O.S.G.. The use of other methods’ of determining Maximum Demand is Not Precludedwhere Specified by the Installation Designer

FirstlyI make no Apologies for the Way am Writing on any Matters . it can be a first day Apprentice or some one Needing aJog of Memory .
Sowe are all in the Same Boat . “ To Learn “

For the Apprentices . The Day we stop learning is the Day we hang Upour Tool-Bag

CookerDesign Current Calculations

Thefirst thing you have to do is get Your Head around the Calculations !!

(From a Design point of View ) 2392-10

DomesticInstallation Oven(s) & Hob(s) are to be Calculated upon their MAXIMUM LOADING
Startwith a simple Calculation ( An Oven has a rating of 2kW ) 2000

(I = P/V ) Formula … I = 2000 ÷ 230V = 8.70A …. Weare Using the Unit Amps


2392-10/ Domestic Installation Oven(s)

Ovenhas 4 Rings ( 2 x 1kW ) & ( 2 x 1.5kW ) & Grill ( 2kW ) & Oven (3kW )

-Controlled via a CookerSwitch with a Socket outlet .

Asa Designer . we’ll have to Apply Diversity ??

Important )- Diversity allowance to be Applied to the FULL LOAD CURRENT for CookingAppliances .

TheO.S.G. is telling us . Purpose of the Final Circuit fed from theConductors )
O.S.G.Table 1B p/97 – column (3) Cooking Appliances → At the Top of the Page Note : Type ofPremises ( 2392-10 → Household Installations ) Domestic Installation(s)

DomesticInstallation(s) Only O.S.G. - 10A + 30% f.l – Full Load ) of connected Cooking Appliances in the Excess of 10A+ 5A if a socket-outlet is incorporated in the Control Unit . ( C.C.U. ) – 45A + 13A Socket Switched with Neon .

Fromyour point of View ( The First 10A ofthe rated current plus 30% of the reminder ( Plus) 5A if the Control Unit incorporates s Socket.

Calculations)- You bank “ Hold OFF“ the first 10 Amps of the Maximum Load Current )
The10A will be used at the End of the Calculations’

-So your Work out the Total Power Rating & then calculate the Full Load Current

Calculations)- Power = ( 2 x 1 ) + ( 2 x 1.5 ) + ( 2+ 3 ) = 10kW

I= 10000 ÷ 230V = 43.48A … round it up to the first four numbers43.47826087 ( 48 ) 43.48A

UsingDiversity allowance stated ↑↑ ( 43.48A sub 10A = 33.48A )

I= 33.48 x 30 ÷ 100 = 10.04A

Youradding the ( 5A ) for Socket outlet . I = 10A + 10.04 + 5A = 25.04A )- Asa Designer this is your Expected Current Demand .

Remember )- Supply Cables Rated to suit DesignCurrent ( Iz ) :)
 
411. Protective Measure – Automatic Disconnection of Supply. ( ADS )

2392-10. Threecomponents . ◄► FaultProtection .

411.3.1.1. Protective Earthing .
411.3.1.2. Protective Equipotential Bonding .
411.3.2. Automatic disconnection in a Case of a Fault.

“ Second Digit “ [ IP ]
2 ] Protection against dripping water when tiltedup to 15% .
4 ] Protectedagainst splashing water .
5 ] Protected against water jets . .
6 ] Protected against heavy seas .
7 ] Protected against the effects of - [ Immersion]
8 ] Protectedagainst complete - [ Submersion ]

Definitions. for degrees of protection provided by enclosures of electrical equipment as:

i) Protection of person against access to hazardous parts inside the enclosure .
ii)Protection of the equipment inside the enclosure against ingress of solidforeign objects .
iii) Protection of the equipment inside theenclosure against harmful effects due to the ingress of water .








 
Protection Against Overcurrent .
Regulation. 131.4.

TheElectricity at Work Regulation 1989 =Part 11 . “ States “
That “ Efficient “ means . suitably located . shall be provided for protecting from “ Excess “ of current every part of the system as may benecessary to prevent danger .

Regulation . Reinforces this . 131.4. States that “ Persons & Livestock “ . shall be protected against injury. & property shall be protectedagainst damage .
Due. to excessive temperatures orelectromagnetic stress caused by Overcurrents . likely to arise in Live conductor’s .

2392-10: 131.2.2.. NOTE:
Inconnection with fault protection . the application of the method of protectiveequipotential bonding is one of the important principles for Safety .

ProtectionAgainst fault current :
Regulation. Reinforces this . 131.4. States that “

TheElectricity at Work Regulation 1989 =Part 5 . “ States “
That “ NoElectrical “ equipment shall be put into use where it’sstrength & capability may be exceededin such a way as may give rise to danger .

Regulation 131.5.
Whichrefers to any [ conductor(s) ] being able to carry fault current withoutgiving rise to excessive temperatures . ( inAddition )
Anyitem of electrical equipment intended to carry fault current shall be providedby mechanical protection against electromagnetic stress which could result ininjury or damage to persons . livestockor property . .

Niceone Bruce .
 
Hospitals’: 2011.

-&-s. Q) The connecting of a Mobile Generator ? . this may be achieved by a [ Plug-in-facility ] BS-EN-60309 - Socket
p/283: BS-EN-60309 : Plugs . sockets-outlets . & couplers forIndustrial purposes . Table - 54.4. [ 551.4.4.note ]

Regulation p/171: - 551.4.4 . NOTE : for suitable connection arrangements see . BS-EN-60309 - Series .

!!!. Do I Need . An External earth leadconnection to the Generator Star . ??
 
Explain the terms

a. Earthing : p/27
b.
Bonding Conductor. : p/23 . A protective conductor providing Equipotential Bonding .


lets Open it Up .

Solution
a. Earthing: connection of the exposed conductive parts of an installation tothe main earthing terminal of that installation.

b. Equipotential Bonding . Electrical connectionmaintaining various . exposed-conductive-parts &extraneous-conductive-parts at substantially the same potential .

Wording: “ Meanings “
Twotypes of [ Bonding ] normally used are

• Main protective bonding . &
• Supplementary protective bonding . [ where required ]

Main protective bonding – is alwaysrequired .
Reasons: Bonding reduces the voltage theremight have been .

[MET ] A terminal block . where Earthing & Bonding conductor(s) are connected together . Etc

Protective Equipotential Bonding411.3.1.2.
Ineach installation . Main protective bondingconductors . shall connect to the [ MET ] ► Extraneous-conductive-parts including the following .
i)Water installation pipes .
ii)Gas installation pipes . Etc .

Bonding– the correct title is ‘ Equipotential bonding ’. ‘ Electrical connection maintainingvarious exposed-conductive- parts and extraneous-conductive-parts at substantiallythe same potential ’



 
Ohm’sLaw .
Thecurrent in Amperes ( I ) is equal to theelectromotive force . Or Voltage ( V) divided by the Résistance ( R ) inohms .

Current (I) = Voltage (V) / Résistance ( R ) : I =V/R .

CurrentFlow - System voltage & Loadrésistance determine the flow of current.
ShortCircuit - Accidental connection createsfault . During a Short-circuit . onlythe résistance of the fault path limits current . Current may increase to manytime’s the load current .

Overloadis defined as an Overcurrent that is confined to the normal current path . “Excessive “ connected loads . ( StalledMotor’s ) Can Overload a circuit .
Mostconductors can carry a moderate Overload for a [ Short duration without damage]

Start-upOr Temporary Surge Currents : Motor’s . Transformer’s.
Overcurrents protection must be selected that will carry thesecurrents . MCB .

Short-circuitis any current not confined to the Normal path.
The “ Term “ comesfrom the fact that such current’s. bypass the normalload . Etc . Short / path around the Load . When a current isGreater than . normal current .

[ Short-circuit’s. ] are usually caused by Accidental contact Or wornInsulation . damage occurs . Facts. [ Moreserious than Overloads ]
[ Short-circuit’s. ] include two Or more conductors accidentallytouching . Short-circuit / Fault currents.

Typesof Electrical Fault’s :
Overcurrents– can be divided into two categories . Overloads / Short-circuits .
Anyelectrical current that “ Exceeds “ therating of the circuit is an “Overcurrent “

Or worn Insulation . damage occurs .
ATest that can be take for Granted . youwill get this on your 2392-10 . practical
Theimportance of this test . is that you could have damaged your cable duringInstalling it .

632.4. Defects or omissions revealed duringInspection & Testing of the Installation work . Shall be made good beforethe Certificate is issued .

p/31 : Origin of anInstallation : The position at which electrical energy isdelivered to an electrical installation .
p/24 : Circuit An assembly of electrical equipment supplied from the same Origin &protected against Overcurrent by thesame Protective device(s)

p/25 . Circuit breakers: .
Circuitbreakers : are designed to protectcircuits from Overloads &Short-circuits conditions . When applied within their ratings .
MCB. is connected to an electrical circuit& acts as a bridge between the circuit & the power supply .
MCBs. are designed to protect electrical circuits from being Overloaded .
Calculatea Watt-load for circuit breakers . 10A x 230V = 2300W .
 
• Surge current Or Inrush current . the maximum .instantaneous input current drawn by an electrical device when first turned on. :oops:

• BS-7671:2011 . put specific responsibility onthe Installer . 510.3 . requires that the Installer takes intoAccount the Manufacture’s Instruction’s .

 
Faultcurrents to be considered include faults between Line conductors & Earth .Line conductors & Neutral . & Line to Line conductors .
most domestic installations the ( PFC ) the value canexceed until 6kA . up to which value the ( Icn & Ics ) values are the same.
highestfault currents will arise with Three-phase Line conductors shorting together & to Earth .






 
Just a reminder .

So where does this [ 0V ] or[ Zero ] potential come from . The Earth .
p/26 . Earth .
The conductive mass of the . Earth .whose electricalpotential at any point is conventionally taken as [ Zero ]
 
Just a reminder . 2392-10 .
Earthing matters will come up in Exams .-&-s

Conductors used in such connections . are called “ Protective Conductors “ . & theycan be . subdivided .

Domestic Installations - Circuit protective conductors . CPC. For connectingexposed-conductive-parts to the [ MET ]
Domestic Installations - Main protective bonding conductors . for [ Bonding] together main incoming services .







 
Whencompleting Additions to a circuit such as an extra socket

a. state the type of Certificate to be issued
b. list three items of information that need to be entered on the form
c. state to who the form should be given.


Solution

a.
A Minor Electrical Installation Works Certificate.
b. (i)- Details of the existing installation . (ii)- Description of the minorworks . (iii)- Essential Tests / Test results.
c. The person ordering the work.


Q/As . it’s all you need to know to passyou on your Exams . 2392-10 . :banghead:


 
( MEIWC )
Minor ElectricalInstallation Works Certificate . are used for . “ Minor Works “ Only .

It come under this . Certification & Reporting : Regulation aretelling you the [ Answer’s ] :13:

Notes p/394 :
Minor WorksCertificate is intended to be Used for . Additions & Alterations .to aninstallation that Do Not Extendto the provision of a New Circuit .

Minor ElectricalInstallation Works Certificate. Q) Inspecting & Testing shouldalways be carried out . A) Irrespective of the extentof the work undertaken .


Let’s open it Up . Q/As -&-s .

Q) state to who theform should be given. A) The personordering the work . 2392-10 :

P/394 : ( To be appended to theCertificate )

2392-10 . You : should havereceived an “ Original “ certificate & the contractor should have retained a ( Duplicate )
if you were the
person ordering the Work .


►►BUT “ not the Owner of the installation . “ You “ should pass this Certificate . Or a copy of it . to the “ Owner

Point to NOTE here . MinorElectrical Installation Works Certificate.

2392-10 . -&-s are looking for . The right Certification& Reporting : for the Job .

This Certificate isNOT appropriate if yourequested the “ Contractor “ to undertake more [ Extensive Installation Work ]
For which youshould have received an [ Electrical InstallationCertificate ] EIC .

Regulations . are saying that ? you cannot use a Minor Certificate for Major Work . Etc .

Minor ElectricalInstallation Works Certificate. Notes . : are used for “ Minor Work “ that Do Not Extend to a New Circuit .

p/394 . Regulation aretelling you the [ Answer’s ]

The addition of a socket outlet to an “ Existing Circuit
The addition of a Lighting point to an “ Existing Circuit
Relocation of a light switch .
Can also be used for the replacement ofaccessories & luminaries .

NOT : for the replacement of distribution boards Or similar items .
 

[TABLE="class: MsoNormalTable"]
[TR]
[TD="width: 746, bgcolor: transparent"] Part 4: Declaration
[/TD]
[/TR]
[TR]
[TD="width: 746, bgcolor: transparent"] I/We CERTIFY that the said works do not impair the safety of the Existing Installation, that the said works have been designed, constructed, inspected and tested in accordance with BS 7671:2011…(IET Wiring Regulations), amended to……………………(date) and that said works, to the best of my/our knowledge and belief, at the time of my/our inspection, complied with BS 7671 except as detailed in Part 1.
[/TD]
[/TR]
[/TABLE]


( MEIWC)
 
Inspection& Testing : 2392-10 : 2011 . -&-s . “ InitialVerification “

Ifthe Inspection & Tests . are Satisfactory . a signed ( EIC ) 631.4 . together with a . Schedule of Inspections .& a Schedule of Test Results . 632.1 .
( Asin Appendix G ) are to be given to the person ordering thework . 632.3.

▲ (EIC ) p/391 . Bottom page . Regulations are telling you the Answers. 2392-10 .
Schedules : The attached Schedules are part of this document & thisCertificate is valid only when they are attached to it .
………….. Schedules ofInspections & ………… Schedules of Test Results are attached.

 
InspectionProcess . “ Wording “

VisualInspection . 2392-10 :

Wesee the words : Omission ?? . of appropriate sleving on Lighting Switch conductors &Two-way lighting strappers .



 
Remember - aLive conductor includes the Neutral also .

2391-10: prepare for taking the Exam .

Studentmust be aware of the correct use of Terminology when Answering Questions .Marks will be lost for Incorrect Use . “Nil Pwa“ - No points

Using: Completion Certificate “ instead of . ( EIC) Electrical InstallationCertificate .
Using: Electrical Inspection Certificate “ instead of . ( EIC ) Electrical Installation Certificate .
Using: Initial Inspection Certificate “ instead of . ( EIC) Electrical InstallationCertificate .
Using: Minor Work Certificate “ instead of . ( MEIWC ) Minor ElectricalInstallation Works Certificate . ◄► This is myFull Tile . Exams

2392-10:
Thisdocument is made up of Three-parts : ( 1. EIC ) 2 . Schedule of Inspections : 3. Schedule of Test Results : Exams .

( EIC ) ThisCertificate must be issued for a completely new Installation .
( EIC ) must beaccompanied by a Schedule of Test Results & a Schedule of Inspection .Without these two documents . the ( EIC ) is notValid . p/392– ( 2) ****

An Inspection & Test which is carried out ona [ New Installation ] to prove compliance is called an [ InitialVerification ]
p/395: Schedule ofInspections – ( forNew Installation work Only )

[ Initial Verification Inspection]
Thisdocumentation which should be completed is the . Electrical InstallationCertificate . ( EIC ) this must be accompanied by a Schedule ofTest Results & a Schedule ofInspection .

Thecertificate issued for an Initial Verification must be accompanied by aschedule of : ????
a.Test results only .
b.Inspections only .
c.Tests & schedules of inspections .
d.Schedule of inspections . & Schedules of test results . “ take your best Shot “ :icon_bs:

“ Facts“
▲ (EIC ) p/391 . Bottom page . Regulations are telling you the Answers. 2392-10 .
Schedules : The attached Schedules are part of this document & thisCertificate is valid only when they are attached to it .
………….. Schedules ofInspections & ………… Schedules of Test Results are attached.

 
Allinformation given by myself on these forums is used at entirely your own riskand is not necessarily the view of www.electriciansforums.net.

Justfor reading “ purposes “

ExtractFans in Bathrooms & Shower rooms .

- Ameans of Isolation to enable the fan to be separated from the source of energybefore gaining access to Live parts .
Themeans of Isolation would be provided by the device at the Origin of the Circuit. MCB – BS- EN 60947-3 Fan Isolatormounted adjacent to the fan

BS-EN 60947-3 . applies to switches . disconnections. switch- disconnections . & fuse-combination units to be used in distribution circuit & motor circuits of which the rated voltage does notexceed 1000V . a.c. or 1500 d.c.

-A means of switching off the fan for the purposes of Mechanical maintenance .cleaning .

BS-EN 60947-3 . fan Isolator mounted adjacent to the fan would fulfil therequirement for switching off for Mechanicalmaintenance . Regulation – 537.3.2.4. .requires the open position of the contacts of such a switch to be clearlyindicated .

-A functional switch to enable the fan to be switched “ On “ & “ OFF “ this functionalswitch may not be required where a . humidistat is used as a means of control .

Any suitable switch in table 53.2. of BS-7671:2011 would fulfil the requirements forthe functional switching . for such rooms without a window the fan is usuallyconnected to the light switch . Or a separate switch provided for rooms with awidow .

□ ExtractFans with a “ Run-on “ timer & / or humidistat .

BS-EN 60947-3 . fan Isolator .
Mountedadjacent to the fan would provide the appropriate means of switching “ OFF “ for Mechanical maintenance . Where theisolator switches both the switch wire & permanent Line conductor this would also provide a meansof [ Local Isolation ] where access to Live parts is required . the isolator should be located adjacent to the fan out with .Zones 0. 1.& 2 in accordance with Section 701of BS-7671:2011

Note; Such isolators also permit the Neutral conductor to be isolated .

□ ExtractFans without a “Run-on “ timer & / or humidistat .

Fanswhich are simply controlled by afunctional switch we would also recommend a BS- EN 60947-3 . fan isolator mounted adjacent to the fan as above. to provide the appropriate means of switching “ OFF “ for Mechanicalmaintenance . & local isolation . this is particularly important ifthe functional switch is mounted outside the room . consequently out with thecontrol of the person working on the fan .

ElectricalFixtures . Building Standards . requires that these fixtures can be Operated Safety .

P/286: BS-EN 60947-3 . – 533.1. 2011 .







 
Methodsof determining ( Ze )

Threemethods : Calculation . Enquiry . Measurement . must be used todetermine ( Ze )

Thedeclared maximum values of ( Ze ) & ( PSCC ) at the Origin .
230VSingle-phase & 230 / 400V Three-phase .

Characteristic: External Earth Fault Loop Impedance . ( Ze )
TN-S- 0.80Ω .
TN-C-S– PME . 0.35Ω .
TT- 21Ω .
Prospective Short Circuit Current ( Isc ) at theOrigin . [ Single-phase supply - 16.000A ] ……….. ( Isc ) meaning . p/38. A .
Prospective Short Circuit Current ( Isc ) at theOrigin . [ Three-phase supply - 25.000A ]

Themaximum values of ( Ze ) & (Isc ) declared by an electricity distributor are based on opposite suppositionsconcerning the impedance of the supplyto an installation . & cannot therefore be expected to occur at the sametime .
Inparticular . the maximum values of ( Ze) are based on the supply of higherimpedance – such as one employing long runs of low voltage cable & a distributiontransformer of lower ( kVA rating ) & the maximum values of ( Isc ) are based on the supply of lower impedance –such as one employing short runs of low voltage cable & a distribution transformerof higher ( kVA rating )

Thedeclared maximum values of ( Ze ) & (Isc ) can . in this case of a . TN-C-S system . be used to estimate the maximum value of ( Ze ) liable to occur in normal circumstances .& hence to determine the range of the possible values of ( Ze )

Example. Consider a Single-phase supply of nominal voltage . 230V . to aninstallation forming part of a TN-C-S system . where the electricity distributor declares a maximum values of ( Ze ) as 0.35Ω & (Isc ) as 16.000A . By Ohms law . it can estimated that .
When ( Isc ) is at is maximum value of 16.000A . ( Ze ) willbe at its minimum value of . 0.014Ω - givenby 230V ÷ 16.000A . therefore . in this case . the normal range of valuesof ( Ze ) should be taken as [ 0.014Ω to 0.35Ω ] in the absence of better information .

Themethod of estimating the minimum value of ( Ze ) given in the Example .strictly applies only to a TN-C-S system . Although it can generally be usedwith reasonable accuracy for a TN-S system also .

Note: Calculator - 230V ÷ 16000 = 0.014 )

The reason why the method referred to inthis Example strictly applies only to a TN-C-S system . is that it uses the maximum [ prospective shortcircuit current ] at the Origin .
Onthe assumption that this is equal to the maximum [ prospective earthfault current ] at the Origin .
- upon which the minimum value of ( Ze ) really depends . Only for a TN-C-S system is the assumptionfully justified . this is because the short – circuit & earth – fault currents in such a system share a common path in the distribution network . due tothere being a combined protective & neutral ( PEN ) conductorin the network . the assumption is only approximately true for a TN-S system . which uses separate protective & neutral conductors throughout .

Enquiry. like calculation . does not verifythat the intended means of earthling is present or that the value of ( Ze ) iswithin the expected normal range therefore . confirmation of theserequirements by measurement is still required before the installation isEnergized .

 
Sinks .Domestic : Domestickitchens, bedrooms and cloakrooms (unlike bathrooms and shower rooms) are notincluded amongst the special installations or locations in Part 7 of BS 7671 and are not rooms where the resistance of thebody is likely to be significantly reduced. Therefore, normal precautionsagainst electric shock should be adequate and the general rules of BS 7671 are applicable. However,whilst BS 7671:2011 does not forbid the installation of asocket-outlet or other accessory close to a sink in a domestic kitchen, bedroomor cloakroom, the requirements of Regulation 512.2.1 have to be taken into account. Therequirements of Regulation 512.2.1 mean that ordinary BS 1363socket-outlets and similar accessories are not suitable to be installed soclose to sinks or draining boards that they are likely to be splashed withwater or operated with wet hands. Thepenetration of water into an accessory could have serious effects. Waterentering the terminals and mechanism may lead to corrosion, internal arcing,general degradation and eventually malfunction. Additionally, and moreseriously, water may provide a track for the line voltage to be transmitted tothe front cover of the accessory, giving rise to the risk of electric shock.
512.2.1.Equipment shall be of a design appropriate tothe situation in which it is to be used or its mode of installation shall takeaccount of the conditions likely to be encountered.’
A rule of thumb recommendation for domestic premises, to avoid theeffects of splashing, is that ordinary BS 1363socket-outlets and similar accessories should ideally be mounted not less thanabout 300 mm (ideally not less than about 1000 mm), in the horizontal plane,from the extremity of a sink top or wash basin.
 
“ Definitions“

A “ wiring system “ & “ Conduit “ are defined in part 2 – 2011 .

Wiringsystem “ p/36.
Anassembly made up of cables or busbars . & parts which secure & . if necessary. enclose the cable or busbars .

Conduit“ p/25 .
Apart of a closed wiring system for cables . in electrical installations . allowing them to be drawn in & / orreplaced . but not inserted laterally .

Steelconduit forms part of a wiring system .

- PEN conductors :

Steelconduit must not be used as a combined protective & neutral ( PEN ) conductor . Regulation 543.2.10 .States .
543.2.10 . – A separate metalenclosure for cable shall not be used asa PEN conductor .

Restrictionson Use .
BS-7671:2011. places restrictions on the use ofSteel Conduit .

LiftShafts .
No cable or conduit is to be run in a lift ( orhoist ) shaft unless it forms part of the lift installationas defined in BS- EN 81-1 – Regulation 528.3.5. refers .
Apermitted exception is equipment relating to the lift installation . such aswell lighting . which commonly utilises conduit.
 
EarthFault Loop Impedance :

A limiting value of earth fault loop impedance . isspecified in the ( ADS ) requirements for TT system under two circumstances.

Wherean RCD . is used for fault protection .
Wherean Overcurrent device . is used for fault protection .

ProtectiveMeasure ( ADS ) for a TT system.
Asfor other types of electrical system . the magnitude & duration of voltagesbetween “ simultaneously accessible “ Exposed-conductive-parts . & Extraneous--conductive-parts . occurring anywherein a installation during an Earth Fault . ADS , achieves this coordinating thecharacteristics of the protective device for automatic disconnection . the earthing arrangements for the installation& the relevant impedance of the circuit concerned .

BS-7671:2011 . States three fundamental requirements for “ Fault Protective “ by ADS in a TT system .
- Protectiveearthing - Regulation / 411.3.1.1.
- Protective equipotential bonding . - Regulation / 411.3.1.2.
- Automaticdisconnection in case of a Fault . - Regulation/ 411.3.2.

Protectivedevices :

Faultprotection . 411.5.2. requires on ormore of the following types of protective devices shall be used . the “ Former being preferred “
- RCD.
-Overcurrent protective device such as .Fuse or Circuit breaker .








 
2392-10 “ Testing “
Meansfor Disconnecting the Earthing Conductor .

542.4.2. – requires means fordisconnection of the Earthing Conductor . to be provided at or near the ( MET ) of aninstallation to “ Facilitate measurement“ of the Résistance of the Earthing arrangements .

Meansof Earthing “ . Earthing Conductor → [ Bolted Link] → Connections : Circuit protective conductor : Mainprotective bonding conductors :
Functionalearthing conductors – if required : & lighting protection system bonding conductors - if Any .
 
Inorder to decide whether or not a specific “ Item “ is an Extraneous-conductive-part :

Q). is the item liable to introduce a potential . generally . EarthPotential .
Isthe item liable to introduce a “potential to a person “ or Livestock . who may be in contact with another potential .

Tointroduce a “ potential “ to such a person . the item must not only be apotential . but must be able to “ Introduce the potential “ introduction of the potential requires [ Two-things ]

- Thefirst is that the item [ or a Conducting item in electrical contact with it ] must be accessible to be [ Touched by a part of such a person’s body ]

- Thesecond is that any [ Electrical résistance ] through which the item is connectedto the [ Source ] of its potential – such as the résistanceconnecting an item with Earth potential . must not be so great as to preventthe potential being introduced to a person – due to voltage drop in the résistance.

Isthe item part of the Installation .

Onlyan item which does not form part of the electrical installation concerned may be an [ Extraneous-conductive-part ] however . items serving a purely non-electrical purpose within theinstallation should not be ruled out . moreover . items forming part of anotherinstallation are not precluded .


 
Thirdpart “ & NOT forming part of the ElectricalInstallation .

Thispart of the definition limits [ Extraneous-conductive-parts ] tobeing items which Do Not From Part . of the electrical installation in question .

Therefore. items which may be [ Extraneous-conductive-parts include ] the following . which are referred to inRegulation – 411.3.1.2. with regard to “ Main Protective bondingconductor “ provided such items arealso covered by other parts of the definition referred .

Waterinstallation pipes .
Gasinstallation pipes .. Etc .

Anyother non-electrical items which fallwithin the definition may be Extraneous-conductive-parts .
Althoughthe definition precludes items forming part of the electrical installation frombeing Extraneous-conductive-parts .items . serving a purely non-electrical purpose within an electricalinstallation should NOT be ruled OUT . such items may include .

A Metalsupport system or carrier for cables having non-metallicsheaths which is not required to be earthed .

Moreover– items forming part of another electrical installation – that is . aninstallation supplied from a different origin or having a separate earthing arrangements .
Are not precluded from being . Extraneous-conductive-parts . such items mayinclude . for Example . a metal conduit or the metal sheath or armouring of acable entering the premises from another building .





 
SpecialInstallations or Locations : 2011:

Theuse of SELV.

701: locations containing a bath or Shower .

701.414. Protection against electric shock .
701.512.3. Erection of switchgear . control gear &accessories .
701.55. Current – using equipment .
701.753. Electric floor heating systems .

702. Swimming pools . Application ofprotective measures against electric shock .

702.414. Protection against electric shock .
702.522.24. Junction boxes .
702.53. Switchgear & controlgear .
702.55. Other equipment .

703. Hot air saunas . Protection against electricshock .
704. Construction & demolition siteinstallations . 704.410.3. - 704.414. Protection against electric shock .
705. Agricultural & horticultural premises . 705.414. Protection against electricshock .
706. Conducting locations . 706.410.3.10. Protection against electric shock .

711. Exhibitions . shows & stands . 711.414.4.5. . Protection againstelectric shock .
712. Solar photovoltaic ( PV ) power supply systems . 712.414. Protection against electricshock .










 
Emergency Lighting :

Checklist .

For Emergency Lighting .
Non-Maintained . -&-s . The light only operates whenthe [ Normal main supply fails ] Emergency Lighting only .
( Permanent L ./ N )

Maintained . -&-s. The lighting operates normally & continues to operate when the normalmains supply fails [ Mains lighting& Emergency lighting ]
( Switched L : Permanent L . / N )

Final Exit Sign’s:
To provide illumination of escape routes .

Junctions : Install within 2 metres of escape route junctions .

Corridors : Install within 2 metres . horizontal distance of achange of direction in an escape route .

Stairways : Installwithin 2 metres . horizontal distance of achange in floor level or stairs [ each tread to receive direct light ]

Final Exit : Install externally within 2 metres horizontal distance of any final exits . Note : that sufficient light will be needed tomuster a roll call .

Alarm Exit : Firealarms . first aid points & fire fighting equipment . installed within 2metres horizontal distance .

Escalators : Shouldnot be used as an escape route . butrequires the same illumination to protect Uses on it when the supply fails .

Toilets : Install in all toilets exceeding [ 8m[SUP]2[/SUP] ] area or where natural light is not present .

Lifts : Toprovide emergency illumination in alllifts .

Control Rooms : Motorgenerator . control & plant rooms for essential & safety services .

Open Areas : Open rooms either with a particular hazard . an escape route passing through or largerthan [ 60m[SUP]2[/SUP] ]

Hazardous Areas : Areas of high risk should beilluminated to [ 10% ] of normal lighting or [ 15 lux ] whichever is greater .

Lighting Requirements .
When luminaires have been sited to cover the locations[ Above ] ▲ additional luminaires may be required toensure minimum lighting levels areachieved .
Manufactures provide spacing tables for this purpose . Spacingtables advise how far to locate the first luminaire . then how far . apart otherluminaires should be located for a given mounting height . Installation to the spacing’s will ensure thelighting levels will be achieved .

Escape route corridors : 1 lux minimum on the centre line of the escaperoute .
Open Areas : 0.5lux minimum on the centre core to within 0.5m of the walls .

Exit signs : Signs should apply to the European SignsDirective & be either . back illuminated or have an Emergency luminairewithin 2m of horizontal height . Signs should be of thesame formal throughout the building .

 
Emergency Lighting :
Form . EmergencyLighting design guide . 4 Edition 2008 .

Workplace directive – 89/654 .
Is 5 or more people areemployed there must be a writtenrecord of the assessments findings & the action taken . -&-s Exams

Maintained Emergency Luminaire :
A Luminaire containing one or more lamps all of whichoperate from the normal supply . or fromthe emergency supply at all material times .

Non - Maintained Emergency Luminaire :
A Luminaire containing one or more lamps . whichoperate from the emergency supply ONLY upon failure of the normal mains supply.

Normal Lighting :
All permanently installed [ Artificial ] lighting operating from the normal electricalsupply that in the absence of adequate [ daylight ] is intended for use duringthe whole time that the premises are Occupied .

Rated duration :
The manufactures declared duration . specifying the time for which the emergency lightingwill provide the rated lumen output after mains failure . this may be for anyreasonable period but in normally [ one or three hours . ] -&-s Exams

Rated Load : Themaximum load that may be connected to the system & will be supplied for theduration .

Re – charge period :
The time necessary for the [ Batteries ] to regain sufficient capacity to achieve their ratedduration .

Self – contained emergency luminaire or Single point luminaire :
A luminaire or sign . providing maintained or .Non-maintained emergency lighting in which all the elements such as the battery. lamp & the control unit are contained within the housing or within one metre of the housing .

Slave or Centrally supplied luminaire :
An emergency luminaire without its own batteriesdesigned to work with a central battery system .



 
Usefuljunk :

EdisonBase – Light Bulb’s . 612.6. (ii) [ Indicates ] 230V / E27 . male screw base.
E27 . the number “ 27 “ simply signifiesthe number of millimetres in diameter of the base itself . [ 27mm ]
 
Zones : Previous 16[SUP]th[/SUP] Edition .
Identifiedzones within the bathroom to [ Illustrate] what typeof electrics in the Bathroom . can be usedor installed .

Zones: 17[SUP]th[/SUP]Edition . “ Updated “

Takeinto account . Windows : doors : walls ceiling & partitions . [2392-10 - You are . Assessing the level of Risk in each Zone ]

Circuits in a Bath or Shower room . both power & lightingmust be Additionally protected by an RCD . 30mA - 701.411.3.3.: 314.1 (iv) : 531.2.4. Unwanted tripping .

17[SUP]th[/SUP]Edition – reinforces this .
Bath or Shower islocated in a building with Protective equipotential bonding in place . 411.3.1.2.

Mainprotective bonding conductor(s) . (i) Water installation pipes . [ Extraneous conductive parts ]

p/27 . Equipotential bonding. Electrical connection maintaining various . Exposed-conductive-parts & Extraneous-conductive-parts

• 2392-10 : Exams

Inyour own words . State . the meaning of a circuit overload & short-circuit protection . What will provide this type of protection !! :icon_bs:
p/35 . RCBO .

Wording .
Residualcurrent operated switching device . designed to perform the functions ofprotection against [ Overload & / or Short-circuit]

 
Bathroomequipment . selection & erection requirements .

Equipmentin “ Zone 1& 2 “ shall be at least IPX4 . Regulation . 701.512.2.( ii )
Equipmentin “ Zone 0 “ shall be at least IPX7 . Regulation . 701.512.2.( i )
Equipment exposed to cleaning jets to be at least IPX5. . Regulation . 701.512.2.

Zone 0 “ only 12V currentusing equipment . complying with a relevant standard is allowed . 701.55 .
(ii) - Fixed & permanently connected .
(iii) - SELV . safety source located outside of Zone .

in Zone 1 “ only :

Water/pumps. electrical shower(s) . Shower/pumps . ventilation equipment . towel rails . waterheaters . luminaires & 25V - SELV equipment is allowed . 701.55.
Fixed& permanently connected . SELV safety . source located outside of Zone . 0. 1. & 2 .

in Zone 2 “ only :

12V. SELV switches & shaver supply .socket-outlets to BS-EN-61558-2-5 . are the onlyallowed switchgear or accessories . 701.512.3.
SELV. safety source located outside of Zone .

2392-10: IP rating. dependent upon it’s location in the room . :banghead:



 
GN-32012 :

Classification of danger & non-compliances ( foruse during periodic inspection & testing )

Classification of danger or non-compliances [Description ]
C1: Danger present . Risk of injury . immediateremedial action required .

Notes &guidance :
To be cited insituations which cannot be left . it is suggested that these are rectified orpossibly . isolation may be recommended or necessary . examples : includeaccessible bare live parts , badly damaged equipment with risk of access tolive parts . incorrect polarity . arcing found in switchgear .

C2: potentially dangerous – urgent remedial action required .
To be cited insituations that . whilst urgent , do not require immediate remedial action . .examples : include a non-earthed installation . ( this requires a further faultto manifest injury ) fundamentally undersized cables . earth loop faultimpedance values greater than ( BS-7671) requirements . a “ borrowed “ neutral . equipment with inappropriatelyselected IP . ( this may be . C1 if severe ) insulationreadings under ( 1M )connections not terminated within appropriate enclosures .

C3: Improvements required .
To be cited where .C1 or C2 . do not apply . examples : include the absenceof most warning notices . absence of therequired diagrams & charts . no or incorrect marking of conductors atterminations , absence of an ( RCD ) specified for additional protection . ( Where the circuit otherwise tests as normal )











 
GN-32012 : ( IR )

InsulationRésistance of a . Three-phase 4core power cable .
The cable is tested.

Insulation Résistancetest on . 4-core power cable :

Test 1 : L1 / L2 .
Test 2 : L1 / L3 .
Test 3 : L2 / L3 .

Test 4 : L1 + L2 +L3 – ( connected together ) to Neutral
The lowest value ofthese tests . is recorded as “ between Live conductors “

Test 5 : L1 + L2 + (connected together ) to Earth .
The lowest value ofthese tests . is recorded as “ between Live conductors & Earth “

Note :it is essential for . Tests 5 & 6 that the cable earth is connected to the installation earthing terminal.

( IR ) readings obtained should be not less than theminimum values referred to table.BS-7671:2011 . Table61 .






 
GN-32012 : ( IR )

612.4.1. : SELV tests .
Test type .

Basic insulation .between Line conductors & all other circuits including other . SELV &PELV . & low voltage circuits . ( 250V – d.c.) Minimum – 0.5M .

Line / Earth : Between al SELV live parts & Earth .

Note: in situations where the SELV conductorsare separated by just ( insulation ) such as within a ( multicorecable ) with low voltage circuits . then the test voltage shall be increasedto ( 500V d.c.) & the (IR ) shall be not less than . ( 1M )

612.4.2. : PELV tests .
Test type .

Basic insulation .between Line conductors & all other circuits including other . SELV &PELV . & low voltage circuits . ( 250V – d.c.) Minimum – 0.5M .

Note: in situations where the PELV conductorsare separated by just ( insulation ) such as within a ( multicorecable ) with low voltage circuits . then the test voltage shall be increasedto ( 500V d.c. ) & the ( IR ) shall be not less than . ( 1M )


 
Teatmethod 2 : for circuits .

Instrument : use a low-résistance ohmmeter for test . ◄► Exams – 2391-10 .

One lead of thetest instrument is connected to the earth terminal at the distribution board . via a length of test cable or ( Wandering Lead ) the other test lead is used to make contactwith the protective conductor at . various points on the circuit under test .e.g. luminaires. switches . spursoutlets . etc . the résistance ofthe ( Wandering Lead ) & the test leads areeither auto-nulled prior to making the test ormeasured & subtracted from measured readings .

This test measuresthe continuity résistance of the circuit protective conductors ( R[SUP]2[/SUP] ) which should be ( Recorded on the Scheduleof Test Results )

Note: Parallel earth paths & effects on thereadings ) ◄► Exams – 2391-10 .

Exams – 2391-10 . Wording : Mainswitch [ OFF ] all fuses removed . circuit/ breakers [ OFF ]

Results : for test method 2 :

The results shouldfirst & foremost indicate ( No Open Circuit ) in the protective conductors . for insulatedwiring systems installed in conditions where accessory boxes & similar are not connected tofabric or other elements that mat be earthed . then the measurement will equate to the protective conductor résistance ( R[SUP]2[/SUP] ) this test can detect poor continuity atjunctions & connections since . for a New installation with new accessories. the contribution of résistance of healthy connections is negligible & canbe ignored . thus by employing the résistance data for copper conductors .

Expected values forhealthy cable & connections can be checked .

Example . Radialcircuit . of length about . 55m with a 2.5mm[SUP]2[/SUP] copper protectiveconductor should have an ( R[SUP]2[/SUP] ) résistance .
Length of circuitis 55m .
Résistance of cableis . 7.41 m/m - at 20°C .
Theoretical minimumd.c. résistance- ( 55 x 7.41 ) / 1000 = 0.41

When verifying this circuitthe . Inspector . should be looking for a reading of that order . say . 0.4 to 05 . if the circuit had several outlets . thusmeasuring that the protective conductor was broken & connected in screwterminals at each accessory . then a slightly higher value may be measured . asthere would be some résistance at the termin
 
( IR ) Testing . 2392-10 . / 2394 .Exams . Q/As .

For circuits containing [two-way switching or two-way & intermediate switching ] the switches must be [ operated one at a time] at a time & the circuits subjectedto additional ( IR) test in these configurations .


 
Testing . .

Earth fault loop impedance: Verification . 612.9.

Where limitation ofearth fault loop impedance is part of a protective measure .then it is fundamental that the [ InitialVerification ] process includesverification of earth fault loop impedances .

The earth faultcurrent loop comprises the followingelements . starting at the point of fault on the line – earth loop .
Circuit protective conductor.
Main earthingterminal & earthing conductor .
TN-system’s the metallic return path or . in the case of . TT & IT . systems .the earth return path .
Path through theearthed neutral point of the transformer .
Source line windings . &
Line conductor fromthe source to the point of fault .

612.8. - 612.9. :
There are [ Two-methods ] used for verifying total . earth faultloop impedance for a circuit :

- Measurement oftotal earth fault loop impedance ( Zs )using an instrument .
- Measurement of ( R[SUP]1[/SUP] + R[SUP]2[/SUP] ) during continuity testing of a circuit . & addition to the measured earth faultloop impedance external to that circuit ( Ze )

Exams . Instrument : use an earthfault loop impedance tester . for this test .

 
Testing . .

ElectricalInstallation Condition Report . ( EICR )
634.1.
Amendment No 1 –BS07671:2008 . reporting of periodicinspection & testing .

Full . ( EICR) documentation comprises .

ElectricalInstallation Condition Report .
&
Schedule ofInspections ( one or more )
&
Schedule of Test results . ( one or more )

Exams : On completion of . periodic inspection &testing . this ( EICR ) & itsaccompanying . Schedule of Inspections .& Schedule of Test results . mustbe given to the . Client or Person . who ordered the Inspection .

634.2.
A most importantpoint to . remember is that any damage . deterioration . defects . Part 2- dangerous conditions &non-compliance with BS-7671: that may give rise to danger ( danger being a riskor injury to persons or livestock ) mustbe recorded on the report .










 
Testing . . 2392-10 . Exam’s Q/As

EarthFault Loop Impedance Testers:

ETC. : To minimise . Electric Shock . hazard from the potential of the protectiveconductor . the [ Test durationshould be within safe limits ] this means that the . instrument should cut [ OFF ] the test current after [ 40mS ] or atime determined by . the safety limits .

EarthFault Loop Impedance Testers: Exams : BS-EN-61557-3 .


 
InitialVerification – ( Inspection & Testing ) forms .

Following an . InitialVerification . or [ Additionor Alteration to an ExistingInstallation ] an (EIC ) is required to be completed &issued together with . InspectionSchedules . & Test results Schedules.

There are twooptions . for ( EIC ) provided . form 1 : or form 2 : .

Form 1 : - Shortform of ( EIC ) to beused when . ONE person is responsible for the. design . construction . inspection & testing of an installation .
Or
From 2 : - ( EIC ) Three signatoryversion . from appendix 6 – BS-7671 .

Whichever . ( EIC ) isused . appropriate numbers of the following forms are required to . accompanythe Certificate .

Form 3 – Schedule ofInspections’ .
&
Form 4 – Generic . Scheduleof Test results .

For completeness .two samples of typical completed from 4s [ Schedule of test results ] areincluded . One . being for a Single-phase installation . & the other for a Three-phase installation .

2392-10 . this isthe kind of things -&-s will beasking you . which for ? . Single-phase / Three-phase installation.
 
Point . to note: p/389 . Certification & Reporting .
( x ) Additionalforms may be required as . clarification . if needed by . Ordinary persons . or inexpansion . for larger or more complex installations .
 
( MEIWC)
Two thing spring tomind . -&-s . 2392-10

The . Minor WorkCertificate . is intended to be used for . Alterations or Additions . to an [ Installation thatdo not extended to the provision of a NEW Circuit ]

This Certificatemay also be used for the .
replacement ofequipment such as accessories or luminaires , but not for the replacement of . distributionboards . or similar items . [ Appropriateinspection & testing . however . should always becarried out irrespective of the extent of the work undertaken . ] -&-s
 

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Green 2 Go Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses Heating 2 Go Electrician Workwear Supplier
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread Information

Title
***Cont../ Useful Information for Electricians & Apprentices***
Prefix
N/A
Forum
Australia
Start date
Last reply date
Replies
933
Unsolved
--

Advert

Thread statistics

Created
amberleaf,
Last reply from
Dan,
Replies
933
Views
96,654

Advert

Back
Top