***Cont../ Useful Information for Electricians & Apprentices*** | Page 32 | on ElectriciansForums

Discuss ***Cont../ Useful Information for Electricians & Apprentices*** in the Australia area at ElectriciansForums.net

A

amberleaf

O.S.G.. The use of other methods’ of determining Maximum Demand is Not Precludedwhere Specified by the Installation Designer

FirstlyI make no Apologies for the Way am Writing on any Matters . it can be a first day Apprentice or some one Needing aJog of Memory .
Sowe are all in the Same Boat . “ To Learn “

For the Apprentices . The Day we stop learning is the Day we hang Upour Tool-Bag

CookerDesign Current Calculations

Thefirst thing you have to do is get Your Head around the Calculations !!

(From a Design point of View ) 2392-10

DomesticInstallation Oven(s) & Hob(s) are to be Calculated upon their MAXIMUM LOADING
Startwith a simple Calculation ( An Oven has a rating of 2kW ) 2000

(I = P/V ) Formula … I = 2000 ÷ 230V = 8.70A …. Weare Using the Unit Amps


2392-10/ Domestic Installation Oven(s)

Ovenhas 4 Rings ( 2 x 1kW ) & ( 2 x 1.5kW ) & Grill ( 2kW ) & Oven (3kW )

-Controlled via a CookerSwitch with a Socket outlet .

Asa Designer . we’ll have to Apply Diversity ??

Important )- Diversity allowance to be Applied to the FULL LOAD CURRENT for CookingAppliances .

TheO.S.G. is telling us . Purpose of the Final Circuit fed from theConductors )
O.S.G.Table 1B p/97 – column (3) Cooking Appliances → At the Top of the Page Note : Type ofPremises ( 2392-10 → Household Installations ) Domestic Installation(s)

DomesticInstallation(s) Only O.S.G. - 10A + 30% f.l – Full Load ) of connected Cooking Appliances in the Excess of 10A+ 5A if a socket-outlet is incorporated in the Control Unit . ( C.C.U. ) – 45A + 13A Socket Switched with Neon .

Fromyour point of View ( The First 10A ofthe rated current plus 30% of the reminder ( Plus) 5A if the Control Unit incorporates s Socket.

Calculations)- You bank “ Hold OFF“ the first 10 Amps of the Maximum Load Current )
The10A will be used at the End of the Calculations’

-So your Work out the Total Power Rating & then calculate the Full Load Current

Calculations)- Power = ( 2 x 1 ) + ( 2 x 1.5 ) + ( 2+ 3 ) = 10kW

I= 10000 ÷ 230V = 43.48A … round it up to the first four numbers43.47826087 ( 48 ) 43.48A

UsingDiversity allowance stated ↑↑ ( 43.48A sub 10A = 33.48A )

I= 33.48 x 30 ÷ 100 = 10.04A

Youradding the ( 5A ) for Socket outlet . I = 10A + 10.04 + 5A = 25.04A )- Asa Designer this is your Expected Current Demand .

Remember )- Supply Cables Rated to suit DesignCurrent ( Iz ) :)
 
First Amendment : Definitions.p/29

Inspection : Examination ofan electrical installation using all the senses as appropriate . :leaving:

17[SUP]th[/SUP] Edition : Definitions p/25

Inspection : Examination ofan electrical installation using all the senses as appropriate .
 
Inspection :- :yawn:

611.3. –
The inspection shall include at least thechecking of the following items where relevant . including as appropriate allparticular requirements for special installations or locations ( Part 7 )

611.3. –

The inspection shall include at least thechecking of the following items . where relevant to the installation and .where necessary . during erection .



 
Just a reminder . 17[SUP]th[/SUP]& FirstAmendedment :13:

Testing - 2391-10 / 2392-10.

612.1.
Thetests of Regulations 612.2. to 6 . Whererelevant . shall be carried out in that order before the installation is [ ENERGIZED ] .
Wherethe installation [ INCORPORATES ] an earthelectrode . The test of Regulation 612.7. shall also be carried out before the [ INSTALLATION is ENERGIZED]

Ifany test indicates a failure to [ COMPLY ] thetest and any preceding test . The results of which may have been [ INFLUENCED ] by the fault indicated . shall berepeated after the fault has been rectified .



 
Exampleof items requiring inspection for an ElectricalInstallation Condition Report ◄ :leaving:

A visualinspection should firstly be made of the external condition of all electrical equipment whichis not concealed
Furtherdetailed inspection . including partial dismantling of equipment as required .should be carried out as agreed with the person ordering the work ( 612.2. )

Theseexample are not exhaustive . numbers in brackers are Regulation references .

ElectricalIntake Equipment :
□ Servicecable .
□Service cut-out / fuse .
□Meter tails – Distributor .
□ Metertails – Consumer .
□Metering equipment .
□Isolator .

Whereinadequacies in distributor’s equipment are encountered . it is recommendedthat the person ordering the report informs the appropriate authority .



 
Presence of Adequate Arrangements for Parallel or SwitchedAlternative Sources ( 551.6: 551.7 )

Automatic Disconnection of Supply . :13:
□ Main earthing / bonding arrangements ( 411.3 : Chap – 54 )

1) Presence of distributor’s earthing arrangement ( 542.1.2.1. :542.1.2.2. ) or
2) Adequacy of earthing conductor size ( 542.1.2.1 : 542.1.2.2. )or
3) Main protective earthing conductor connections ( 542.3.2.)
4) Accessibility of earthing conductor connections ( 543.3.2. )
5) Adequacy of main protective bonding conductor sizes ( 544.1. )
6) Main protective bonding conductor connections ( 543.3.2. :544.1.2. )
7) Accessibility of all protective bonding connections ( 543.3.2.)
8) Provision of earthing / bonding labels at all appropriate locations( 514.11. )

Other Methods of Protection .
( Where any of the methods listed below are Employed detailsshould be provided on separate sheets )

• Non-conducting location ( 418.2. )
• Earth-free local equipotential bonding ( 418.2. )
• Electrical separation ( Section 413: 418.3 )
• Double insulation ( Section 412 )
• Reinforced insulation (Section 412 )

 
542.1.2. Supply Arrangements .

542.1.2.1.
ForTN-S system . means shall be providedfor the main earthing terminal of the installation to be connected to theearthed point of the source of energy . Part of the connection may be formed bythe distributor’s lines and equipment .

542.1.2.2.
TN-C-S system . where protective multiple earthingis provided . means shall be provided for the main earthing terminal of theinstallation to be connected by the distributor to the neutral of the source ofenergy .

542.1.2.3.
Fora TT or IT system . the main earthing terminal shall beconnected via an earthing conductor to an earth electrode complying withRegulation ( 542.2. )

542.1.2.4.
Wherethe supply to an installation is at high voltage . protection against faultsbetween the high voltage supply ans earth shall be provided in accordance withSection 442.

(542.2. ) Earthing Arrangements .


 
ConditionReport Inspection Schedule for Domestic & Similar Premises with up to ( 100A ) Supply :waving:
Note:- This form is suitable for many types of smaller installation not exclusivelydomestic .

ConsumerUnit(s) - Distribution board(s)

4.1. Adequacy of working space / accessibility to Consumer Unit / Distribution board ( 132.12 : 513.1. ) [ Still the Same17[SUP]th[/SUP]Edition ]
4.2. Security of fixing (134.1.1. ) [ Still the Same – 17[SUP]th[/SUP]Edition ]
4.3. Condition of enclose(s) in term of ( IP ) rating etc ( 416.2. ) [ Still the Same17[SUP]th[/SUP] Edition ]
4.4. Condition of enclose(s) in term of ( Fire ) rating etc ( 526.5. ) [ Still the Same17[SUP]th[/SUP]Edition ]
4.5. Enclose not damaged / deteriorated so as to impair safety (621.2. (iii)) [ Still the Same17[SUP]th[/SUP] Edition ]
4.6. Presence of main linked switch ( as required by 537.1.4. ) [ Still the Same17[SUP]th[/SUP]Edition ]
4.7. Operation of main switch ( Functional check ) 612.13.2.
4.8. Manual operation of circuit-breakers and RCDs to provedisconnection ( 612.13.2. )
4.9. Correct identification of circuit details and protectivedevices ( 514.8.1. : 514.9.1. )
4.10. Presence of RCD quarterly test notice at or near Consumerunit / Distribution board ( 514.12.2. ) [ Still the Same17[SUP]th[/SUP]Edition ]
4.11. Presence of non-standard ( mixed ) cable colour warningnotice at or near Consumer unit / Distribution board ( 514.14. ) [ Still the Same17[SUP]th[/SUP]Edition ]
4.12. Presence of alternative supply warning notice at or near Consumerunit / Distribution board ( 514.15. )
4.13. Presence of other required labelling ( please specify ) –Section 514.
4.14. Examination of protective device(s) and base(s) : correcttype and rating ( no signs of unacceptable thermal damage . arcing oroverheating ( 421.1.3. ) [ Still the Same17[SUP]th[/SUP]Edition 421.3.]
4.15. Single-pole protective devices in line conductor only . (132.14.1 : 530.3.2. ) [ Still the Same17[SUP]th[/SUP]Edition ]
4.16. Protection against mechanical damage where cables enter Consumerunit / Distribution board ( 522.8.1. :522.8.11. – the same )
4.17. Protection against electromagnetic effects where cablesenter Consumer unit / Distribution board / Enclosures ( 521.5.1. ) [ Still the Same17[SUP]th[/SUP] Edition ]
4.18. RCD(s) provided for fault protection – includes RCBOs (411.4.9.: 411.5.2. – the same : 531.2. – the same )
4.19. RCD(s) provided for additional protection - includes RCBOs (411.3.3. : 415.1. - Still the Same )

OUTCOMES:- Acceptable condition ( Tick ) : Unacceptable condition State – C1 or C2 ) Improvementrecommended State – C3 ) Not Verified N/V ) Limitation LIM ) Not applicable N/A )

OUTCOME:- Use codes above . Provide additional comment where appropriate .
C1. C2 . & C3 . Coded items to be recorded in section K of the ConditionReport .
Furtherinvestigation required ? ( Y or N )
 
612.13.2. Equipment . suchas switchgear and controlgear assemblies . drives . control and interlocks .shall be subjected to a functional test to show that it is properly mounted .adjusted and installed in accordance with the relevant requirements of theseRegulations .

612.13.2. Assemblies . suchas switchgear and controgear assemblies . drivers . controls and interlocks .shall be subjected to a functional test to show that they are properly mounted. adjusted and insalled in accordance with the relevant requirements of theseRegulations .

514.9.1. ) for simple installations the forgoing information maybe given in a schedule . A durable copy of the schedule relating to a distribution board shall be provided within oradjacent to each Distribution board

514.9.1. ) For simpleinstallations the foregoing information may be given in a schedule . A durablecopy of the schedule relating to a Distribution board shall be provided within or adjacent to each Distributionboard . Any symbol used shall comply with BS-EN 60617.

514.9.2. Any symbol used shall comply with IEC-60617.

( 514.8.1. ) [ Still the Same17[SUP]th[/SUP]Edition ]

( 514.15. ) Where aninstallation includes alternative or additional sources of supply . warningnotices shall be affixed at the following locations in the installation .
( 514.15. ) Where aninstallation includes a generating set which is used as an additional source ofsupply in parallel with another source . waring notices shall be affixed at thefollowing locations in the installation .

( 522.8.1 ) A wiring system shall be selected and erected to avoidduring installation . use or maintenance . damage to the sheath or insulationof the cables and their terminations . The use of any lubricants that can havea detrimental effect on the cable or wiring system are not permitted .
( 522.8.1 ) A wiring system shall be selected and erectedto avoid during installation . use or maintenance . damage to the sheath orinsulation of the cables and their terminations.

( 411.4.9.) . Where an RCD is used to satisfy the requirements’ of Regulation 411.3.2.2. the maximum values of earth faultloop impedance in table 41.5. may be applied for non-delayed RCDs to BS-EN 61008-1and BS-EN 61009-1 for a nominal voltage ( Uo of230V ) In such cases . an overcurrentprotective device shall provide protection against overload current and faultcurrent in accordance with Chapter 43 .

( 411.4.9.) Where an RCD isused to satisfy the requirements’ of Regulation 411.3.2.2. the maximum values of earth fault loop impedance in table41.5. may be applied for non-delayed RCDs to BS-EN61008-1 and BS-EN 61009-1for final circuits not exceeding 32A . In such cases . an overcurrentprotective device shall provide protection against overload current and faultcurrent in accordance with Chapter 43 .

( 411.3.3. ) An exception to (i) is permitted for :
a) socket-outlets for use under the supervision of skilled orinstructed persons . or .
b) A specific labelled or otherwise suitably indentifiedsocket-outlet provided for connection of a particular item of equipment .
( 411.3.3. ) An exception to (i) is permitted for :
a) socket-outlets for use under the supervision of skilled orinstructed persons . e.g. in some commercial industrial locations . or
b) A specific labelled or otherwise suitably indentifiedsocket-outlet provided for connection of a particular item of equipment .

Note 1 & Note 2 - Thesame . 17[SUP]th[/SUP] Edition .
 
Symbols used in the Regulations :presents3:

( Ze ) That part of the earth fault loop impedance whichis external to the installation ( Ω ) –313.1.
( Zs ) Earth fault loop impedance ( Ω ) – 411.4.5.
( R1 ) Résistance of lineconductor of a distribution or final circuit ( Ω ) – Appx 6 Schedule of test results .
( R2 ) Résistance ofcircuit protective conductor ( CPC ) of a distribution or final circuit ( Ω ) – Appx 6 Schedule of test results .



 
ProtectionAgainst Overload Current . :presents3:

433.1. Every circuit shall be designed so that a small overload oflong duration is Unlikely to Occur .
433.1. Every circuit shall be designed so that a smalloverload of long duration is Unlikely to Occur .
 
□ Listall the Relevant documentation that need to be Completed for this ElectricalInstallation Condition Report . :19:

- NewElectrical Installation / “ Meaning “ Initial Verification .
( InitialInspection Test & Verification )

Definitions’ - p/36 . FirstAmendedment .
Verification ) All measures by means of which compliance ofthe Electrical Installation with the relevant requirements of ( BS-7671 ) are checked . comprisingInspection . Testing & Certification .

“ Certification & Reporting “
- Electrical Installation Condition Report .
- Schedule ofInspections . ( 2392-10 ) for New Installation Work Only :- First Amendedment. Tells us .
- Condition ReportInspection Schedule ) :- for Domestic andsimilar premises with up to 100A Supply .

632 – Initial Verification :

632.1. Following the Initial Verification required by Chapter 61 . an ElectricalInstallation Certificate together with schedules of inspection and schedules oftest results . shall be given to the person ordering the work . These schedulesshall be based on models given in Appendix 6 .

632.2. The schedules of test results shall indentify every circuit. including its related protective device(s) and shall record the results ofthe appropriate tests and measurements detailed in Chapter 61 .

632.3. The person or persons responsible for the design .construction . inspection & testing of the installation shall . asappropriate . give to the person ordering the work a Certificate which takesaccount of their respective responsibilities for the safety of thatinstallation . together with the schedules described in Regulation 632.1.

632.4. Defects or omissions revealed during inspection &testing of the installation work covered by the Certificate shall be made goodbefore the Certificate is issued . -&-s
 
□As an “ Inspector “ Existing Installation :19:
PeriodicInspection Report And Testing .

“ Certification & Reporting “
- ElectricalInstallation Certificate Report .
- Schedule of Inspections .
- Schedule of Test Results .

634 – Periodic Inspection & Testing .
634.1. Following the periodic inspection & testing describedin Chapter 62 . an Electrical Installation Certificate Report . together withschedules of inspection & schedules of test results . shall be given by theperson carrying out the inspection . or a person authorized to act on theirbehalf . to the person ordering the inspection . these schedules shall be basedon the models given in Appendix 6 . The schedule of test results shall recordthe results of the appropriate tests required of Chapter 61 .

634.2. Any damage . deterioration . defects . dangerous conditionsand non-compliance with the requirements of the regulations . which may giverise to danger . together with any significant limitations of the inspection& testing . including their reasons . shall be recorded .

621.5. Periodic inspection& testing shall be undertaken by a Competent Person .

Definitions’ - p/25 . FirstAmendedment .
Competent Person : Aperson who possesses sufficient technical knowledge . relevant practical skills& experience for the nature of the Electrcal Work Undertaken & is ableat all times to prevent danger and . where appropriate . injury to him /herself and others .

Inspection& Testing )- are Two different Words “ Meaning “

Definitions’ - p/36 . FirstAmendedment .
Testing ) Implementation of measuresto assess an Electrical Installation by means of which its effectiveness isproved . This includes ascertaining values by means of appropriate measuring instruments. where measured values are not detectable by Inspection .

Definitions’ - p/29 . FirstAmendedment .
Inspection ) Examination of an ElectricalInstallation using all the senses as appropriate .
 

Reply to ***Cont../ Useful Information for Electricians & Apprentices*** in the Australia area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
273
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
770
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
777

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top