Would you not find the fault before hand unless you did the R1 + RN continuity test on that particular circuit? How often do people do the R1 + RN test?
most electricians will on older properties.

you use to have a N+E cable between each light and seperart L etc to switch and back.

now if they put the live from downstairs lights to switch then upto light on stairs it can cause this issue.

how you test varies depending on visual inspection
 
People living in Ivory towers !!
Luckily there are electricians out there who thankfully live in the real world.
A borrowed neutral on 2 way lighting is an unfortunate by product from by gone practices.
Left untouched in its original form it posed little problems, and guess what, you wont find many fatally electrocuted customers living in properties wired this way.
It was compliant with the regs of the time.
Whats important is that you do not feed the borrowed neutral circuits from different mcb's.
That would leave the installation with a potentially dangerous condition.
In an ideal world you would rewire the offending lighting circuit for compliance with current regs.
And make the customer aware of the requirement.
If for some reason this is not an option, ie customer refuses point blank because of costs and or disruption to decorations.
Well you could walk away !!
Which would leave those suggesting you do so, to move in and wire the lighting circuits onto 1 mcb effectively making them one circuit and in doing so removing a shared neutral scenario.
Of course you should list this as a departure, and make your comments on the existing installation as to the if's what's and whys.
Its your choice and a judgement call as a qualified sparks.
What it isn't, and never has been, is a shock horror, lets be drama queens run forest run scenario.
Presumably you are with a scheme provider considering a board change is notifiable and if your going to building control on your own back,it will cost you lots of ÂŁÂŁÂŁÂŁs
So if in doubt just phone there technical helpline and ask there advice.
They will give you exactly the same options as I have mentioned above, and at least that way you are getting sensible, and practical advice.
Forums are only as good as the people using them so be careful, and always get advice from qualified trusted sources as a cross check.
Hope that helps.
 
A borrowed neutral on 2 way lighting is an unfortunate by product from by gone practices.
Left untouched in its original form it posed little problems, and guess what, you wont find many fatally electrocuted customers living in properties wired this way.
It was compliant with the regs of the time.
.

How do you know it was compliant with the regs of the time? I can't find anything in the 13th or 14th which allows it.
 
People living in Ivory towers !!
Luckily there are electricians out there who thankfully live in the real world.
A borrowed neutral on 2 way lighting is an unfortunate by product from by gone practices.
Left untouched in its original form it posed little problems, and guess what, you wont find many fatally electrocuted customers living in properties wired this way.
It was compliant with the regs of the time.
Whats important is that you do not feed the borrowed neutral circuits from different mcb's.
That would leave the installation with a potentially dangerous condition.
In an ideal world you would rewire the offending lighting circuit for compliance with current regs.
And make the customer aware of the requirement.
If for some reason this is not an option, ie customer refuses point blank because of costs and or disruption to decorations.
Well you could walk away !!
Which would leave those suggesting you do so, to move in and wire the lighting circuits onto 1 mcb effectively making them one circuit and in doing so removing a shared neutral scenario.
Of course you should list this as a departure, and make your comments on the existing installation as to the if's what's and whys.
Its your choice and a judgement call as a qualified sparks.
What it isn't, and never has been, is a shock horror, lets be drama queens run forest run scenario.
Presumably you are with a scheme provider considering a board change is notifiable and if your going to building control on your own back,it will cost you lots of ÂŁÂŁÂŁÂŁs
So if in doubt just phone there technical helpline and ask there advice.
They will give you exactly the same options as I have mentioned above, and at least that way you are getting sensible, and practical advice.
Forums are only as good as the people using them so be careful, and always get advice from qualified trusted sources as a cross check.
Hope that helps.
how is having them fed from different mcb's a problem? if there on the same double pole rcd then the N wont be disconnected without the L anyway.

remember the N are usually commoned together
 
How do you know it was compliant with the regs of the time? I can't find anything in the 13th or 14th which allows it.
under the 13/14th you would only have 1 neutrel bar so they are all linked so would make no difference if it was fed from another mcb, not good practise but not against the regs of the time as far as im aware
 
under the 13/14th you would only have 1 neutrel bar so they are all linked so would make no difference if it was fed from another mcb, not good practise but not against the regs of the time as far as im aware

You still only have one neutral bar but borrowed neutrals are just as bloody dangerous.
The last time I came across borrowed neutrals was between 2 adjacent TPN boards, live taken from one board and neutral from the other.
 
under the 13/14th you would only have 1 neutrel bar so they are all linked so would make no difference if it was fed from another mcb, not good practise but not against the regs of the time as far as im aware

It's been against the regs for at least 35 years, probably longer. And whether it complied or not, it's as dangerous now as it was then.

The problem arises when some poor sod comes along to change, for example, a ceiling rose.

With the MCB off/fuse removed on the circuit being working on, and the circuit proved dead work proceeds.

If there is a load on the other circuit (the one that is sharing the neutral) full line voltage will appear on the neutral as it is pulled from is terminal. It's f***ing dangerous (to electricians, handymen, diyers and anyone else likely to work on it) because safe isolation requires two (or more) MCBs to be turned off.

Under normal circumstances it does not pose any problem to the installation user.
 
It's been against the regs for at least 35 years, probably longer. And whether it complied or not, it's as dangerous now as it was then.

The problem arises when some poor sod comes along to change, for example, a ceiling rose.

With the MCB off/fuse removed on the circuit being working on, and the circuit proved dead work proceeds.

If there is a load on the other circuit (the one that is sharing the neutral) full line voltage will appear on the neutral as it is pulled from is terminal. It's f***ing dangerous (to electricians, handymen, diyers and anyone else likely to work on it) because safe isolation requires two (or more) MCBs to be turned off.

Under normal circumstances it does not pose any problem to the installation user.

that's why you should knock the main switch off.
 

Reply to Consumer unit change in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
461
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
1K
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
2K

Similar threads

That's a hell of a big jump to make, an RCD trips therefore a rewire is required! If a wheel on your van gets a puncture do you go out and buy a...
Replies
6
Views
999
davesparks
D
I opened up the CU again and the round junction box above and what I found was the blue and brown wires coming in from the wall just above the 15a...
2 3
Replies
33
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top