O.S.G.. The use of other methods’ of determining Maximum Demand is Not Precludedwhere Specified by the Installation Designer
FirstlyI make no Apologies for the Way am Writing on any Matters . it can be a first day Apprentice or some one Needing aJog of Memory .
Sowe are all in the Same Boat . “ To Learn “
For the Apprentices . The Day we stop learning is the Day we hang Upour Tool-Bag
CookerDesign Current Calculations
Thefirst thing you have to do is get Your Head around the Calculations !!
(From a Design point of View ) 2392-10
DomesticInstallation Oven(s) & Hob(s) are to be Calculated upon their MAXIMUM LOADING
Startwith a simple Calculation ( An Oven has a rating of 2kW ) 2000
(I = P/V ) Formula … I = 2000 ÷ 230V = 8.70A …. Weare Using the Unit Amps
2392-10/ Domestic Installation Oven(s)
Ovenhas 4 Rings ( 2 x 1kW ) & ( 2 x 1.5kW ) & Grill ( 2kW ) & Oven (3kW )
-Controlled via a CookerSwitch with a Socket outlet .
Asa Designer . we’ll have to Apply Diversity ??
Important )- Diversity allowance to be Applied to the FULL LOAD CURRENT for CookingAppliances .
TheO.S.G. is telling us . Purpose of the Final Circuit fed from theConductors )
O.S.G.Table 1B p/97 – column (3) Cooking Appliances → At the Top of the Page Note : Type ofPremises ( 2392-10 → Household Installations ) Domestic Installation(s)
DomesticInstallation(s) Only O.S.G. - 10A + 30% f.l – Full Load ) of connected Cooking Appliances in the Excess of 10A+ 5A if a socket-outlet is incorporated in the Control Unit . ( C.C.U. ) – 45A + 13A Socket Switched with Neon .
Fromyour point of View ( The First 10A ofthe rated current plus 30% of the reminder ( Plus) 5A if the Control Unit incorporates s Socket.
Calculations)- You bank “ Hold OFF“ the first 10 Amps of the Maximum Load Current )
The10A will be used at the End of the Calculations’
-So your Work out the Total Power Rating & then calculate the Full Load Current
Calculations)- Power = ( 2 x 1 ) + ( 2 x 1.5 ) + ( 2+ 3 ) = 10kW
I= 10000 ÷ 230V = 43.48A … round it up to the first four numbers43.47826087 ( 48 ) 43.48A
UsingDiversity allowance stated ↑↑ ( 43.48A sub 10A = 33.48A )
I= 33.48 x 30 ÷ 100 = 10.04A
Youradding the ( 5A ) for Socket outlet . I = 10A + 10.04 + 5A = 25.04A )- Asa Designer this is your Expected Current Demand .
Remember )- Supply Cables Rated to suit DesignCurrent ( Iz )
UsefulJunk :
IP56Protection .
Eachdigit in an ( IP ) Ingress Protection rating denotes résistance to Dust &Water . IP56 rating breakdown as follows .
IP- Ingress Protection
(5 ) Dustproof to sawdust . Dust & other Small Partials .
(6 ) Waterproof to Strong Jets of water .from any Direction .
Gardens. Workplaces / Shops . Industry . Farm buildings . Swimming pools . Squash courts . Gyms . ETC
IP- Ingress Protection
IP66. Offers total Dust Ingress Protection . & is protected againstHigh-Pressure Jets from any Direction .
UsefulJunk bulbs
whydoes light bulbs blow ?
Whydoes the Circuit Breaker trip ?
TheCircuit Breaker does not trip because a broken filament has dropped onto a leadout wire as some people would have you believe but is due to the gas orfilament in the lamp becoming Ionised . The hightemperature & large electric field can cause the gas to go into a CONDUTIVE STATE & the plasma will spread until it SHORTS OUT the lead wires
Useful Junk “ Wording “ The Humble light switch .
“ Gang“
Means there are more than One Switch on a singlefitting .
“ Way“
Means that the switches will operate from two or morelocations . i.e.
•What isthe current rating of a Switch ? The maximum Currenta Switch is designed to Carry !
•What isthe Voltage rating of a switch ? The maximumVoltage allowable in the circuit in which the switch is installed . 230V
Testing - ►► A common trick question in any ExamPaper(s) 2391-10 / 2392-10 -&-s
►►►►► ( Making you aware - The x5 test is ( N/A )for Anything BIGGER than ( 30mA ) RCD / ADS ☜
Testcurrent at )- 5 I∆n . The maximum testtime not be longer than )- 40mS “ Answer“ Device shouldoperate in less than 40mS
( 500 is x5 ) I will give it its full title )- x5 I∆n ≤ 30mA Deviceshould operate in less than 40mS -&-sOut of this . there three Questions in here
The point of all this is ( ThisForum will help you as much as possible 99.9% ) We all Love -&-s . Yeah
2392-10Question ?? -&-s
Asa Competent Person ) Tester to be .-&-s are judging you on this matter .
Amusing the Wording ( Testing – full stop )
ARCD must be Tested . ( No excuses )The Regulations are telling us . Therequirement(s) are stated in thefollowing Regulation ??? Where !!
TheEffectiveness of the RCD must be Verified by a TEST SIMULATING an APPROPRATEFAULT CONDITION ) – Full stop “ Push the Button “ ◄◄
Regulation 612.13 )- Functional Testing ◄◄
► Do not Mix up the two Regulation(s) 612.13 )- 612.10 ) ← ← ← ← ← ← ← ← ← ← ← ← ← ← ←
(Megger 1552 – out at this stage ) Regulation 612.10– Wording on this matter is.
( Visual Inspection is the First line of Defence ) Eyes
AdditionalProtection ( ADS ) The Verification of the Effectiveness of the measuresapplied for Additional Protection is Fulfilled by VISUALINSPECTION & TEST
RCDs shall be VERIFIED using SUITABLE TESTEQUIPMENT According to BS-EN 61557-6 …… ( Megger 1552 – out at this stage )
Thiswill take you to Regulation 612.1 . p/157
MeasuringInstruments & Monitoring Equipment & Methods shall be chosen inAccordance with the relevant parts of BS-EN 61557.
Youwill be Complying with Chapter 41 ( will be met )
Chapter41 – Protection against Electric Shock (Plain English is the RCD working to BritishStandard ? is it Safe . The Manufacture say there have tested it – all you doing covering you But . the other way of looking at this is “ The public will be Safe “
I don’twant to Harp on .
Remember“ RCDs – BS – 200mS -&-s ………………….. Still in Use
Remember“ RCDs – BS - EN 300mS -&-s
TestInstrument :
Whatthe Regulation(s) are saying – The Test instrument used to Test RCDs should becapable of applying the FULL RANGE of TEST CURRENT ( BS-EN 61557 )
-&-s Question ?? The Test Current should be APPLIED for NO longerthan ( 2 seconds ) Your Answer
Must dash of to the Wholesalers now . Amber
Justa point to Note here : RCDs Range of Tests
Whilethe following Tests are NOT a Specific requirement of BS-7671:2008 . it is recommended that they are carried out
Regulation(s)Table 61. p/158
( IR ) Insulation Résistance
≥ 0.5MΩ for SELV & PELV with D.C. you Test voltage of 250V -&-s 100%
≥ 1.0MΩ for systems up to & including 500V with a D.C. testvoltage of 500V &-s 100%
Workingmy why around the Regulations .
i)– RCD Table . performance criteria for RCDs to BS-EN 61008-1 & BS-EN 61009-1
Regulations:
Table3A . p/243
RCDswhich are identified in Two Main groups or Types of Delay .
Without time delay ( Classedas General Use )
With time delay ( Classed asType S for selectivity )
A 300mA RCD – is Only intended for Equipment & Fireprotection . -&-s ( Fireprotection )
Table( 12A ) P/358
ForDesign purposes )- “ Informative “ wecan class this as . Voltage Drop Table (Maximum 3% Lighting / Maximum 5% forother uses when the circuit is supplied from a public Low Voltage DistributionSystem
Calculations)- 3% of 230V = 6.9V ….. 3x 230V ÷ 100 = 6.9V
Calculations)- 5% of 230V = 11.5V ….. 5 x 230V ÷ 100 = 11.5V
If-&-s was to ask you a Question )- What is the Maximum Volt drop on aLighting Circuit ?? 5%
Apprentices. Designer(s) in the Making
Table41.1 - what the Regulations are sayingis )- Maximum Disconnection Time . 2392-10
TN- ( 120V < Uo ≤ 230V ) 0.4 seconds
TT-( 120V < Uo ≤ 230V ) 0.2 seconds ( PS now the catch .411.3.2.2. – Final Circuits’ NOTEXCEEDING 32A ◄◄◄ -&-s . this willgo around
( Final Circuit . is different from Ring Final Circuit (s) still NOTEXCEEDING 32A ◄◄◄ Watch their Wording .
Example)- Maximum Disconnection Times . Permittedby the 17[SUP]th[/SUP] Edition – for A.C. circuits’ of ( Nominal Voltage (Uo) 230V to Earth .
( 0.2s ) ( 0.4s ) ( 1s ) & ( 5s ) → ( 0.4 s being the most common inTN- systems – 0.2s in TT )
Apprentices – Regulations p/35 Symbols used in the Regulations ( Uo – Nominal a.c. rms Voltage to Earth . ( V ) … 41.1 . MaximumDisconnection times .
Designing.
41.2 to 41.5 )- Values for Maximum Earth Fault Loop Impedance ( Zs )
Designing.
41.5)- Providing Maximum Earth Fault Loop Impedance ( Zs ) values for RCD
Designing.
p/103- 52.1 )- Providing maximum operating temperaturesfor type of cable Insulation .
Thermoplastic / 70°C ) Temperature limit ↔ Thermosetting / 90°C ) Temperature limit
90°C) Temperature limit ( b)
Wherea conductor operates at a temperature exceeding 70°C it shall be ascertainedthat the equipment connected to the conductor is suitable for the resulting temperatureat the connection .
Designing.
p/104– 52.2 )- Cable surrounded by Thermal Insulation . O.S.G. P/125 Table 6B
Testing purposes . p/117 – 53.2
Guidanceon the selection of protective ( Isolation & Switching Devices )
BS-EN 61009-1 .. General RCD
BS-EN 61008-1 .. General RCD
BS-EN 61008-1 ( RCCBs ) General
BS-EN 61009-1 ( RCBOs ) General
BS-4293 ( RCCBs ) General
BS-7288 ( SRCDs ) General
BS-EN 61008-1 ( RCCBs ) Delay ( S )
BS-EN 61009-1 ( RCBOs ) Delay ( S )
BS-4293 ( RCCBs ) Delay ( S )
RCD)- 0.5I∆n Test should also be carried out ( Tocheck for Unwanted Tripping )
Apprentices. “ Reasons “
AdditionalProtection . the 17[SUP]th[/SUP] Edition make a good point here ?? ( ADS ) using there Words Additional Protection Ring Final Circuit 30mA = 40mS
Inthe UK they Sell Electrical Equipment ( ghd – HairTongs £ 100 pounds plus ) Theseconversion plugs enable ( 2 – pin ) Europlugs to be connected to a standard UK 13A Socket outlet . inthe UKthey do not have a Fuse in the conversion plugs ( so there relaying on ( ADS )
Made in China – 50 / 60 Hz - 150W
Your Mans an Electrician (this is the second pair of ghd – my good ladyhas came home with the cable insulation has melted away in the middle of thecable ) Yes I can fix them ! right in the bin
2392-10/ Leaning Curve .
Regulation536.2. Selectivity between Overcurrent Protective Devices . MCBs
Discrimination:
Whereselectivity between Overcurrent Protective Devices isnecessary to prevent Danger & where required for proper functioning of theInstallation .
( ManufacturersInstructions shall be taken into Account )
Regulation536.2. – “ Plain English “ Regulations is Demandingt hat .
Discrimination)- relates to all Faults . Short circuits . Faults between Line conductors & or Line to Earth Faults .
Regulation536.3. Selectivity between RCDs
Where selectivity between RCD is necessary to prevent Danger & where required forproper functioning of the Installation .
( ManufacturersInstructions shall be taken into Account )“Plain English “Regulations is Demanding that .
O.S.G.– Table 1A .
Currentdemand to be assumed for points of Utilisation & Current using Equipment .
Allother Stationary Equipment . British Standard rated current . or normal current .
( Consultthe Manufactures & / or the Standard & / or ratingplate )
ExternalEarth Fault Loop Impedance :
Regulation313.1 (iv) – Requires an assessment ofthe ( External Earth Fault Loop Impedance Ze ) of that part of the systemExternal to the Installation .
( from -&-s point of view . The Origin ofthe Installation )
Suitabilityof Supply :
Regulation313.1 (v) – Demands an assessment to bemade of the suitability of the Supply for the requirements of the Installation ( Including MaximumDemand )
Regulation 314.4. – 2392-10 as a Domestic Installer .
Thisis important . Each circuit to be electrically separated & connectedindividually & detached from all other circuits where they terminate in a ConsumerUnit .
Theconnections of each circuit Line(s) & Neutral(s) & Circuit protective conductors ( CPCs ) must follow a logical sequence at theirTermination in the Consumer Unit
One MCB Separate Way .
Importantto recognize that an Overcurrent Protective Device ( MCB ) or a ( RCD ) willnot provide Automatic Disconnection when human contact is made between Two LiveParts only . ( Line & Neutral ) an RCD mayAutomatically disconnect if contact is also made Simultaneously with Earth Parts
Thenwe go down the road of “ Touched Voltage“ 50V
ElectricShock under Fault Conditions is when contact ismade with an Exposed Conductive Parts . ( Metal Enclosures/ Class 1 item of Equipment )
( Whichis not live Under Normal Conditions but which has Become Live under EARTH FAULT CONDITIONS )
Workingmy way around the Regulations :
BS-7671:2008)- References to Accessories .
Regulation132.12 )- All electrical equipment mustbe assessable for operation . Inspection & Testing . ( Fault detection ) Maintenance& Repair
(Definitions ) A device . other than current using equipment . associated withsuch equipment or with the wring of an Installation .
“ PlainEnglish “ An accessoryis an item of electrical equipment that does not use anycurrent . Switches or a Socket outlet .
Regulation 421.7. & 526.5. )- Every termination . connection or jointbetween live conductors including the Neutral conductormust be made in a suitable accessory or enclosure
Regulation530.4.2. )- All Accessories must be fitted toan appropriate mounting box or enclosure .ETC.
Regulation 553.1.6. )- A wallmounted socket outlet must be mounted high enough above a floor or work surfaceto prevent damage to the flexible cord of the plug top
Regulation 553.1.6. )- Do Not Mix this up with Part P .
BS-7671does not give Specific Heights for Accessories .
Ifwe look at the ( Building Regulations )
Accessories must be mountedbetween 450 mm & 1200mm from the finished floor level . ETC.
Reply to ***Cont../ Useful Information for Electricians & Apprentices*** in the Australia area at ElectriciansForums.net
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
Good to know thanks, one can never have enough places to source parts from!
OFFICIAL SPONSORS
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...