What reading do you get if you split the ring and fire connected lives to earth down each leg?
Follow along with the video below to see how to install our site as a web app on your home screen.
Note: This feature may not be available in some browsers.
Discuss Dead short between line and neutral- RFC in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net
Hey, whoa, hang on there a minute. Are you saying that I was right about something?
Thanks for posting back.
Congratulations on your tenacity, great feeling when you sus a problem, IR testing can be a doddle but is a bit like fishing, needs patience and you'v got to love what your doing well done.
Pict,
Thank you for sharing your findings. I will include this in the list of things to check if I get dodgy IR readings. Well done to you!OK. Sorted!
Thank you to all those who have assisted me here. The bottom line is the plug tops (extension leads without neons nor surge protection) still connected but switched off were the problem. I had one on each RFC. I spent an hour taking a cupboard unit down to remove plug tops and an hour putting it back! I could turn them off but could not extract the plug top. On removing the plugs, I get >999 Mohms on each RFC. I do have 560 Mohms on neutral to earth on one but I can live with that! On the whole board, I am still getting low N to E of about 6 Mohms but I suspect I do have some damp somewhere and resistances in parallel etc. Still its quite acceptable.
I am still learning here and am doing so on my own installation. It's the best way IMO. I have learnt so much in the last 24 hours about IR testing and I am grateful to all of you for helping me. Without all the advice, I would still be pulling what little hair I do have, out!
My last problem is an RCD installed. It trips out on half test and ramps at 13mA ! I think I will replace that!!
Regards PP
Reply to Dead short between line and neutral- RFC in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net