O.S.G.. The use of other methods’ of determining Maximum Demand is Not Precludedwhere Specified by the Installation Designer
FirstlyI make no Apologies for the Way am Writing on any Matters . it can be a first day Apprentice or some one Needing aJog of Memory .
Sowe are all in the Same Boat . “ To Learn “
For the Apprentices . The Day we stop learning is the Day we hang Upour Tool-Bag
CookerDesign Current Calculations
Thefirst thing you have to do is get Your Head around the Calculations !!
(From a Design point of View ) 2392-10
DomesticInstallation Oven(s) & Hob(s) are to be Calculated upon their MAXIMUM LOADING
Startwith a simple Calculation ( An Oven has a rating of 2kW ) 2000
(I = P/V ) Formula … I = 2000 ÷ 230V = 8.70A …. Weare Using the Unit Amps
2392-10/ Domestic Installation Oven(s)
Ovenhas 4 Rings ( 2 x 1kW ) & ( 2 x 1.5kW ) & Grill ( 2kW ) & Oven (3kW )
-Controlled via a CookerSwitch with a Socket outlet .
Asa Designer . we’ll have to Apply Diversity ??
Important )- Diversity allowance to be Applied to the FULL LOAD CURRENT for CookingAppliances .
TheO.S.G. is telling us . Purpose of the Final Circuit fed from theConductors )
O.S.G.Table 1B p/97 – column (3) Cooking Appliances → At the Top of the Page Note : Type ofPremises ( 2392-10 → Household Installations ) Domestic Installation(s)
DomesticInstallation(s) Only O.S.G. - 10A + 30% f.l – Full Load ) of connected Cooking Appliances in the Excess of 10A+ 5A if a socket-outlet is incorporated in the Control Unit . ( C.C.U. ) – 45A + 13A Socket Switched with Neon .
Fromyour point of View ( The First 10A ofthe rated current plus 30% of the reminder ( Plus) 5A if the Control Unit incorporates s Socket.
Calculations)- You bank “ Hold OFF“ the first 10 Amps of the Maximum Load Current )
The10A will be used at the End of the Calculations’
-So your Work out the Total Power Rating & then calculate the Full Load Current
Calculations)- Power = ( 2 x 1 ) + ( 2 x 1.5 ) + ( 2+ 3 ) = 10kW
I= 10000 ÷ 230V = 43.48A … round it up to the first four numbers43.47826087 ( 48 ) 43.48A
UsingDiversity allowance stated ↑↑ ( 43.48A sub 10A = 33.48A )
I= 33.48 x 30 ÷ 100 = 10.04A
Youradding the ( 5A ) for Socket outlet . I = 10A + 10.04 + 5A = 25.04A )- Asa Designer this is your Expected Current Demand .
Remember )- Supply Cables Rated to suit DesignCurrent ( Iz )
Workingmy way around the 17[SUP]th[/SUP] Edition – Selection & Erection / Part 5
Making you aware of “ Accessibility“ :aureola:
Everyconnection shall be Accessible for Inspection
- Exceptions include . ◄◄ :50:
- Designedto be Buried .
- Compound resin Joint .
- Connectionto Floor / Ceilingheating Elements .
-Soldered . Welded . Brazed . Compressed Joints . or appropriate compressiontool .
Workingmy way around the 17[SUP]th[/SUP] Edition – Selection & Erection / Part 5
Making you aware of “ Installation CircuitArrangements “ Part – 3 & 5 :dupe:
Thenumber of circuits & outlets per distribution board will be .
520.3. FundamentalPrinciples . :freak:
i)Cables & Conductors .
ii)Connections . Terminations & Joints.
iii)Supports & Suspensions .
iv)Enclosures & Protection against External Influences .
OvercurrentProtection – Chapter 43 .
Isolation& Switching – Section 527 .
Currentcarrying capacity of the conductors – Section 523 .
ExternalInfluences – Chapter 52 . 522 . App 5
CableSelection Overview .
Therequirements are :-
Thecable supplying the Load should be able to carrythe current to the Load safety . after takinginto account Diversity . without the cable Overheating– 523 . App 4
Protective Devices should beable to provide protection for the cable from Excess Current – 432. 433 .
TheLength of the cable is Limited to Ensureadequate voltage supplies the Load . 525.
MaximumLoop Impedance of a circuit is Low enough to ensure disconnection within timesspecified by Table 41.1.
( 0.4 - TN ) & (0.2 sec - TT ) for all circuits 32A ( FinalCircuits Not Exceeding 32A ) P/46
(5 sec disconnection time ) for Sub –main distribution circuits . Etc .
2392-10: Protection against Shock .
Two Important Measurements mustbe taken to prevent this hazard . :50:
i) Impedance of acircuit conductors is kept to a minimum . The Earth Fault LoopImpedance under Fault Conditions .
ii) Overcurrent device protecting the circuit isselected to rapidly disconnect an Earth Fault .
Room Thermostat should belocated in the part of the house where people spend the most time . it shouldbe ( 1.5m. ) above floor level .
( 0.5m away from an outside wall ) :aureola:
Relevanttests of Regulation – 612.2. to 612.13 .Example Continuity of Protective conductors & Earth Fault Loop Impedance .Applicable to parts of the system(s) such as room & cylinder Thermostats .motorized valves & programmers .
( YES ) Automatic Disconnection of Supply ( ADS ) is acommonly – used protective measures against Electric Shock in such systems .The Continuity of the protective conductorsto each point should be confirmed . This value of ( R2 ) or ( R1 + R2 ) may be used to estimate the Maximum EarthFault Loop Impedance of each control circuit for Verification Purposes . Insulation Résistancetests should also be carried out . precautions having been taken to avoiddamage . to any Electronic Components . The test results should be recorded on a Schedule oftest results .
Regulation. 411.3.1.1. – 411.3.2. – 612.9.
DoesBoiler pipework need to have Main Protective Bonding Conductor for ElectricalSafety Reasons . :dupe:
Thereis “ NO SPECIFIC “ requirements for Boiler pipework to be SupplementaryProtective Bonding Conductors .
However:- Such bonding may called for in the Boiler Manufactures . in which case BS-7671:2008 .requires those Instructions to be followed ( Regulation 510.2. refers )
Anystated requirements for Additional Bondingthat is considered to be Unnecessary should be queried with the Manufactures Concerned. & Amended Installation instruction requested .
DoesBoiler pipework need to have Main Protective Bonding Conductor for ElectricalSafety Reasons .
Regulationnumber(s) 411.3.3 . :aureola:
Isan RCD Main Switch . ( Such as a 100mA time – delayed device )still required in the Consumer Unit of a New Domestic Installation forming partof a TT System . :dupe:
Fora Domestic Installation complying with the 17[SUP]th[/SUP] Edition where allthe Final Circuits are RCD – protected .
AnRCD Main Switch. is NOlonger required . Provided that the Consumer Unit is of all Insulated Construction .
2392-10:-
Asthe Designer of an Installation . Am I allowed to rely on the RCD element of an RCBOto provide for Fault Protection in order to allow for ( Loop ImpedanceValues ) Greater than given in Table 41.3 .
Yes) . So long as all the other Applicable requirements of the 17[SUP]th[/SUP] Edition ( as Amended ) are met .Including those for protection against Overload & Short – Circuit .
Regulationnumber(s) 411.4.4. - 411.4.5. - 411.4.9. :aureola:
Wherethe Earth Fault Loop Impedance for a circuit Exceeds the Maximum ( Zs) for the Overcurrent Device . is it permissible to use an RCD .
Yes:- Regulation . 411.4.4. - 411.5.2.
CanI use an ( Electrical Connector ) having “ push fit “ connections that the Manufacturer claims areMaintenance free in an area that will be inaccessible when the installation iscomplete .
NotNecessarily . Not all types or designs of Push Fits ( Screw less – type ) Clamping with the requirements ofRegulation - 526.3. ( vi )
Ifthe connector will be inaccessible when the Installation is complete . it mustComply with BS-5733 for a Maintenance – free accessorywith the Manufactures Instructions .
BS-5733 Requires . Example . Tests for Résistance to ageing .Cyclic loading . Overload . Fault current & Vibration .
Workingmy way around the 17[SUP]th[/SUP] Edition – Protection . Isolation . Switching. Control & Monitoring .
Making you aware of “ Motor Control:
537.5.4. “ Plain English “ :rant:
537.5.4.1.) Non – automatic restart .
537.5.4.2.) Non – reversal of Motor on breaking .
537.5.4.3.) Non – reversal of Motor for SafetyPurposes .
Sizing of Main & CircuitProtective Conductors’ . :icon_bs:
(K1 ) = k value for Line Conductor – Table 43.1. – p/49
( K2 ) = k value for ProtectiveConductor – Table 54.2. – 54.6. - p/129 . p/130 .
Workingmy way around the 17[SUP]th[/SUP] Edition . 2392-10
Regulation. 544.1.2. Main ProtectiveBonding Conductor . ( Gas / Water ) :rant:
Positioningof Bonding Connection . ( Apprentices –look at the drawings – p/32 – Regulations )
17[SUP]th[/SUP]Edition . The main equipotential bonding connection to any . Gas . Water . orother services shall be made as near as practicable to the point of entry ofthat “ Service “ into the premises . Where thereis an Insulating section or insert at that point . or there is a ( Meter ) Theconnection shall be made to the Consumer’s hard ( MetalPipework ) & before any branch pipework . Where practicable theconnection shall be made within ( 600mm ) of themeter outlet union or at the point of ( Entry ) to the building if the meter isExternal .
Thisone may come up in Exams . -&-s
Workingmy way around the 17[SUP]th[/SUP] Edition . 2392-10
Regulation. 544.1.2. Main ProtectiveBonding Conductor . ( Gas / Water )
External Supply Meters . are Bonded at thePoint of Entry . ◄◄◄ :icon_bs:
Workingmy way around the 17[SUP]th[/SUP] Edition . 2392-10
Regulations. p/32 . The . How’s & Why’s . Fig / 2.1
(2 ) - Main Protective Bonding Conductors .
Protective Bonding must beApplied to all Areas where there is .
TheLikelihood of ElectricShock is Greatly Increased to Water . :icon_bs:
Workingmy way around the 17[SUP]th[/SUP] Edition . 2392-10
Definitions. p/24 .
Extraneous-Conductive-Part. Conductive part liable to introduce apotential . generally Earth Potential . & not forming part of theElectrical Installation .
( A Metallic Fixture notassociated with the Electrical Installationthat could become Live under Fault Conditions ) :icon_bs:
Workingmy way around the 17[SUP]th[/SUP] Edition . 2392-10
525 (- Volt Drop for NormalOperation – Appendix 2 & 12 . ) 2392-10 . :icon_bs:
Formula: to find the Actual Volt Drop when the Cable is known . App 4 .
( V.D. / max = mV / A / m x Ib x L / 1000 )
Alternativeformula when the Cable is NOT Known & theminimum size is to be found :
( mV /A/ m – max = V.D./ max = V.D. – max x 1000 / Ib x L )
ApplyingElectrical Design . :smug:
Selectcable size from Appendix 4 .
• Cableselection for type should have already been considered due to initial characteristicsof purpose . Environment . Maintainability . part 3 & 4 . Appendix 5 – External Influences .
• Appendix4 – table 4A1 provides methods of Installation which are cross referenced whenselecting the maximum Current Carrying Capacity ofthe circuit cable . p/260 .
• 2392-10 . DomesticInstallation cables are to be used the Appendix 4 – Table 4D5 . ( Sheathed flat cables) T&E.
525.1– Requirements for volt drop inbuildings .
Table 12 – Voltage Drop . Regulation - p/358
Making you Aware .
(i) Low voltage Installations supplied directly from apublic Low voltage distribution system ( lighting – 3% ) – ( Other uses 5% )
(ii)Low voltage Installations supplied from private LV supply – ( * ) ( lighting – 6% ) – ( Other uses 8% )
( * ) The voltagedrop within each final circuit should not exceed the values given in ( i )
Wherethe wiring systems of the Installation are longer than ( 100m ) .the voltage drops indicated above may be increased by ( 0.005% ) per metre of the wiring system beyond ( 100m ) without this increase being greater than ( 0.5% )
Thevoltage drop is determined from the demand bythe Current-using Equipment . applying Diversity factors where Applicable. or from the value or the Design Current of the Circuit .
Current– Using Equipment :17:
554.1.Electrode water heaters & boilers .
554.1.4. RCD tooperate in Excess of 10% of rated current but can be extended to 15% dependant upon machine . Time Delay RCDs maybeUsed .
Reply to ***Cont../ Useful Information for Electricians & Apprentices*** in the Australia area at ElectriciansForums.net
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
Good to know thanks, one can never have enough places to source parts from!
OFFICIAL SPONSORS
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...