What’s your thoughts of a new renovated house that has the consumer unit in the bathroom. It’s situated above the bath in a cupboard. It was brought 2 weeks ago and have no certs. They want a Eicr done. Obviously the sockets has to go too.

Thanks
 

Attachments

  • [ElectriciansForums.net] Consumer unit in bathroom
    E6E1F921-7BF1-46CC-8EF8-676393E1A395.jpeg
    365.9 KB · Views: 171
  • [ElectriciansForums.net] Consumer unit in bathroom
    D3438627-ADB4-4EFC-A218-CBE36CAB552F.jpeg
    350.3 KB · Views: 141
  • [ElectriciansForums.net] Consumer unit in bathroom
    BBD32DD6-A7A7-48A1-A029-BF03C65E7A2B.jpeg
    405.6 KB · Views: 147
The cheapest solution is to box it in the cupboard, it's then out of zones and out of reach. It would just be a C3 for access but a bit of a bodge. The ideal and recommended solution is to relocate it.
 
Very interesting thread and many of the comments are extremely pertinent, however I am just astonished that anyone would install that CU in that location. No matter what technical justification might be relevant, it's just a bad installation idea.
A few years ago I was doing some work on a new-build housing estate where all the houses had the CU installed at high level in the downstairs cloakroom. This was a mainstream builder and I am aware the same installation was carried out on other estates. Now, I accept the cloakroom had no bath or shower, but the only way to gain access to the CUs in these houses was by standing on the WC...there's no room to place a ladder or hop-up. I accept these houses passed BC regulations, but in my opinion the CU should not be mounted high up above a WC. A less-able person would find access extremely tricky and indeed hazardous, and for that reason alone it shouldn't be allowed.
 
We’re all pretty adamant it shouldn’t be there, but the OP questions how it should be coded on an EICR, as it is already there.

I’m wondering originally if that room was an entrance hall…. Ergo, CU was there before the bath was.


Although a keyed lock could easily be fitted to the cupboard door, the suitability of the equipment is not good for the environment.


C2…. Just to make sure it gets done.
 
Although a keyed lock could easily be fitted to the cupboard door, the suitability of the equipment is not good for the environment.
Agreed. While having it locked is (in some ways) an improvement, there are still issues, in particular that locking it impairs isolating power quickly or restoring power (e.g. lights) quickly.
Daft scenario: someone's alone in the house, having a bath, and the lights trip. Standing in a foot of water in a slippy bath, dripping wet, scrambling for a key to operate a breaker doesn't seem a very acceptable scenario!

I think the Reg 12 guidance in EAWR speaks for itself:
"The suitable means for cutting off the supply (regulation 12(1)(a)) should be in a suitable location regarding the nature of the risks, the availability of people to operate the means and the speed at which operation may be necessary. Access to switches etc should be kept clear and unobstructed, free of tripping and slipping hazards etc;"

The only solution I'd be happy with is putting the whole lot in an IP box or two and extending supply and final circuits to somewhere else.
 
The cheapest solution is to box it in the cupboard, it's then out of zones and out of reach. It would just be a C3 for access but a bit of a bodge. The ideal and recommended solution is to relocate it.
But then that brings up the accessibility of the CU and inconvienence caused to reset a tripped breaker

This is one of those situations where this thread could and probably will end up going round in circles without a solution acceptable to all
Looking at the pictures I would have to question how accessable the CU is for being working on it looks close to the ceiling and above the bath so it is impossible to put a ladder near it to safely access it, no doubt the customer would complain if you scratched the bath as well
The socket for me is a definite no no as it puts the seeds of temptation there for plugging in whatever tech someone wants to take into the bathroom while they have a bath or shower. I read somewhere recently deaths from electrocution using tech while having a bath are on the rise

Daft scenario: someone's alone in the house, having a bath, and the lights trip. Standing in a foot of water in a slippy bath, dripping wet, scrambling for a key to operate a breaker doesn't seem a very acceptable scenario!
I was thinking similar someone in the shower and another person knocks on the bathroom door asking the person in the shower to reset a tripped breaker
The only solution I'd be happy with is putting the whole lot in an IP box or two and extending supply and final circuits to somewhere else.
Or relocate the bathroom!!. Why create work for the electrician because the plumber or more likely the not so handy handyman screwed up😄

I think any solution where the installation remains as is with locks, IP enclosures etc is always going to be flawed the homeowner isn't going to want danger and warning stickers placed on the cupboard doors I can see it now "This cupboard door must remain locked while the bath or shower is in use".
User complacency IMO is the biggest danger here and safety can so easily compromised when whatever solution is adopted or agreed on is degraded over time and is eventually forgotten that is when someone is injured or becomes a fatality and questions are asked as to why it was done like that and why was it not rectified when the problem was highlighted
 
The CU’s are in a wall unit, any self respecting kitchen/bathroom furniture installer (think that’s the right title) would tell you that 🙂. So they are not in a cupboard, so that negates that part of the debate.
 
Can the CU and related controls be reasonably operated without standing in the bath?

I know lots of dumb things have been done in the past, but if this was a new build then surely the needs of disabled (or elderly with limited mobility) access would also make such stupid unusual choice of location a no-no?
 
Was that always the bathroom?

Looking at the size of the CU I'm guessing it is a large property, so I wonder if a utility room has been converted in to a bathroom. The cabinet looks like it was added afterwards to me as neatly cut (is still a stupid approach) and if the CU was put there then I would have expected it on top of the back-board.

Dumb either way!
 
Last edited:
Wonder how big the bathroom is, as it seems a big property ?.

Relocate the socket outlet 2.5 m away from the bath.
 
An outlet socket on a landing directly outside a bathroom door less than an MTR away would be compliant as it's behind a door.

An airing cupboard with electrical heating etc in a bathroom behind a door is compliant.

Electrical equipment under a bath is also compliant.

An electric shower which has just a plastic cover and also has uninsulated connections inside is also compliant.

Because is behind a barrier, it's technically not in a zone.

If not in a zone, then IP rating etc shouldn't be an issue. ?
You're making some really good points.

None of us on here, I hope, would install this CU in this location but we may be put in the situation of advising someone on "is it safe/compliant".

The vast majority of my work is commercial and the answer is always pony up and put it right. One example was a national storage company that decided to have showers fitted in all their sites mostly in the disabled WC, don't know who did it but very few of the showers were RCD protected and none of the other circuits pressent in the room were. So that's lights, whatever random circuits passed through he rooms. In the end most the showers were disconnected.

I can see why domestic solutions have to be a little more creative, the customer may not have the money to fully correct and a significant safety improvement will be better than no action. Just make sure you offer the full correction in writing.

In this case I'd quote for the CU to be moved to a compliant location. Get their refual in writing, email is a powerful tool, before suggesting the socket is removed and the door to the cupboard should be screwed shut, a lock will just be removed and left off, but then the CU is not easily accessible I the event of a trip.

What a mess, don't envy domestic sparks.
 
Very interesting thread and many of the comments are extremely pertinent, however I am just astonished that anyone would install that CU in that location. No matter what technical justification might be relevant, it's just a bad installation idea.
A few years ago I was doing some work on a new-build housing estate where all the houses had the CU installed at high level in the downstairs cloakroom. This was a mainstream builder and I am aware the same installation was carried out on other estates. Now, I accept the cloakroom had no bath or shower, but the only way to gain access to the CUs in these houses was by standing on the WC...there's no room to place a ladder or hop-up. I accept these houses passed BC regulations, but in my opinion the CU should not be mounted high up above a WC. A less-able person would find access extremely tricky and indeed hazardous, and for that reason alone it shouldn't be allowed.
It is without doubt wuckfittery of the highest order and Its not as rare as it should be.
 
Besides all else, I would definitely call it dangerous.... having to work on a consumer unit, balancing with one foot on each edge of that bath. 😮 😉
Good point .Safe direct access should be important . Looked at job yesterday .New luxury conversion .CB is about 8 foot high and super close to the top of the stairs . Its just daft
 

Reply to Consumer unit in bathroom in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
521
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
1K
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
2K

Similar threads

At some point, all sewage pumps will fail, or need extensive maintenance. I make it quite clear that I'm not interested in either.
Replies
16
Views
1K
I opened up the CU again and the round junction box above and what I found was the blue and brown wires coming in from the wall just above the 15a...
2 3
Replies
33
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top