Evening all,

Help needed did a Recent CU change, 15th edition install, inaccessible junction boxes on RFC with a FCU down rated to 3 amp feeding a bathroom fan. FCU is inaccessible (I needed to find out if it has been fused down bathroom lino up and floor boards) all tested out ok too.

What I need to understand is this compliant to 17th edition on a CU change. I Know it's not accessible, but is fused accordingly. Rcbo for that circuit could be used as means of isolation of fan if it is noted at the board. Am I right in thinking this?
 
a FCU that is inaccessible is a big no no. find it, drag it out, and make it accessible. who in their right mind would fit a FCU where you can't get to it?
 
Now, if there are issues with an installation that are not considered unsafe, although not to current BS, (unearthed lighting circuits excluded), you ARE NOT generally required to put these right, although they should be noted on the cert in the correct box.
 
It would be a pig of a problem if Terry the tiler comes and tiles the floor and then the fuse blows, no chance of changing it then. I wouldn't say you're responsible as you've only changed the cu but it would be worth telling them it needs moving
 
Evening all,

Help needed did a Recent CU change, 15th edition install, inaccessible junction boxes on RFC with a FCU down rated to 3 amp feeding a bathroom fan. FCU is inaccessible (I needed to find out if it has been fused down bathroom lino up and floor boards) all tested out ok too.

What I need to understand is this compliant to 17th edition on a CU change. I Know it's not accessible, but is fused accordingly. Rcbo for that circuit could be used as means of isolation of fan if it is noted at the board. Am I right in thinking this?

So you've changed the CU, note it on the cert. There are millions of homes in the UK with similar issues.
 
Last edited by a moderator:
Thanks for all your replies, I ask as I had my Assesment Monday just gone and got a Non confirmity for this arrangement. Obviously after further investigation it had been down rated, stupidly but not unsafe. Lesson learnt, more investigation needed before changing the cu.

I shall note on cert Murdoch, thank you.

I really love this site, better than FB. Lol.
 

Reply to Cu change in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

News and Offers from Sponsors

  • Sticky
  • Article
Wicked I've just actually looked through it and it's very smart. Some good stuff in it. There's a tile association company that do a magazine...
Replies
2
Views
281
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
270
  • Article
Hi everyone, Another weekend, another sale! Get ready for colder days with Haverland Radiators, combining efficiency with modern design. Keep...
Replies
0
Views
351

Similar threads

  • Question
In the current book (18th, amendment 2) it is under regs 433.2 and 434.2 In most domestic situations the usual approach is the whole circuit is...
Replies
3
Views
638
S
  • Article
Tile adhesive just not setting Hi all, New to this forum and an amateur DIY'r. Got a problem I'm hoping that someone can help me with as I'm...
Replies
0
Views
72
superfuel
S

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top