Dazzol2009

Hi Guys,
Was called to look at this job today, problem with a tripping dishwasher on hi temp, had a look at the C/U and noticed this arrangement, obviously as you can probably see fairly newish board, but still has ELCB wired pre board, and then an rcd within board, my understanding is most people when updating boards usually bin the ELCB and put a 17th edition board in with rcd protection.
I phoned up my Elecsa tech man, and he would just bin the ELCB and put another rcd in the board, I would welcome any opinions on this.
 

Attachments

  • [ElectriciansForums.net] Current Operated ELCB
    20131108_155718.jpg
    100.4 KB · Views: 153
No, you won't! Only if one of them is a S type (time delayed) will you achieve discrimination. The fact that one is a 30mA and the other is a 100mA makes diddly squat of difference to an earth fault of 700A.

This is why I said the new board that was installed was a waste of space,a useless amount of money spent,all in the name of someone who shouldn't be installing/just interested in making money on the back of incompetence

If it is seen that upgrading is required,then either improvement for the benefit of the customer should be the focus, or the amount of money that can be gained by dealing that customer bullcrap has to be the priority

Do the job right,alter the garbage that was installed and replace the original stand alone RCD with an isolator
 
Last edited:

Reply to Current Operated ELCB in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Sticky
  • Article
Wicked I've just actually looked through it and it's very smart. Some good stuff in it. There's a tile association company that do a magazine...
Replies
2
Views
277
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
269
  • Article
Hi everyone, Another weekend, another sale! Get ready for colder days with Haverland Radiators, combining efficiency with modern design. Keep...
Replies
0
Views
350

Similar threads

  • Question
What is the distance from the point outside the house to the shed?
Replies
8
Views
756
Sockets will probably be ok on one, a little inconvenient in the event of a fault though, I'd probably like a 7th rcbo in. Wonder if hes linked...
Replies
93
Views
7K
suffolkspark
S

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top