amberleaf

O.S.G.. The use of other methods’ of determining Maximum Demand is Not Precludedwhere Specified by the Installation Designer

FirstlyI make no Apologies for the Way am Writing on any Matters . it can be a first day Apprentice or some one Needing aJog of Memory .
Sowe are all in the Same Boat . “ To Learn “

For the Apprentices . The Day we stop learning is the Day we hang Upour Tool-Bag

CookerDesign Current Calculations

Thefirst thing you have to do is get Your Head around the Calculations !!

(From a Design point of View ) 2392-10

DomesticInstallation Oven(s) & Hob(s) are to be Calculated upon their MAXIMUM LOADING
Startwith a simple Calculation ( An Oven has a rating of 2kW ) 2000

(I = P/V ) Formula … I = 2000 ÷ 230V = 8.70A …. Weare Using the Unit Amps


2392-10/ Domestic Installation Oven(s)

Ovenhas 4 Rings ( 2 x 1kW ) & ( 2 x 1.5kW ) & Grill ( 2kW ) & Oven (3kW )

-Controlled via a CookerSwitch with a Socket outlet .

Asa Designer . we’ll have to Apply Diversity ??

Important )- Diversity allowance to be Applied to the FULL LOAD CURRENT for CookingAppliances .

TheO.S.G. is telling us . Purpose of the Final Circuit fed from theConductors )
O.S.G.Table 1B p/97 – column (3) Cooking Appliances → At the Top of the Page Note : Type ofPremises ( 2392-10 → Household Installations ) Domestic Installation(s)

DomesticInstallation(s) Only O.S.G. - 10A + 30% f.l – Full Load ) of connected Cooking Appliances in the Excess of 10A+ 5A if a socket-outlet is incorporated in the Control Unit . ( C.C.U. ) – 45A + 13A Socket Switched with Neon .

Fromyour point of View ( The First 10A ofthe rated current plus 30% of the reminder ( Plus) 5A if the Control Unit incorporates s Socket.

Calculations)- You bank “ Hold OFF“ the first 10 Amps of the Maximum Load Current )
The10A will be used at the End of the Calculations’

-So your Work out the Total Power Rating & then calculate the Full Load Current

Calculations)- Power = ( 2 x 1 ) + ( 2 x 1.5 ) + ( 2+ 3 ) = 10kW

I= 10000 ÷ 230V = 43.48A … round it up to the first four numbers43.47826087 ( 48 ) 43.48A

UsingDiversity allowance stated ↑↑ ( 43.48A sub 10A = 33.48A )

I= 33.48 x 30 ÷ 100 = 10.04A

Youradding the ( 5A ) for Socket outlet . I = 10A + 10.04 + 5A = 25.04A )- Asa Designer this is your Expected Current Demand .

Remember )- Supply Cables Rated to suit DesignCurrent ( Iz ) :)
 
Thedifference between the First Amendment & 17[SUP]th[/SUP]Edition

Section 706 : 706.1. p/188 .

Theonly wording that is changed . added on .

This section does not apply to electrical systems as defined inBS-7909 used in structures . sets . mobileunits etc as used for public or private events , touring shows . theatrical .radio . TV or film productions & similar activities of the entertainmentindustry . :19:


 
Thedifference between the First Amendment & 17[SUP]th[/SUP]Edition

Theonly wording that is changed .

Section 708 : 708.411.4.. p/223 . TN system ◄ . :19:
The Electricity Safety . Quality & Continuity Regulations 2002 ( ESQCR ) prohibit the connection of aPME earthing facility to any metalwork in a leisure accommodation vehicle (including a caravan )

This does not preclude the use of a PME earthing facility as themeans of earthing for other purposes . such as to the installations ofpermanent buildings .

Note : The requirements of other section of Part 7 . may alsoapply .



 
Thedifference between the First Amendment & 17[SUP]th[/SUP]Edition

Theonly wording that is changed .

708.553.1. Plugs & Sockets-outlets . :19:
708.53.1.8. N/C .
708.53.1.9. N/C .
708.53.1.10. N/C .
708.53.1.11. N/C .

708.53.1.12. Each socket-outlet shall be protected by anindividual overcurrent protective device . in accordance with the requirementsof Chapter 43 .

A fixed connection for the supply to each leisure accommodationvehicle ( including caravans ) or tentshall be protected individually by an overcurrent protective device . inaccordance with the requirements of Chapter 43 .

708.53.1.13. N/C .
708.53.1.14. Socket-outletprotective conductors shall not be connected to a PME earthing facility .

The protective conductor of each socket-outlet shall be connectedto an Earth Electrode & therequirements of Regulation 411.5. for aTT system shall be complied with

 
Thedifference between the First Amendment & 17[SUP]th[/SUP]Edition

Theonly wording that is changed . Section 709 .

709.1. N/C
709.3. N/C
709.313. N/C
709.41. N/C
709.41.3.5. N/C
709.41.3.6. N/C
709.411.4. TN-system . The Electricity safety . Quality & ContinuityRegulations 2002 ( ESQCR ) prohibit theconnection of a PME earthing facility to any metalwork in a boat .

This does not preclude the use of a PME earthing facility as themeans of earthing for other purposes . such as to the installations of permanentbuildings .

Note : The requirements ofother sections of Part 7 may also apply .

 
709.5. N/C
709.512.2. N/C
709.512.2.1. N/C
709.512.2.1.2. N/C
709.512.2.1.2.3. N/C
709.512.2.1.2.4. N/C
709.521. N/C
709.521.1. N/C
709.521.1.4. . N/C
709.521.1.5. The following wiring systems . etc . ii) Non-sheathed cables in cable management systems . rest are the same .
709.521.1.6. . N/C
709.521.1.7. . N/C
709.521.1.8. . N/C
709.531. . N/C
709.531.2. .
709.533. . N/C
709.537.
709.537.2. N/C
709.537.2.1. N/C
709.537.2.1.1. N/C
709.553. N/C
709.553.1. N/C
709.553.1.8. N/C
709.553.1.9. N/C
709.553.1.10.. N/C
709.553.1.11.. N/C
709.553.1.12.. N/C
709.553.1.13. N/C

709.553.1.14. Socket-outletprotective conductors shall not be connected to a PME earthng facility .

Fig – 709.1. p/228 .

Main Switch . L1 / N / PE .
Main Switch . L / N / PE . – drawing the same .

Fig – 709.2. p/229 . – drawing the same .

The rest all the same . / The rest all the same . Instructions for Electricity Supply .

 
Section740 :

740.1. N/C
740.1.1. N/C . Scope :- Note / Note . The permanent electrical installation is excludedfrom the scope .
740.3. N/C .
740.31. N/C .
740.313. N/C .
740.313.1.1. N/C .
740.313.3. ( Phase to Line ) N/C .
740.4. N/C .
740.4.1. N/C .
740.410.3. N/C .

( NEW ) 740.410.3.5. - The protective measures of obstacles ( Regulation 417.2 ) is not permitted .
Placingout of arms reach is acceptable for electric dodgems ( Regulation 740.55.9. )

740.410.3.6. N/C .

( The Electricity at Work Regulation “ 1989 “ ) Design . Erection – Verification ElectricalInstallation in Fairgrounds . ( YES )

740.411. N/C .
740.411.4. TN-
( NEW ) 740.411.4.1. A PME earthing facility shall not be used asthe means of earthing for an installation falling within the scope of thissection .
Note : The ESQCR . prohibitthe use of a PME earthing facility asthe means of earthing for the installation of a caravan or similar construction.
( NEW ) 740.411.4.3. Where the type of system earthing is . TN- . a PEN conductor shall not be used downstream ofthe similar construction .
740.411.6. N/C .
740.415. N/C .
740.415.1. N/C .
740.415.2. N/C .
740.415.2.1. N/C .
740.415.2. N/C .
740.415.2.1. N/C .
740.42. N/C .
740.422.3. N/C .
740.422.3.7. N/C . -
 
740.5. N/C .
740.51. N/C .
740.512. N/C
740.512.2. N/C
740.52. N/C
740.521. N/C
740.521.1. – Conduit systemsshall comply with the relevant part of the BS-EN . That’s . it Wording . Rest ok .

NOTE . 2 ) Where mechanical protection of cables is provided . p/221
The following methods are considered to meet the aboverequirements . p/270

(i) ◄ Conduit systems shall . etc .
(ii) ◄ Cable trunking systems & cable . etc .

NOTE . 3 ) Cable of type H07RNF . Changed to NOTE 2 . Restok .

740.526. N/C
740.53. N/C
740.537.1. N/C
740.537.2.1.1. N/C
740.537.2.2. N/C
740.55. N/C
740.55.1. N/C
740.55.1.1. N/C
740.55.1.2. N/C
740.55.1.3. N/C
740.55.1.4. N/C
740.55.1.5. N/C
740.55.3. N/C
740.55.3.1. N/C
740.55.3.2. N/C
740.55.5. N/C
740.55.7. N/C
740.55.8. N/C
740.55.9. N/C
740.551. N/C
740.551.8. N/C
740.6. N/C
 
Appendix2 ( Informative ) p/240

StatutoryRegulations & Associated Memoranda .

( vi ) Theatres & otherplaces licensed for public ETC.
conditions of licence under : (a) in England& Wales. The local Government ( Miscellaneous provisions ) Act 1982.
(a) The Secretary of state for the Home Department .

Statutory Regulations & Associated Memoranda . p/292

( vi ) Theatres & otherplaces licensed for public ETC.
conditions of licence under : (a) in England& Wales. The local Government licensingAct 2003.
(a) Department for Culture . Media & Sport .


 
UsefulJunk : ( ESQC ) Whereto find it .

17[SUP]th[/SUP] Edition p/241 & FirstAmendment . p293

UnderRegulation 28 . of the Electricity Safety . Quality & Continuity Regulation 2002 . requires distributors to provide the following information to relevantpersons free of charge .

- The maximum prospective short-circuit currentat the supply terminals .
- The maximum earth loop impedance of the earthfault path outside the installation ( Ze )
- The type & rating of the distributorsprotective device or devices nearest to the supply terminals
- The type of earthing system applicable to theconnection .
- The number of phases of the supply
- The frequency of the supply & the extentof the permitted variations .
- The voltage of the supply & the extent ofthe permitted variations .




 
First Amendment . p/4

Introduction to BS-7671:2008 .

Note 2 )- Particular attention is drawn to Section 701 . This section now allows socket-outlets (Other than SELV & shaver supply units to BS-EN 61558-2-5 ) to be installedin locations containing a bath or shower ( 3m ) horizontally beyond theboundary of zone 1 .
 
SWA. ?? Example . :hurray:

□ The Wire Armouring is ( Steel ) & therefore is ( Conductive ) The steel is covered by an Exposed Oversheathof Insulation . So not Exposed .
□ The cable is Terminated on mostinstallation(s) with ( Brass-glands ) which are ( Conductive ) These parts aretherefore ( Exposed conductive parts ) these may also be covered with ( PVC. Shrouds )

“ Function(s) “

TheArmouring is to protect the Cable against ( Mechanical damage ) & to allow the cableto be run out of safe Zone .
TheArmouring is connected to Earth to enable the supply to be ( Automatically disconnected) by the ( Circuit Protective Device ) Underthis Fault Condition(s)

Types of ProtectiveConductor . 543.2. :svengo:

543.2.1. A protectiveconductor may consist of ( One ) or ( More ) of the following .

i) A single-core cable .
ii) A conductor in a cable.
iii) A An insulated or bare conductor in a common enclose withinsulated live conductor(s) .
iv) A fixed bare orinsulated conductor .
v) A metal covering . for example . ( THE sheath . screen orarmouring of a cable )
vi) A metal conduit . metallic cable management system or otherenclosure or electrically continuous support system for conductors .
vii) An (Extraneous-conductive-part ) complying with Regulation 543.2.6.
 
Defining Protective Conductor . p/32

Protective Conductor isdefined in ( PE ) (BS-7671:2008 ) First Amendment . underPart 2 Definitions as .

A conductor used for some measures of protection against electricshock & intended for connecting together any of the following parts .

- Exposed conductive parts.
- Extraneous conductiveparts .
- The main earthing terminal .
- Earth electrode(s) .
- The earthed point of the source . or an artificial neutral .
 
Earthing Arrangements for Protective Purposes . 543.6. :svengo:

543.6.1. – Where overcurrent protective devices areused for fault protection . the protective conductor shall be incorporated inthe same wiring system as the live conductors or in their immediate proximity .




 
134.1.4.p/19p/21.
Erection )- Terminating the Cable Ends of S.W.A. cables . :20:

BS-7671:2008. Fundamental requirements set out in Regulation . FirstAmendment / 17[SUP]th[/SUP] Edition

Everyelectrical joint & connection shall be of proper construction as regards Conductance . Insulation. Mechanical strength & Protection .

 

Reply to ***Cont../ Useful Information for Electricians & Apprentices*** in the Australia area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
273
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
770
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
777

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top