Hi,

Ok, let me know what your thoughts are as to MCB size, cable size of cable from cooker to wall, nothing more, just let me know, then ill tell you what I have just found.

The cooker uses 10.4kW to 11.6kW, its free standing, 4 rings and double oven, new oven, well bought it off someone, but still has all labels on it etc, looks like its been used once. So lets just say on christmas day when you have stuff warning in the top oven, turkey in the bottom, and all 4 rings on boiling potatoes etc, the point is, it "could" draw 11.6kW.

1. What size MCB
2. What size cable for circuit
3. Size of cable from cooker to outlet.
 
Minimum required MCB = 25A (32A if there is a socket outlet on the ccu)
Minimum required cable size for circuit (installation methods and rating facotrs allowing) = 2.5mm (4mm if there is a socket outlet on the ccu)
Size of cable from cooker to outlet = 2.5mm HR flex

What I would fit:

MCB = 32A
Cable size (other factors allowing) = 6mm
Size of cable from cooker to outlet = 4mm butyl
 
I accept diversity etc and all that, but on Christmas day, its going to pull more, it is, personally I dont think a 32A breaker would hold out. Ill be honest, the woman was bed bound, and there was a fryer next to the over and lots of food, so I would think that the oven will get abused on Christmas day.

Naturally I would have thought it needed a bigger cable, it can draw 50A, 4mm cable is only good for 37A.

The point to the story is, I have not connected it as personally I think it needs a bigger cable and supply, I know what would have happened if I did connect it, the MCB would trip. I know the MCB would protect the flex I put in, but just think, that 32A breaker is going to me maxed out and running hot in my opinion.

Cool me a fool if you like, but you wouldnt connect a 10.5kW shower on 4mm would you.

[ElectriciansForums.net] Cooker Connection[ElectriciansForums.net] Cooker Connection[ElectriciansForums.net] Cooker Connection
 
It won't pull anywhere near 50A on christmas day. It might if all the rings on the hob and both oven compartments and grill were all turned on to max power at exactly the same time, but staggered starting and the fact that it doesn't take much power to maintain heat means that to install anything larger than 6mm is just plain bonkers! Frankly, if you did, you'd be wasting money better spent on other things.
 
Oh dear, well ill let her get someone else in that can do it as im back home now, I just couldn't bring myself to connect it, ill be honest, every cooker I have connected before only used <6kW so was a little, not confused, but made me think, and being mr safety I over engineered my thoughts.

I suppose you can't fault me as such for verging on the side of safety and avoiding problems, just when something tells you it used >10kW my brain switches to think, right 10mm cable.
 
The fact that the connection box has a sticker on asking for 4mm flex does nothing to ease your mind ?

Follow your calcs and you wont go wrong. A 32A supply is what is needed here by my reckoning too, so 4mm or 6mm supply cable depending on installation method.
 
If you are not prepared to listen to the more experienced electricians then why post such thread, you have already made your mind up before hand.

I am listening thanks, just wanted a second opinion as it didn't seem right to me. I know it said 4mm but you should never just believe what a sticker says as it may be wrong, if that sticker had fallen off then I would only have had the power rating of the oven to go on.

anyway, next time I'll just connect it and be done with it. Thanks for clearing this up everyone.
 
as damian stated. all the elements are on stats, so all drawing full power simultaneously is about as rare as you busking outside harrods with your drum.
 
Uksparks don't listen to them they are trying to trick you!! get it on some 16mm twin on a D 63 amp mcb
 

Reply to Cooker Connection in the UK Electrical Forum area at ElectriciansForums.net

Similar threads

  • Question
One thing you may find is that it will most probably be a 6mm cable and to get two of them in to a terminal may prove to be a stumbling block if...
Replies
3
Views
1K
  • Question
Hello oscar21, When I wrote about cables heating up I meant that IF a cable heated up that heat could not dissipate correctly if the cable was...
2
Replies
16
Views
2K

Recommended Sponsor News

Exclusive Forum Offer! Free euro 2024 wall chart for first 10 responses!

Hi everyone,

We have 10 exclusive Uheat EURO 2024 Wallcharts to giveaway for Electricians Forum Members! The first 10 people to reply YES to this thread - I will message and get them sent out to you just in time for this years tournament! GO GO GO

Quickwire Now Sponsor ElectriciansForums.net

I am sure you will join me in welcoming our newest sponsors of ElectriciansForums.net - Quickwire! They have decided to join us after seeing you guys discussing their products here. Now we have an expert on board that you can chat to @Quickwire-Sam who will be happy to answer your queries!

[ElectriciansForums.net] Quickwire Now Sponsor ElectriciansForums.net


@Quickwire-Sam said "At Quickwire, we're all about speed, safety, and reliability. We're a family-run business, and every Quickwire connector is proudly made right here in the UK, ensuring noticeable quality. In short, Quickwire is the fastest connection method on the market. Whether you're an experienced electrician or a DIY enthusiast, Quickwire makes electrical connections ridiculously quick and easy. We're passionate about blending British craftsmanship with innovation. If you have any questions or if there's any way we can help, please just ask me!"

PCBWay Now Sponsor ElectriciansForums.net!!

I hope you will all join me in welcoming our newest sponsor to the forum PCBWay! You can contact their friendly people by sending a message to @PCBWay who will be happy to answer your queries.

Welcome to the community and thanks for your sponsorship!

[ElectriciansForums.net] PCBWay Now Sponsor ElectriciansForums.net!!

PCBWay provides services including PCB Prototype and batch Production, PCB Assembly (SMT), 3D Printing, CNC Machining, PCB Design, Electronics Modules Selling, etc. We are committed to meeting the needs of global makers from different industries in terms of quality, delivery, cost-effectiveness, and any other demanding requests in electronics.

[ElectriciansForums.net] PCBWay Now Sponsor ElectriciansForums.net!!

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top