O.S.G.. The use of other methods’ of determining Maximum Demand is Not Precludedwhere Specified by the Installation Designer
FirstlyI make no Apologies for the Way am Writing on any Matters . it can be a first day Apprentice or some one Needing aJog of Memory .
Sowe are all in the Same Boat . “ To Learn “
For the Apprentices . The Day we stop learning is the Day we hang Upour Tool-Bag
CookerDesign Current Calculations
Thefirst thing you have to do is get Your Head around the Calculations !!
(From a Design point of View ) 2392-10
DomesticInstallation Oven(s) & Hob(s) are to be Calculated upon their MAXIMUM LOADING
Startwith a simple Calculation ( An Oven has a rating of 2kW ) 2000
(I = P/V ) Formula … I = 2000 ÷ 230V = 8.70A …. Weare Using the Unit Amps
2392-10/ Domestic Installation Oven(s)
Ovenhas 4 Rings ( 2 x 1kW ) & ( 2 x 1.5kW ) & Grill ( 2kW ) & Oven (3kW )
-Controlled via a CookerSwitch with a Socket outlet .
Asa Designer . we’ll have to Apply Diversity ??
Important )- Diversity allowance to be Applied to the FULL LOAD CURRENT for CookingAppliances .
TheO.S.G. is telling us . Purpose of the Final Circuit fed from theConductors )
O.S.G.Table 1B p/97 – column (3) Cooking Appliances → At the Top of the Page Note : Type ofPremises ( 2392-10 → Household Installations ) Domestic Installation(s)
DomesticInstallation(s) Only O.S.G. - 10A + 30% f.l – Full Load ) of connected Cooking Appliances in the Excess of 10A+ 5A if a socket-outlet is incorporated in the Control Unit . ( C.C.U. ) – 45A + 13A Socket Switched with Neon .
Fromyour point of View ( The First 10A ofthe rated current plus 30% of the reminder ( Plus) 5A if the Control Unit incorporates s Socket.
Calculations)- You bank “ Hold OFF“ the first 10 Amps of the Maximum Load Current )
The10A will be used at the End of the Calculations’
-So your Work out the Total Power Rating & then calculate the Full Load Current
Calculations)- Power = ( 2 x 1 ) + ( 2 x 1.5 ) + ( 2+ 3 ) = 10kW
I= 10000 ÷ 230V = 43.48A … round it up to the first four numbers43.47826087 ( 48 ) 43.48A
UsingDiversity allowance stated ↑↑ ( 43.48A sub 10A = 33.48A )
I= 33.48 x 30 ÷ 100 = 10.04A
Youradding the ( 5A ) for Socket outlet . I = 10A + 10.04 + 5A = 25.04A )- Asa Designer this is your Expected Current Demand .
Remember )- Supply Cables Rated to suit DesignCurrent ( Iz )
2392-10:- “ Consumer Controlgear “ 530.3.4. :speechless:
ForInstallation with a 230V single-phase supplyrated up to 100A that are under the control of ( Ordinary Persons) should either .
• Comply with BS-EN 60439-3 & Regulation 432.1. of BS-7671.
• Be a Consumer Unit – incorporating components complyingwith BS-EN 60439-3
Regulation Chapter 532 . :- Devices for Protectionagainst the Risk of Fire . :whatchutalkingabout
532.1.Where in accordance with the requirement of Regulation 422.3.9. it is necessaryto limit the Consequence of ( Fault Currents )in wiring system from the point of view of ( Fire Risk ) THE Circuitshall be either .
i)Protected by an RCD complying with Regulation 531.2. for ( Fault Protection ) &
- The RCD shall be installed at the ( Origin of the Circuit ) to be Protected . &
- TheRCD shall Switch all Live Conductors . &
-The rated Residual Operating Current of the RCDshall Not Exceed ( 300mA) ETC .
Chapter537 . Isolation & Switching .
Isolation– ( 537.2.
Switchingoff for Mechanical Maintenance - ( 537.3.
EmergencySwitching - ( 537.4 .
FunctionalSwitching - ( 537.5.
Fire-fighter’s Switches – ( 537.6 . :speechless:
A Fire-fighter’sswitch shall be provided in the Low Voltage circuit supplying :
i)( Exterior ◄ ) electrical installationsoperating at a Voltage Exceeding Low Voltage . &
ii)( Interior ◄ ) Discharge lighting installations operating ata Voltage ( ExceedingLow Voltage )
(Temporary Installation ) Fire-fighter’s Switches – ( 537.6.1.
Forthe purpose of this regulation . An installation in a CoveredMarket . Arcadeor Shopping Mall is considered to be an (Exterior Installation )
• A Temporary Installation in a Permanent Building used for Exhibitions isconsidered ( NOT to be an Exterior Installation )
“ Isolation“ :icon14:
Itemsto be Considered in Relation to “ Isolation “ devices.
• Number of poles to be “ Isolated“
• “ Isolation “ of groups &inconvenience .
• Devices designed and / orinstalled to prevent Unintentional or Inadvertent closure .
• “ Isolation “ devices to beClearly Indentified and Indicate the Installation or Circuit it Isolates .
Isolationrequirements for ( TN-S ) Systems .
Single-phase. L ≈ N - Circuit Protective Conductor .
Three-phase. L1 . L2 . L3. ≈ N . - Circuit ProtectiveConductor .
Emergency Switching :icon14:
Whatare the requirements for Emergency Switching in relation . to
• Full Load Current .
• Hand – held devices .
• Identification of Emergency Switching devices .
• Positioning & Accessibility .
• Positioning & Identification .
• Further Danger .
Firefighters Switch :
A Fire-fighter’s Switch is a Device intended for Use by Fire Service . ( Although ) NotExclusively SO :speechless:
It’spurpose is to ( De-energise ) designated parts of an Installation . That operateat a voltage in ( Excess of Low Voltage ) Neon Lighting .
2392-10: :speechless:
542: Earthing Arrangements .
542.1.General Requirements .
542.1.1.The Main Earthing Terminal . Etc
542.1.2. TN-S .
542.1.3. TN-C-S .
542.1.4. TT or IT .
Chapter54 . p/124
EarthingArrangements & Protective Conductors .
542- Earthing Arrangements . p/126
543- Protective Conductors . p/128
544- Protective Bonding Conductors . p/134 .
ProtectiveConductors .
Areconductors provided for the purposes of Safety . for some measures of Protection Electric Shock . Reg - p/27
Look– fig 2.1 / p32 . Earthing & Protective conductor .
2392-10:
-&-s . Q ) How many Types of EarthingSystem are recognised by BS-7671:2008 . :icon14:
A) 312.3.1. p/38 :- Types of System are . [ TN-C : TN-S : TN-C-S : TT : IT :
2392-10:
TheEarth Fault Loop Impedance ( Zs ) for a Consumer’sCircuit is determined by ? :icon14:
(R1 + R2 ) + Ze
Part 2 Definitions - P/36 :
TheProspective Short Circuit Current at the Origin of the Consumer’s Installationmust be taken into account when ??
Selectingthe type of Overcurrent Protective Device to be installed .
Wherepracticable Main Protective Bonding Conductor . to the Gas services in abuilding should be made within .
[600mm of the Meter on the Consumer Side ] :speechless:
O.S.G.P/27 (- Main Protective Bonding Conductors are required to connect the followingMetallic Parts to the ( Main Earthing Terminal) 411.3.1.2.
Extraneous-conductive-part : A Conductive part such as a Metal Pipe . ( LIBLE )to introduce Earth Potential into the Building.
MainProtective Bonding Conductor is the Electrical Interconnection between the MainEarthing Terminal & the incoming Metallic Services : Water / Gas .
TN-C-S. Earthing arrangements .
Regulations544.1.1. p/134 . & Table 54.8 / p134
IETwiring regulations – 17[SUP]th[/SUP] Edition . The required size of the Main Bonding Conductor is ( 10.0mm[SUP]2 [/SUP] ) for supplieswith a Neutral Conductor of ( 35.0mm[SUP]2 [/SUP] ) or Less
Becauseof this You will be required to use ( 10.0mm[SUP]2 [/SUP] ) Single Core Earth Cable toconnect both the Incoming ( Water pipe ) & the Incoming ( Gas pipe ) to theMain Earthing Terminal inside the Consumer Unit . ( CU )
I've skimmed through the last few pages, mostly initially with a "WTF" expression, which then becomes an "AAAAH, I get it". I thank you.
2392-10:
Q)- A single-phase circuit using 2.5mm[SUP]2 [/SUP] single-core PVC cables in conduit supplies adesign current of 20A .
If the cables are 15m long & have a rated voltage drop of ( 18mV/A/m ) the actual VoltageDrop will be . ????
A)- ( 18mV/A/m ) x 20A x 15m ) ÷ 1000 = 5.4V
2392-10: -&-s
Duringthe Testing Line of an Electrical Installation .Which Test would be carried out first . ????
612.2.1– Continuity of Protective Conductors . ◄
612.3.– Insulation Résistance . ( IR )
612.6. – Polarity .
612.9.– Earth Fault Loop Impedance .
Megger ( 1552 / 1553 ) :speechless:
SetUp :
RCD Touch Voltage selection ( To select either 25V or 50V )
1 )With the instrument turned OFF . hold down the Yellow test button & turn the left hand rotary switch to any ON position .
2 )Keep the button held down until the instrument displays the “ SET “ Warning .
3) Now release the TEST button .
4) Pressthe TEST button again to view the currentsetting for the Touch voltage .
Thedisplay shows the touch voltage limit . 50V
Note: The MFT can also display the measuredTouch Voltage on a bar-graph display .
Ifthe touch voltage display is Active . a bar-graph display will also appear .
5) Press the ORANGE( buzzer ) button to change the touchvoltage limit setting . 25V / 50V
6) Press the BLUE (RCD ) button to turn the bar-graphdisplay ON or OFF .
7) Press the TESTbutton to exit from the set-up menu .
Isolation& Switching : :49:
537.2.1. Every circuit shall be Isolated from the Live Supply.
Threepoints of Isolation .
Origin– 537.1.4.
DistributionBoards – 537.2.1.1.
FinalCircuits – 537.2.1.1.
MustIsolate all ( Phases) but not necessarily the Neutral– No link in CPC
Note (- 537.2.1.7.
Isolationat the Origin .
TN-S Phases or Lines & Neutrals
TN-C-S Phases only but both Lines & Neutral where access is Obtained by UnskilledPersons – 537.1.4.
TT- Both Line & Neutral .
Reply to ***Cont../ Useful Information for Electricians & Apprentices*** in the Australia area at ElectriciansForums.net
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
Good to know thanks, one can never have enough places to source parts from!
OFFICIAL SPONSORS
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...