Hi, working on a job, guy wants all appliances on grid switch, the oven needs 32amp supply so best way I can think of is 6mm into contactor 6mm to cooker then 1.0mm from contactor to 20amp DP in grid switch to keep it on grid???
Thing confusing me is the grid is on a 4mm 32amp at the moment and the 6mm will be from a 32amp MCB but that will mean the DP controlling contactor is on one circuit and oven fed between contactor is on another
32A MCB 6mm in and 6mm out contactor to oven, 1.5mm from supply 6mm at contactor to fuse spur then 1.0mm to 20amp DP grid switch, L from Spur and SL back to A1 terminal with N link from load side of spur back to A2, sorry I appreciate your help just wanting to understand
As Dave says and shows in my drawing the neutral can go direct to the coil from the supply neutral. Only the line need go through the spur/fuse.
Reply to Contactor for oven in the UK Electrical Forum area at ElectriciansForums.net
I've put a 2 way unit inside kitchen cupboards before now if we were re-using the original cooker supply but the customer wanted 2 x 16A ovens. I...
Check the clearance between the back panel and/or terminal cover that you've removed. Look for small burn marks.