Joined
Nov 6, 2016
Messages
468
Reaction score
778
Location
Blackpool,Lancashire.
I was called to a house where they said the fuse for the sockets kept blowing.They had kept replacing the fuse until it didn't blow anymore but now the sockets have no power!.

When i arrived to have a look they said another electrician had come out and in order to fix the fault had replaced the consumer unit! The sockets still had no power to them.
Anyway i had a look and found the house to wired in rubber cable.Obviously the blasting had totally destroyed the conductors blowing apart the fault and now was sat there with no power.

I turned my attention to the consumer that the 'electrician'(and i use the term loosely) had fitted.
Heres what i found.
http://i.Upload the image directly to the thread.com/OVG1tOt.jpg

He has used the old cotton covered tails and fed it through an unbushed hole with the red clearly digging into the consumer unit.

Also the main earth cable looked like it was only 2.5mm!
http://i.Upload the image directly to the thread.com/ADKv2od.jpg
No earth bonding to gas or water.
Heres the inside.
http://i.Upload the image directly to the thread.com/ooOlYg2.jpg

Needless to say there was no certificate,no labels,no part 'p' notification etc.

I am gob smacked at the incompetence of this so called electrician.

What do others think?

[ElectriciansForums.net] Cowboy electrician
 
Yes mate a proper metal mitre box, especially made for cutting angles on trunking with a junior hacksaw.
My trunking / tubing cutter just makes straight cuts. I had one with an anvil bed where you change the jaws & could cut angles, but couldn't get on with it.
 
I was called to a house where they said the fuse for the sockets kept blowing.They had kept replacing the fuse until it didn't blow anymore but now the sockets have no power!.

When i arrived to have a look they said another electrician had come out and in order to fix the fault had replaced the consumer unit! The sockets still had no power to them.
Anyway i had a look and found the house to wired in rubber cable.Obviously the blasting had totally destroyed the conductors blowing apart the fault and now was sat there with no power.

I turned my attention to the consumer that the 'electrician'(and i use the term loosely) had fitted.
Heres what i found.
http://i.Upload the image directly to the thread.com/OVG1tOt.jpg

He has used the old cotton covered tails and fed it through an unbushed hole with the red clearly digging into the consumer unit.

Also the main earth cable looked like it was only 2.5mm!
http://i.Upload the image directly to the thread.com/ADKv2od.jpg
No earth bonding to gas or water.
Heres the inside.
http://i.Upload the image directly to the thread.com/ooOlYg2.jpg

Needless to say there was no certificate,no labels,no part 'p' notification etc.

I am gob smacked at the incompetence of this so called electrician.

What do others think?

View attachment 34239
 

Reply to Cowboy electrician in the UK Electrical Forum area at ElectriciansForums.net

Similar threads

L
  • Question
My Understanding is the 6 Months interval is IET Guidance and this wording is incorporated onto the label which is a requirement in 514.12.2 where...
Replies
9
Views
502
You can get surge-protected 13A plugs such as this...
Replies
2
Views
278

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top