O.S.G.. The use of other methods’ of determining Maximum Demand is Not Precludedwhere Specified by the Installation Designer

FirstlyI make no Apologies for the Way am Writing on any Matters . it can be a first day Apprentice or some one Needing aJog of Memory .
Sowe are all in the Same Boat . “ To Learn “

For the Apprentices . The Day we stop learning is the Day we hang Upour Tool-Bag

CookerDesign Current Calculations

Thefirst thing you have to do is get Your Head around the Calculations !!

(From a Design point of View ) 2392-10

DomesticInstallation Oven(s) & Hob(s) are to be Calculated upon their MAXIMUM LOADING
Startwith a simple Calculation ( An Oven has a rating of 2kW ) 2000

(I = P/V ) Formula … I = 2000 ÷ 230V = 8.70A …. Weare Using the Unit Amps


2392-10/ Domestic Installation Oven(s)

Ovenhas 4 Rings ( 2 x 1kW ) & ( 2 x 1.5kW ) & Grill ( 2kW ) & Oven (3kW )

-Controlled via a CookerSwitch with a Socket outlet .

Asa Designer . we’ll have to Apply Diversity ??

Important )- Diversity allowance to be Applied to the FULL LOAD CURRENT for CookingAppliances .

TheO.S.G. is telling us . Purpose of the Final Circuit fed from theConductors )
O.S.G.Table 1B p/97 – column (3) Cooking Appliances → At the Top of the Page Note : Type ofPremises ( 2392-10 → Household Installations ) Domestic Installation(s)

DomesticInstallation(s) Only O.S.G. - 10A + 30% f.l – Full Load ) of connected Cooking Appliances in the Excess of 10A+ 5A if a socket-outlet is incorporated in the Control Unit . ( C.C.U. ) – 45A + 13A Socket Switched with Neon .

Fromyour point of View ( The First 10A ofthe rated current plus 30% of the reminder ( Plus) 5A if the Control Unit incorporates s Socket.

Calculations)- You bank “ Hold OFF“ the first 10 Amps of the Maximum Load Current )
The10A will be used at the End of the Calculations’

-So your Work out the Total Power Rating & then calculate the Full Load Current

Calculations)- Power = ( 2 x 1 ) + ( 2 x 1.5 ) + ( 2+ 3 ) = 10kW

I= 10000 ÷ 230V = 43.48A … round it up to the first four numbers43.47826087 ( 48 ) 43.48A

UsingDiversity allowance stated ↑↑ ( 43.48A sub 10A = 33.48A )

I= 33.48 x 30 ÷ 100 = 10.04A

Youradding the ( 5A ) for Socket outlet . I = 10A + 10.04 + 5A = 25.04A )- Asa Designer this is your Expected Current Demand .

Remember )- Supply Cables Rated to suit DesignCurrent ( Iz ) :)
 
Re: Continued Useful Information for Electricians’ & Apprentices

“ Meaning “ Instantaneous :

O.S.G.Table 1B – column 5
Water–Heater(s) Instantaneous

Instantaneouswater heaters heat Only the water that is needed .
Thisis done by controlling the flow of water through a small water tank which hasheating elements inside it
Themore restricted the flow of water then the hotter the water becomes . Thetemperature of the water can therefore be Continuously Altered or Stabilisedlocally at whatever temperature is selected .

TheShower-type water heater must be supplied via its OWN MCB in the ConsumerUnit - Double pole isolator “ as a rule“ located near the shower .

Thereare Two-main methods of heating Water Electrically
Eitherheating a large quantity stored in a Tank or Heating only what is required whenit is needed .

•Non-pressure .
Non-pressurewater heaters . which are typically rated at ( Less than 3kW & contain Lessthan 15 litres of water ) Heat water ready for use & are Usually situateddirectly over the sink

WaterHeating Control . ( must have a Functional Switching Device for Convenience )

BS-7671some references
Regulations554.3.3. )- An Immersion Heater must be connected to the supply by Double-polelinked Switch Only . The use of a plug top & socket outlet is Not permitted
Note: No change for 16[SUP]th[/SUP] Edition to the 17[SUP]th[/SUP] Edition 2008 –Red Cover

Regulations554.2.1. )- An Immersion Heater must be Provided with a Thermal Cut-Out toprevent the water from boiling if the thermostat fails .

ImmersionHeaters should be supplied through a Switched Cord-Outlet Connection Unitcomplying with BS-1363-4 .
BS– 1363-4 )- Specification for 13A FusedConnection Units – Switched & Unswitched .

TheRing Final Circuit :
RedCover . BS-7671:2008. makes the following reference to Ring Final Circuits .

RingFinal Circuit must Not supply an Immersion Heater . Storage Heaters etc . 433.1.5.
TheRing Final Circuit Arrangements . p/362 .
(ii)Not supplying ImmersionHeater(s) . comprehensive Electric Space Heatingor Loads of a Similar profile from the Ring Circuit

Regulations314.2 )- All Final Circuits must be wired Separately from all Other Final Circuits
 
Re: Continued Useful Information for Electricians’ & Apprentices

Earth Loop Impedance ( EL-Z ) Test

This is a Live Test:

The Main Power has to be Energised to carry outthis procedure . There a certain amount of information required .as a rule thisTest is straightforward
{ Three-prong Test } if was carried out on alighting circuit you would be required to connect to the Line . Neutral . Earth.

Example : were Testing on the Ring Final circuit .What will be measured is called the Maximum ( Zs ) or the Measured ( Zs ) itshould be compared to the Maximum ( Zs ) in BS-7671:2008 .
so Prior to Testing it is Important to known whichCircuit-breaker is protecting the circuit to be Tested . { in this case it willbe an RCBO to BS-EN61009-1 Rated at 32A }

Look in the Regulations BS-7671 page 49 table 41.3– the maximum ( Zs.s ) you must obtain a reading which is a reading less thanin this case it is 32A - 1.44Ω . it is Important to Note when Testing youshould obtain less than 80% of the figure . Sousing a calculator 1.44Ωs x .8 = we are looking for 1.15Ω

We are looking for LESS THAN [ 1.15Ω < ] With the Instrumentplugged into the furthest socket ↔ The Loop Scale .
Test is taken & a reading of [ 1.1Ω ] → Less than the Maximum value .
 
Re: ***Cont../ Useful Information for Electricians’ & Apprentices***

Symbol \ : Therefore. ◄ Electrical Therefore [\Sometimes used in proofs beforeLogical ] – Therefore : so : hence . Therefore : it follows –that .
Symbol ¥ : What is it ? Infinity – as a Tester you will use this a lot
 
Re: ***Cont../ Useful Information for Electricians’ & Apprentices***

Mineral Insulated Copper Conductor “ Pyro “

Orange : General use .
Red : Fire Alarms .
White: Emergency Lighting .
 
Re: ***Cont../ Useful Information for Electricians’ & Apprentices***

The Basics .

Ib)– term used to describe a circuit’s design current in Amp’s . ( TheLoad )
In)– term used to describe a circuit’s Protective size in Amp’s ( MCB ) orfuses .
Iz)– term used to describe a circuit’s value . in Amp’s once all de-rating factor have been considered .
It)– term used to describe the tabulated current rating of a cable in Amp’s .( The Current a cable can Safety Carry )

[ Ib ≤ In ≤ Iz ≤ It ]

The formula above states the Underlying principle of the calculation of a circuitscable size .
The first factor you need to consider is Design Current. ( Ib )
 
Re: ***Cont../ Useful Information for Electricians’ & Apprentices***

Inspection& Testing – 2391-10 / Designer

TheCertificate couldbe used in a Court of Lawto prove the competence of the Electrical Tester should anything happen at alatter date . if we were to certify an Electrical Installation that would laterresult in damage or harm to persons or property we would Require Proof that we carried outa Full Inspection & Test in accordance with BS-7671:2008 which would satisfythe Electricity at Work Act . The legalities ofour responsibilities are that we are guilty until proven innocent . So havingcorrect paper work & Test Records could save your neck .
 
Re: ***Cont../ Useful Information for Electricians’ & Apprentices***

Remember . if any of the Initial Verification Checks require you to Remove Covers then you will need to Carry Out Safe Isolation .
Otherwise you will CONTRAVENE the ELECTRICITY at WORK ACT
 
Re: ***Cont../ Useful Information for Electricians’ & Apprentices***

Keeping Circuits inOrder .

BS-7671:2008.
Regulations314.1. (i) & (ii) states that every Installation shall be divided intoCircuits to avoid Danger & minimise Inconvenience & to facilitate safeoperations . Inspection . Testing & Maintenance .

( T ) Regulation 514.1.2.
Statesas far as reasonably practicable . wiring shall be arranged or marked that itcan be Indentified for Inspection . Testing . Repair or Alteration of theInstallation .


 
Re: ***Cont../ Useful Information for Electricians’ & Apprentices***

BS-7671:2008.
Makes the following reference to Ring Final Circuits .

Regulation132.12 )- All Electrical Equipment must be )- Accessible for Operation . Inspection & Testing . Fault detection. Maintenance & repair .
Regulation 411.3.3. )- Unlessspecifically labelled or suitably Indentified . All 13A socket outletsmust be 30mA – RCD protected .
Regulation 543.2.9. )- Except where the Circuit Protective Conductor is formed by a MetalCovering or Enclosure containing all of the Conductors of the Ring .The Circuitprotective conductor of every Ring Final Circuit shall also be run in the formof a Ring having BothEnds connected to the Earthing Terminal atthe Origin of the Circuit.

Apprentices. Top Page Note : “ Wording “ Informative . ◄◄
Apprentices. Read the Wording ) p/362 . Ring FinalCircuit Arrangements . Regulation 433.1.5.
TheLoad current in any part of the circuit should be unlikely to EXCEED for LONG PERIODS the Current-Carrying-Capacity of the cable .
Regulation433.1.5 – refers )- This can generallybe Achieved BY

Regulation 433.1.5. )- Appendix 15 p/362 . Note : Informative . Cookerrated more than 2kW .

ARing Final Circuit must not serve a floor Area Greater than ( 100m[SUP]2[/SUP]) p/362 .. PS Ring – 100m[SUP]2 -[/SUP]32A
Regulation 433.1.5. p/362 )- A Ring Final Circuit mustStart & Finish in the Consumer Unit & be connected to ( 30A / 32A ) MCB etc .
Regulation 433.1.5. p/362 )- The minimum C.S.A. of theLine & Neutral conductor is 2.5mm[SUP]2 [/SUP] . The minimum C.S.A. of the CPC is 1.5mm[SUP]2 [/SUP]
Regulation 433.1.5. p/362 )- An Unfused Sur can feedeither One Single or One Double outlet only & can be taken from the MCB inthe Consumer Unit .
Regulation 433.1.5. p/362 )- The number of Spurssupplied from a Fused Spur connected unit ( a Switched Fused Spur ) depends on the size of the Fuse in the Fused connection unit .
Regulation314.4. )- All FinalCircuits must be wired separately from all other Final Circuits .
Note : O.S.G. IB )- Top of the Page. Purpose of the Final Circuit fed from theconductors . ETC.

O.S.G.p/18 )- Socket Outlets must be spaced at least 150mm away from Gas-pipes unlessthere is a plane of Non-combustible Insulating Material Separating them .
O.S.G.p/54 )- Lengths of Unfused Spurs off a Ring Final Circuit should not generallyExceed ( 1/8 ) the cable length from the Spur to the furthest part of theRing
O.S.G.p/54 )- The Wording : As a Rule of Thumb for Rings . Unfused Spur lengths ETC. ( 1/8 )
 
Re: ***Cont../ Useful Information for Electricians’ & Apprentices***

Conduit Capacities . Basics

To calculate the number of Cables that may be draw into a Conduit .

O.S.G.You make use of the FOUR Tables

Table5A – Cable factors – conduit for short straightruns up to ( 3m )
Table5B – Cable factors – Use in short straight runs up to ( 3m )
Table5C – Cable factors – for long short straight over ( 3m ) or runs of any lengthincorporating bends .
Table5D– Cable factors – conduit factors for conduit incorporating bends & long straightruns

AllCables are Stranded . ( there are Two types of Cables in use Solid or Stranded )

Example:
Conduit25 metres long without bends with ( 3 x 1.5mm[SUP]2[/SUP]& 3 x 2.5mm[SUP]2 [/SUP]Stranded conductors )

a) Select the correct table for the cable factors & conduit ( 5A )
b) Obtain the cable factors for each size of cable ( 1.5mm[SUP]2 [/SUP] = 31 & 2.5 mm[SUP]2 [/SUP] = 43 ) → ( 5A )
c) Multiply the number of cables by the factor ( 3 x 31 ) +( 3 x 43 ) = 222
d) Select the correct table for the conduit factor & length of run ( 5B )
e) Obtain the factor which is greater than the sum of cable factor(s) ( 20mm = 460)
f) The conduit size is 20mm .

O.S.G.Trunking Capacities : & Tables from “ BS-7671 “

Minimum trunking size is calculate in much the same way conduit although trunking hasits own Table .
O.S.G.– No consideration is paid to the Length of Run .

Firstlyf or Exam - &- maximum allowable 45%space factor .

Table 5E O.S.G. - Cable factors for Trunking .
Table 5F O.S.G. – Factors for Trunking .

Trunking with 100 x 1.5mm[SUP]2[/SUP] & 100 x2.5mm[SUP]2[/SUP]

a) Obtain the cable factors for each size & type of cable ( 1.5mm[SUP]2[/SUP] = 8.6 & 2.5mm[SUP]2[/SUP] = 12.6 … ( P.V.C. Cable factor ) → Stranded Cable
b) Multiply the number of cables by the factor ( 100 x 8.6 ) + ( 100 x 12.6 ) = 2120
c) Obtain the factor which is greater than the sum of cable factor(s) ( 75 x 75 =2371 )
d) The Trunking size is ( 75mm x 75mm )
 
Re: ***Cont../ Useful Information for Electricians’ & Apprentices***

O.S.G.
Apart from Indicating that Diversity & Maximum Demand must be assessed . The Regulations themselves gives little help on calculations’ .

In BS-7671:2008 ( 17th Edition ) Regulation 311.1 gives requirements for the assessment of requirements of Maximum Demand . etc. determining the maximum demand have to consider Diversity .

• Water Heater(s) Thermostatic
( 2 x 6kW & 7 x 3kW ) Table 1B states “ No Diversity Allowable “

Small Shop ??
So the Total load will be .
P = ( 2 x 6kW ) + ( 7 x 3kW ) = 12 + 21 = 33kW → I = 33.000 ÷ 230V = 143.47A ( Unit in Amps )

( 2 x 6kW ) = 12
( 7 x 3kW ) = 21

• Ring Circuit(s) 8 x 32A
O.S.G. Table 1B states “ 100% of the largest & 50% of remained “ The Total Load ??
Table 1B Colum 9 ( Next column across 100% / 50% )

First Ring ( I – 32A ) PS … Not Domestic Installation(s)
Remaining Ring Final Circuit(s) ( I = 7 x 32A = 224A x 50% ÷ 100% = 112A ( Total for Ring Final Circuit(s) = 144A

Table 1B Colum 9 ( 100% / 40% - for Domestic Installation(s) 2392-10 Domestic Installation(s)
Ring Final Circuit – Full Demand on First Circuit → MCB is 32A . ( Then add 40% of remaining ) The two Ring Final Circuits are on 32A MCBs
After Diversity = 32 + ( .4 x 32 = 12.8 ) = 32 + 12.8 = 44.8 Amps . [ 40% for rest of Socket Outlets ]

The Term → ( MD ) Maximum Demand . is self-explanatory . it simply the sum of all the Individual Loads to be connected for a Simultaneous & Significant period .
 
Re: ***Cont../ Useful Information for Electricians’ & Apprentices***

Inspection& Testing “ Overview “ 2392-10

Youwill need to demonstrate “ Assessor “

- Carryout an Initial Inspection of the Installation .
- Selectcorrect Instrument(s) to carry out Tests .
- Completethe Correct Sequence of Tests .
- Record the Test ResultsObtained .
- Carryout Functional Testing of an Installation .
- Fill in recognised Certificatesof Completion .

KnowledgeRequirements – 2392-10

• Howto Carry out an Initial Inspection .
• Howto Correct any Deviationsfound during Inspection .
• Howto use Various Test Instruments .
The Importance of the Sequence of Tests .
• Howto carry out Functional Testing
• Howto Document Inspection & Testing .

Whatwould you do if you Discover Unsatisfactory Test Results . ??

ThePurpose of Inspection & Testing is to PROVIDE . So far is reasonably practicable.

• Thesafety of Persons & Livestock .
132.1. Design – The Electrical Installationshall be designed to prove .
i)The protection of Persons . Livestock & Property . ETC.
ii)The proper Functioning of the Electrical Installation – for the Intended USE .

•Protection against Damage to Property by Fire &Heat arising from an InstallationDefect .
•Confirmation that the Installation is NOT Damaged or Deteriorated so far as to ImpairSafety .
• TheIdentification of Installation Defects & Non-compliance with the Requirementsof the Regulations which may give Rise to Danger .

Inspection& Testing . 2392-10
During & or on Completionof a New Installation

Withthat in Mind ? 2392-10
Youhave to Satisfy the Requirements of Part P of the Building Regulation(s)
 

Reply to ***Cont../ Useful Information for Electricians & Apprentices*** in the Australia area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
271
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
770
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
776

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top