Converting to a TT system... possibly | on ElectriciansForums
Guest viewing is limited

Discuss Converting to a TT system... possibly in the UK Electrical Forum area at ElectriciansForums.net

Joined
Dec 24, 2016
Messages
404
Reaction score
92
Location
london
1.25ohm external earth fault loop impedance on TN-S supply to building

Supply authority stated our only option is a TT conversion as they will not covert to PME.

What would be my best course of action when converting to a TT as the building is quite old and i do not want a 100ma main switch for diversity reasons and nuisance tripping, so Would it be suitable to convert to TT and have all final circuits in a RCBO with a board charge?
 
Thank you Midwest looking at page 33 is quite useful

on a side note i want to avoid hammering a TT rod through a gas pipe, i have never installed an Earth mat are these a viable option as the property is surrounded by soil/grass
 
Thank you Midwest looking at page 33 is quite useful

on a side note i want to avoid hammering a TT rod through a gas pipe, i have never installed an Earth mat are these a viable option as the property is surrounded by soil/grass
A sweep with a cat, not the feline kind, should help you avoid any other services.

SDS adapter and you can have a rod in the ground in a few seconds with little effort.
 
One question, will the rod be a better bet than the poor TNS earth?
 
Thank you Midwest looking at page 33 is quite useful

on a side note i want to avoid hammering a TT rod through a gas pipe, i have never installed an Earth mat are these a viable option as the property is surrounded by soil/grass

We install mats regularly.

You will still need to dig down about 300mm but you will be able to CAT scan the area accurately.

The reason mats are deemed safer is that most Permit to Digs instruct you to CAT scan every 300mm. You cannot do this when driving an earth rod in.
 

Reply to Converting to a TT system... possibly in the UK Electrical Forum area at ElectriciansForums.net

Similar threads

  • Question
I think there is a little truth in what the guy in the video says, but he makes more out of it than he should. A N-E fault on a circuit protected...
Replies
28
Views
2K
  • Question
much more information required. Is the supply to the first building a DNO supply or a sub main cable from another building ? if it is a sub main...
Replies
5
Views
885

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top