***Cont../ Useful Information for Electricians & Apprentices***
A
amberleaf
O.S.G.. The use of other methods’ of determining Maximum Demand is Not Precludedwhere Specified by the Installation Designer
FirstlyI make no Apologies for the Way am Writing on any Matters . it can be a first day Apprentice or some one Needing aJog of Memory .
Sowe are all in the Same Boat . “ To Learn “
For the Apprentices . The Day we stop learning is the Day we hang Upour Tool-Bag
CookerDesign Current Calculations
Thefirst thing you have to do is get Your Head around the Calculations !!
(From a Design point of View ) 2392-10
DomesticInstallation Oven(s) & Hob(s) are to be Calculated upon their MAXIMUM LOADING
Startwith a simple Calculation ( An Oven has a rating of 2kW ) 2000
(I = P/V ) Formula … I = 2000 ÷ 230V = 8.70A …. Weare Using the Unit Amps
2392-10/ Domestic Installation Oven(s)
Ovenhas 4 Rings ( 2 x 1kW ) & ( 2 x 1.5kW ) & Grill ( 2kW ) & Oven (3kW )
-Controlled via a CookerSwitch with a Socket outlet .
Asa Designer . we’ll have to Apply Diversity ??
Important )- Diversity allowance to be Applied to the FULL LOAD CURRENT for CookingAppliances .
TheO.S.G. is telling us . Purpose of the Final Circuit fed from theConductors )
O.S.G.Table 1B p/97 – column (3) Cooking Appliances → At the Top of the Page Note : Type ofPremises ( 2392-10 → Household Installations ) Domestic Installation(s)
DomesticInstallation(s) Only O.S.G. - 10A + 30% f.l – Full Load ) of connected Cooking Appliances in the Excess of 10A+ 5A if a socket-outlet is incorporated in the Control Unit . ( C.C.U. ) – 45A + 13A Socket Switched with Neon .
Fromyour point of View ( The First 10A ofthe rated current plus 30% of the reminder ( Plus) 5A if the Control Unit incorporates s Socket.
Calculations)- You bank “ Hold OFF“ the first 10 Amps of the Maximum Load Current )
The10A will be used at the End of the Calculations’
-So your Work out the Total Power Rating & then calculate the Full Load Current
Calculations)- Power = ( 2 x 1 ) + ( 2 x 1.5 ) + ( 2+ 3 ) = 10kW
I= 10000 ÷ 230V = 43.48A … round it up to the first four numbers43.47826087 ( 48 ) 43.48A
UsingDiversity allowance stated ↑↑ ( 43.48A sub 10A = 33.48A )
I= 33.48 x 30 ÷ 100 = 10.04A
Youradding the ( 5A ) for Socket outlet . I = 10A + 10.04 + 5A = 25.04A )- Asa Designer this is your Expected Current Demand .
Remember )- Supply Cables Rated to suit DesignCurrent ( Iz ) :)
2392-10 “ Testing “
Meansfor Disconnecting the Earthing Conductor .
542.4.2. – requires means fordisconnection of the Earthing Conductor . to be provided at or near the ( MET ) of aninstallation to “ Facilitate measurement“ of the Résistance of the Earthing arrangements .
Meansof Earthing “ . Earthing Conductor → [ Bolted Link] → Connections : Circuit protective conductor : Mainprotective bonding conductors :
Functionalearthing conductors – if required : & lighting protection system bonding conductors - if Any .
Inorder to decide whether or not a specific “ Item “ is an Extraneous-conductive-part :
Q). is the item liable to introduce a potential . generally . EarthPotential .
Isthe item liable to introduce a “potential to a person “ or Livestock . who may be in contact with another potential .
Tointroduce a “ potential “ to such a person . the item must not only be apotential . but must be able to “ Introduce the potential “ introduction of the potential requires [ Two-things ]
- Thefirst is that the item [ or a Conducting item in electrical contact with it ] must be accessible to be [ Touched by a part of such a person’s body ]
- Thesecond is that any [ Electrical résistance ] through which the item is connectedto the [ Source ] of its potential – such as the résistanceconnecting an item with Earth potential . must not be so great as to preventthe potential being introduced to a person – due to voltage drop in the résistance.
Isthe item part of the Installation .
Onlyan item which does not form part of the electrical installation concerned may be an [ Extraneous-conductive-part ] however . items serving a purely non-electrical purpose within theinstallation should not be ruled out . moreover . items forming part of anotherinstallation are not precluded .
Thirdpart “ & NOT forming part of the ElectricalInstallation .
Thispart of the definition limits [ Extraneous-conductive-parts ] tobeing items which Do Not From Part . of the electrical installation in question .
Therefore. items which may be [ Extraneous-conductive-parts include ] the following . which are referred to inRegulation – 411.3.1.2. with regard to “ Main Protective bondingconductor “ provided such items arealso covered by other parts of the definition referred .
Waterinstallation pipes .
Gasinstallation pipes .. Etc .
Anyother non-electrical items which fallwithin the definition may be Extraneous-conductive-parts .
Althoughthe definition precludes items forming part of the electrical installation frombeing Extraneous-conductive-parts .items . serving a purely non-electrical purpose within an electricalinstallation should NOT be ruled OUT . such items may include .
A Metalsupport system or carrier for cables having non-metallicsheaths which is not required to be earthed .
Moreover– items forming part of another electrical installation – that is . aninstallation supplied from a different origin or having a separate earthing arrangements .
Are not precluded from being . Extraneous-conductive-parts . such items mayinclude . for Example . a metal conduit or the metal sheath or armouring of acable entering the premises from another building .
SpecialInstallations or Locations : 2011:
Theuse of SELV.
701: locations containing a bath or Shower .
701.414. Protection against electric shock .
701.512.3. Erection of switchgear . control gear &accessories .
701.55. Current – using equipment .
701.753. Electric floor heating systems .
702. Swimming pools . Application ofprotective measures against electric shock .
702.414. Protection against electric shock .
702.522.24. Junction boxes .
702.53. Switchgear & controlgear .
702.55. Other equipment .
703. Hot air saunas . Protection against electricshock .
704. Construction & demolition siteinstallations . 704.410.3. - 704.414. Protection against electric shock .
705. Agricultural & horticultural premises . 705.414. Protection against electricshock .
706. Conducting locations . 706.410.3.10. Protection against electric shock .
711. Exhibitions . shows & stands . 711.414.4.5. . Protection againstelectric shock .
712. Solar photovoltaic ( PV ) power supply systems . 712.414. Protection against electricshock .
Emergency Lighting :
Checklist .
For Emergency Lighting .
Non-Maintained . -&-s . The light only operates whenthe [ Normal main supply fails ] Emergency Lighting only .
( Permanent L ./ N )
Maintained . -&-s. The lighting operates normally & continues to operate when the normalmains supply fails [ Mains lighting& Emergency lighting ]
( Switched L : Permanent L . / N )
Final Exit Sign’s:
To provide illumination of escape routes .
Junctions : Install within 2 metres of escape route junctions .
Corridors : Install within 2 metres . horizontal distance of achange of direction in an escape route .
Stairways : Installwithin 2 metres . horizontal distance of achange in floor level or stairs [ each tread to receive direct light ]
Final Exit : Install externally within 2 metres horizontal distance of any final exits . Note : that sufficient light will be needed tomuster a roll call .
Alarm Exit : Firealarms . first aid points & fire fighting equipment . installed within 2metres horizontal distance .
Escalators : Shouldnot be used as an escape route . butrequires the same illumination to protect Uses on it when the supply fails .
Toilets : Install in all toilets exceeding [ 8m[SUP]2[/SUP] ] area or where natural light is not present .
Lifts : Toprovide emergency illumination in alllifts .
Control Rooms : Motorgenerator . control & plant rooms for essential & safety services .
Open Areas : Open rooms either with a particular hazard . an escape route passing through or largerthan [ 60m[SUP]2[/SUP] ]
Hazardous Areas : Areas of high risk should beilluminated to [ 10% ] of normal lighting or [ 15 lux ] whichever is greater .
Lighting Requirements .
When luminaires have been sited to cover the locations[ Above ] ▲ additional luminaires may be required toensure minimum lighting levels areachieved .
Manufactures provide spacing tables for this purpose . Spacingtables advise how far to locate the first luminaire . then how far . apart otherluminaires should be located for a given mounting height . Installation to the spacing’s will ensure thelighting levels will be achieved .
Escape route corridors : 1 lux minimum on the centre line of the escaperoute .
Open Areas : 0.5lux minimum on the centre core to within 0.5m of the walls .
Exit signs : Signs should apply to the European SignsDirective & be either . back illuminated or have an Emergency luminairewithin 2m of horizontal height . Signs should be of thesame formal throughout the building .
Form . EmergencyLighting design guide . 4 Edition 2008 .
Workplace directive – 89/654 .
Is 5 or more people areemployed there must be a writtenrecord of the assessments findings & the action taken . -&-s Exams
Maintained Emergency Luminaire :
A Luminaire containing one or more lamps all of whichoperate from the normal supply . or fromthe emergency supply at all material times .
Non - Maintained Emergency Luminaire :
A Luminaire containing one or more lamps . whichoperate from the emergency supply ONLY upon failure of the normal mains supply.
Normal Lighting :
All permanently installed [ Artificial ] lighting operating from the normal electricalsupply that in the absence of adequate [ daylight ] is intended for use duringthe whole time that the premises are Occupied .
Rated duration :
The manufactures declared duration . specifying the time for which the emergency lightingwill provide the rated lumen output after mains failure . this may be for anyreasonable period but in normally [ one or three hours . ] -&-s Exams
Rated Load : Themaximum load that may be connected to the system & will be supplied for theduration .
Re – charge period :
The time necessary for the [ Batteries ] to regain sufficient capacity to achieve their ratedduration .
Self – contained emergency luminaire or Single point luminaire :
A luminaire or sign . providing maintained or .Non-maintained emergency lighting in which all the elements such as the battery. lamp & the control unit are contained within the housing or within one metre of the housing .
Slave or Centrally supplied luminaire :
An emergency luminaire without its own batteriesdesigned to work with a central battery system .
Usefuljunk :
EdisonBase – Light Bulb’s . 612.6. (ii) [ Indicates ] 230V / E27 . male screw base.
E27 . the number “ 27 “ simply signifiesthe number of millimetres in diameter of the base itself . [ 27mm ]
Zones : Previous 16[SUP]th[/SUP] Edition .
Identifiedzones within the bathroom to [ Illustrate] what typeof electrics in the Bathroom . can be usedor installed .
Zones: 17[SUP]th[/SUP]Edition . “ Updated “
Takeinto account . Windows : doors : walls ceiling & partitions . [2392-10 - You are . Assessing the level of Risk in each Zone ]
Circuits in a Bath or Shower room . both power & lightingmust be Additionally protected by an RCD . 30mA - 701.411.3.3.: 314.1 (iv) : 531.2.4. Unwanted tripping .
17[SUP]th[/SUP]Edition – reinforces this .
Bath or Shower islocated in a building with Protective equipotential bonding in place . 411.3.1.2.
Mainprotective bonding conductor(s) . (i) Water installation pipes . [ Extraneous conductive parts ]
p/27 . Equipotential bonding. Electrical connection maintaining various . Exposed-conductive-parts & Extraneous-conductive-parts
• 2392-10 : Exams
Inyour own words . State . the meaning of a circuit overload & short-circuit protection . What will provide this type of protection !! :icon_bs:
p/35 . RCBO .
Wording .
Residualcurrent operated switching device . designed to perform the functions ofprotection against [ Overload & / or Short-circuit]
Bathroomequipment . selection & erection requirements .
Equipmentin “ Zone 1& 2 “ shall be at least IPX4 . Regulation . 701.512.2.( ii )
Equipmentin “ Zone 0 “ shall be at least IPX7 . Regulation . 701.512.2.( i )
Equipment exposed to cleaning jets to be at least IPX5. . Regulation . 701.512.2.
Zone 0 “ only 12V currentusing equipment . complying with a relevant standard is allowed . 701.55 .
(ii) - Fixed & permanently connected .
(iii) - SELV . safety source located outside of Zone .
in Zone 1 “ only :
Water/pumps. electrical shower(s) . Shower/pumps . ventilation equipment . towel rails . waterheaters . luminaires & 25V - SELV equipment is allowed . 701.55.
Fixed& permanently connected . SELV safety . source located outside of Zone . 0. 1. & 2 .
in Zone 2 “ only :
12V. SELV switches & shaver supply .socket-outlets to BS-EN-61558-2-5 . are the onlyallowed switchgear or accessories . 701.512.3.
SELV. safety source located outside of Zone .
2392-10: IP rating. dependent upon it’s location in the room . :banghead:
GN-32012 :
Classification of danger & non-compliances ( foruse during periodic inspection & testing )
Classification of danger or non-compliances [Description ]
C1: Danger present . Risk of injury . immediateremedial action required .
Notes &guidance :
To be cited insituations which cannot be left . it is suggested that these are rectified orpossibly . isolation may be recommended or necessary . examples : includeaccessible bare live parts , badly damaged equipment with risk of access tolive parts . incorrect polarity . arcing found in switchgear .
C2: potentially dangerous – urgent remedial action required .
To be cited insituations that . whilst urgent , do not require immediate remedial action . .examples : include a non-earthed installation . ( this requires a further faultto manifest injury ) fundamentally undersized cables . earth loop faultimpedance values greater than ( BS-7671) requirements . a “ borrowed “ neutral . equipment with inappropriatelyselected IP . ( this may be . C1 if severe ) insulationreadings under ( 1M )connections not terminated within appropriate enclosures .
C3: Improvements required .
To be cited where .C1 or C2 . do not apply . examples : include the absenceof most warning notices . absence of therequired diagrams & charts . no or incorrect marking of conductors atterminations , absence of an ( RCD ) specified for additional protection . ( Where the circuit otherwise tests as normal )
GN-32012 : ( IR )
InsulationRésistance of a . Three-phase 4core power cable .
The cable is tested.
Insulation Résistancetest on . 4-core power cable :
Test 1 : L1 / L2 .
Test 2 : L1 / L3 .
Test 3 : L2 / L3 .
Test 4 : L1 + L2 +L3 – ( connected together ) to Neutral
The lowest value ofthese tests . is recorded as “ between Live conductors “
Test 5 : L1 + L2 + (connected together ) to Earth .
The lowest value ofthese tests . is recorded as “ between Live conductors & Earth “
Note :it is essential for . Tests 5 & 6 that the cable earth is connected to the installation earthing terminal.
( IR ) readings obtained should be not less than theminimum values referred to table.BS-7671:2011 . Table61 .
GN-32012 : ( IR )
612.4.1. : SELV tests .
Test type .
Basic insulation .between Line conductors & all other circuits including other . SELV &PELV . & low voltage circuits . ( 250V – d.c.) Minimum – 0.5M .
Line / Earth : Between al SELV live parts & Earth .
Note: in situations where the SELV conductorsare separated by just ( insulation ) such as within a ( multicorecable ) with low voltage circuits . then the test voltage shall be increasedto ( 500V d.c.) & the (IR ) shall be not less than . ( 1M )
612.4.2. : PELV tests .
Test type .
Note: in situations where the PELV conductorsare separated by just ( insulation ) such as within a ( multicorecable ) with low voltage circuits . then the test voltage shall be increasedto ( 500V d.c. ) & the ( IR ) shall be not less than . ( 1M )
Teatmethod 2 : for circuits .
Instrument : use a low-résistance ohmmeter for test . ◄► Exams – 2391-10 .
One lead of thetest instrument is connected to the earth terminal at the distribution board . via a length of test cable or ( Wandering Lead ) the other test lead is used to make contactwith the protective conductor at . various points on the circuit under test .e.g. luminaires. switches . spursoutlets . etc . the résistance ofthe ( Wandering Lead ) & the test leads areeither auto-nulled prior to making the test ormeasured & subtracted from measured readings .
This test measuresthe continuity résistance of the circuit protective conductors ( R[SUP]2[/SUP] ) which should be ( Recorded on the Scheduleof Test Results )
Note: Parallel earth paths & effects on thereadings ) ◄► Exams – 2391-10 .
Exams – 2391-10 . Wording : Mainswitch [ OFF ] all fuses removed . circuit/ breakers [ OFF ]
Results : for test method 2 :
The results shouldfirst & foremost indicate ( No Open Circuit ) in the protective conductors . for insulatedwiring systems installed in conditions where accessory boxes & similar are not connected tofabric or other elements that mat be earthed . then the measurement will equate to the protective conductor résistance ( R[SUP]2[/SUP] ) this test can detect poor continuity atjunctions & connections since . for a New installation with new accessories. the contribution of résistance of healthy connections is negligible & canbe ignored . thus by employing the résistance data for copper conductors .
Expected values forhealthy cable & connections can be checked .
Example . Radialcircuit . of length about . 55m with a 2.5mm[SUP]2[/SUP] copper protectiveconductor should have an ( R[SUP]2[/SUP] ) résistance .
Length of circuitis 55m .
Résistance of cableis . 7.41 m/m - at 20°C .
Theoretical minimumd.c. résistance- ( 55 x 7.41 ) / 1000 = 0.41
When verifying this circuitthe . Inspector . should be looking for a reading of that order . say . 0.4 to 05 . if the circuit had several outlets . thusmeasuring that the protective conductor was broken & connected in screwterminals at each accessory . then a slightly higher value may be measured . asthere would be some résistance at the termin
( IR ) Testing . 2392-10 . / 2394 .Exams . Q/As .
For circuits containing [two-way switching or two-way & intermediate switching ] the switches must be [ operated one at a time] at a time & the circuits subjectedto additional ( IR) test in these configurations .
Testing . .
Earth fault loop impedance: Verification . 612.9.
Where limitation ofearth fault loop impedance is part of a protective measure .then it is fundamental that the [ InitialVerification ] process includesverification of earth fault loop impedances .
The earth faultcurrent loop comprises the followingelements . starting at the point of fault on the line – earth loop .
Circuit protective conductor.
Main earthingterminal & earthing conductor .
TN-system’s the metallic return path or . in the case of . TT & IT . systems .the earth return path .
Path through theearthed neutral point of the transformer .
Source line windings . &
Line conductor fromthe source to the point of fault .
612.8. - 612.9. :
There are [ Two-methods ] used for verifying total . earth faultloop impedance for a circuit :
- Measurement oftotal earth fault loop impedance ( Zs )using an instrument .
- Measurement of ( R[SUP]1[/SUP] + R[SUP]2[/SUP] ) during continuity testing of a circuit . & addition to the measured earth faultloop impedance external to that circuit ( Ze )
Exams . Instrument : use an earthfault loop impedance tester . for this test .
amberleaf,
Dan,