ryan77

-
Joined
Jan 4, 2013
Messages
18
Reaction score
1
Location
wawwick
Replacing cracked cover on ring circuit, the mcb was turned off , circuit dead
tested with volt meter and got beep continuity on L-N L-E N-E, .
Ring working before replaced the socket front .

Im thinking because appliances with neons pugged in on the ring
and it being TNC system that this accountts for it, but wondering if this right ?
All commets welcome.
 
You haven't tested the circuit properly. Use the proper tester, continuity tester, insulation resistance tester, and test it as you are supposed to do for a ring. r1, rn, r2, R1+R2, then insulation resistance, the will highlight any problems that maybe present, or not as the case may be.

Cheers…………Howard
 
Replacing cracked cover on ring circuit, the mcb was turned off , circuit dead
tested with volt meter and got beep continuity on L-N L-E N-E, .
Ring working before replaced the socket front .

Im thinking because appliances with neons pugged in on the ring
and it being TNC system that this accountts for it, but wondering if this right ?
All commets welcome.


christ kid...

go away, get decent test gear to carry out the job to a satisfactory level and learn how to use it...(preferably not on other peoples property/s)...

and i`ll give you a clue: an AVI is not how we do an r1 r2 rn...is it..

go invest in a low resistance ohmmeter will you....one that can measure to 2 decimal places...
 
You haven't tested the circuit properly. Use the proper tester, continuity tester, insulation resistance tester, and test it as you are supposed to do for a ring. r1, rn, r2, R1+R2, then insulation resistance, the will highlight any problems that maybe present, or not as the case may be.

Cheers…………Howard
scary innit....
 

Reply to Continuity at socket on ring main in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
709
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
1K
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
3K

Similar threads

Continuity of the suspect cable appears fine all cores, from this I could work out the length of it and it really doesn’t appear looking at the...
Replies
2
Views
386
  • Question
They ought to be able to check for the voltage going completely off using one MCB off at a time to confirm that. That would be my assumption...
Replies
9
Views
904

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top