Hi everyone.
I have been asked to relocate a consumer unit from a cupboard outside a house into the inside of the property. The main fuse and meter will be remaining outside however the run is about 6/7 metres long, i believe it states in BS7671 that the meter tails cannot exceed 3m in length.
would this require me to put a separate fused connection unit within the 3m of isolater and then run a 25mm SWA + 16mm earthing conductor from the fused connection unit, to the 6/7m away consumer unit location? If not who knows a better way?
thanks, chris.
 
at the foot of the NAPIT document linked above

"Conclusion Other methods of determining the maximum demand can be used with the values selected being the responsibility of the installation designer or a suitably qualified electrical engineer."

Yup - like the one outlined by the IET is completely irrelevant these days with fuseboards typically having more breakers ......
 
Hi Everyone, i have decided to install a 25mm 3 core SWA from an 80a FCU like the one shown here
Wylex Domestic Switch Fuse 80A - https://www.toolstation.com/shop/Electrical/d190/Wylex+Consumer+Units/sd2615/Wylex+Domestic+Switch+Fuse/p51068

However the earth terminal on the FCU can take a maximum of 16mm. 16mm is fine for the main earth CSA but the cores are all 25mm for the L+N tails..

Can i use a 2 core 25mm SWA and use the cable sheath for the sub main from FCU?

If only there was a 2x25mm/1x16mm SWA!

Anyone have any suggestions?
 
Anyone have any suggestions?

Maybe something like this.
[ElectriciansForums.net] Consumer unit to be moved away from service head
 

Reply to Consumer unit to be moved away from service head in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
438
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
1K
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

This was posted this week, on topic ....... https://niceic.com/newsletter/omission-of-overload-protection/?dm_i=7G1W,7GCE,K4L2A,WHET,1
Replies
8
Views
733
I would hazard a guess your electrician may be able to contact your DNO and have the switch swapped to a MFS very quickly..
Replies
13
Views
665

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top