Hi everyone.
I have been asked to relocate a consumer unit from a cupboard outside a house into the inside of the property. The main fuse and meter will be remaining outside however the run is about 6/7 metres long, i believe it states in BS7671 that the meter tails cannot exceed 3m in length.
would this require me to put a separate fused connection unit within the 3m of isolater and then run a 25mm SWA + 16mm earthing conductor from the fused connection unit, to the 6/7m away consumer unit location? If not who knows a better way?
thanks, chris.
 
Yes i havent ap

Ah my mistake ive just added the rating of the MCBs up
The old school rule of thumb is to exclude the highest rated circuit breaker, add up up the rest of the circuit breakers, times this figure by 0.4 and add this figure to the rating of the highest rated circuit breaker you excluded.
 
Yes i havent ap

Ah my mistake ive just added the rating of the MCBs up
The old school rule of thumb is to exclude the highest rated circuit breaker, add up up the rest of the circuit breakers, times this figure by 0.4 and add this figure to the rating of the highest circuit breaker you excluded.
 
What is the main REC fuse rating 100A? if so need 100A metal switch-fuse with 80A fuse.

Not a dig Chris but thought that you would have learnt regarding diversity prior to you doing 17th and 2391.
Yes main fuse rating is 100A, thank you.

And i know it wasnt a dig! I work for a housing association and havent done any maximum demand calculations since my college days.
 
Yes main fuse rating is 100A, thank you.

And i know it wasnt a dig! I work for a housing association and havent done any maximum demand calculations since my college days.
Fair enough as said Pete said no profile anyway know where you're coming from now and yes if not doing all the things learnt at college you soon get rusty no offence meant Chris.
I would run a three core SWA the only thing if you are using 25mm is that the core that you are using for the earth it fits in the main earth terminal.
 
Fair enough as said Pete said no profile anyway know where you're coming from now and yes if not doing all the things learnt at college you soon get rusty no offence meant Chris.
I would run a three core SWA the only thing if you are using 25mm is that the core that you are using for the earth it fits in the main earth terminal.
Yes i only made this the other day i am yet to fill in all the details, will get round to it soon.
Yeah the supervisors do all the drawings and calculations so the rust appears to have set in haha! No offence taken.
That was my thought too im almost certain it will be too large for the MET i may have to figure something out for that.
 
The old school rule of thumb is to exclude the highest rated circuit breaker, add up up the rest of the circuit breakers, times this figure by 0.4 and add this figure to the rating of the highest circuit breaker you excluded.

That sounds just as ridiculous as Appendix A in the OSG :)
 
I've not come across a 'standard' house yet that can't live on 16mm and 60A, even big ones. Max demand calcs are a pita, you can talk yourself into all sorts of absurd figures, but the reality is that these scenarios never arise, and on the off chance that they do, the dno aren't daft enough to let your error damage their network beyond the fuse in the cutout.
 
Yes i only made this the other day i am yet to fill in all the details, will get round to it soon.
Yeah the supervisors do all the drawings and calculations so the rust appears to have set in haha! No offence taken.
That was my thought too im almost certain it will be too large for the MET i may have to figure something out for that.
you can fit a reducing lug.
 

Reply to Consumer unit to be moved away from service head in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
381
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
961
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

This was posted this week, on topic ....... https://niceic.com/newsletter/omission-of-overload-protection/?dm_i=7G1W,7GCE,K4L2A,WHET,1
Replies
8
Views
722
I would hazard a guess your electrician may be able to contact your DNO and have the switch swapped to a MFS very quickly..
Replies
13
Views
660

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top