their own back as and when they feel like it then relying on a forum to help them with the most basic problems.
He hasn't been spoken down to yet, but it could easily be arranged.
Thanks for the feedback, I've just read that reg and I think you might of read my post wrong.
I'm saying each in it's own mcb both rcd protected - not ideal when it trips I suppose.
Or maybe I've got it wrong I'm still new to all this :)
I've said it before and I'll say it again.
It always comes up on this sort of post that tests should be carried out before changing a CU. Fine. But given that most CU change requests involve a quote beforehand,I'll be b*****d if I'm going to carry out pretty much a full EICR for nothing on a job that I might not even get. OK,there's no harm in carrying out an IR test and a few Zs readings on the quote visit,but that still leaves a host of potential issues that only extensive testing will identify.The alternative,and my approach,is to carry out some basic tests at the quote stage,and include in the quote that full testing will be carried out while the CU is being replaced and that any faults which require rectifying may incur additional cost. It works for us and we quote and get loads of CU changes.
Quite frankly if anyone tells me they carry out full tests likely to find faults such as breaks in cpc continuity,breaks in rfc continuity,borrowed neutrals etc before every CU change I dont believe them.
I think you'll still have a shared neutral? I don't think your solution didn't mention separating the two circuits - the quickest safe way is to put them both on the same MCB, making them into 1 single circuit.
This guy explains it much better than I can on here.
https://www.youtube.com/watch?v=7C7Tkge5gvQ&noredirect=1
Thanks very much mate, I understand now. I see you're right. Cheers for posting the video I found it very useful.
You don't leave all of the testing until after fitting the new board do you?
I do the dead testing prior to removing the old board, then fit the board, then live testing.
I don't do any testing when quoting for the job but do allow a few hours of fault finding time plus have provision in the terms and conditions that says I will test the installation and not proceed if a major fault exists.
No,like you at least an IR test before removal. Usually RFC tests/R1+R2 during replacement,as the usual rats nest makes these tests much easier once the old boards out the way and you just have the cables. I've only come badly unstuck once,when a seemingly simple CU change uncovered an absolute nightmare. It took two days to complete the change and sort all of the issues...obviously an EICR before hand would have found it out and had I known I would have recommended a full rewire!
I reckon most issues when I do a CU change rarely add more than an hour or two to the job,often a lot less.
Reply to Consumer unit change in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net
2 3
