What reading do you get if you split the ring and fire connected lives to earth down each leg?
 
I think you have a sockets off all round job here, one RFC at a time both legs out at the CU, and testing as you diconnect each in turn testing "upsteam" of yourself working back to the CU till you get >999 then you know it's "behind you" so to speak maybe your first thought of a "nail" is not so far out,
Pict
 
I once had a poor IR reading between L & N but not exactly 0.00 M Ohms. I opened the sockets one by one, cleaned the muck/dust off, checked for any short and the readings improved considerably. JB's will be a pain to look into especially if they are under floor boards.

Can’t think of anything else other than neons or loads still on the circuit.

PS: check for permanently connected appliances such as cooker hood, lighter unit for the gas cooker and so on.
 
Last edited:
OK. Sorted!

Thank you to all those who have assisted me here. The bottom line is the plug tops (extension leads without neons nor surge protection) still connected but switched off were the problem. I had one on each RFC. I spent an hour taking a cupboard unit down to remove plug tops and an hour putting it back! I could turn them off but could not extract the plug top. On removing the plugs, I get >999 Mohms on each RFC. I do have 560 Mohms on neutral to earth on one but I can live with that! On the whole board, I am still getting low N to E of about 6 Mohms but I suspect I do have some damp somewhere and resistances in parallel etc. Still its quite acceptable.

I am still learning here and am doing so on my own installation. It's the best way IMO. I have learnt so much in the last 24 hours about IR testing and I am grateful to all of you for helping me. Without all the advice, I would still be pulling what little hair I do have, out!

My last problem is an RCD installed. It trips out on half test and ramps at 13mA ! I think I will replace that!!

Regards PP
 
Last edited by a moderator:
Congratulations on your tenacity, great feeling when you sus a problem, IR testing can be a doddle but is a bit like fishing, needs patience and you'v got to love what your doing well done.
Pict,
 
Ok Mods - lock it down lock it down ........

(Seriously I'm only pulling your pencil pusher, well done on sorting it and no offence intended to the loser Pict....) :yesnod:
 
OK. Sorted!

Thank you to all those who have assisted me here. The bottom line is the plug tops (extension leads without neons nor surge protection) still connected but switched off were the problem. I had one on each RFC. I spent an hour taking a cupboard unit down to remove plug tops and an hour putting it back! I could turn them off but could not extract the plug top. On removing the plugs, I get >999 Mohms on each RFC. I do have 560 Mohms on neutral to earth on one but I can live with that! On the whole board, I am still getting low N to E of about 6 Mohms but I suspect I do have some damp somewhere and resistances in parallel etc. Still its quite acceptable.

I am still learning here and am doing so on my own installation. It's the best way IMO. I have learnt so much in the last 24 hours about IR testing and I am grateful to all of you for helping me. Without all the advice, I would still be pulling what little hair I do have, out!

My last problem is an RCD installed. It trips out on half test and ramps at 13mA ! I think I will replace that!!

Regards PP
Thank you for sharing your findings. I will include this in the list of things to check if I get dodgy IR readings. Well done to you!
 

Reply to Dead short between line and neutral- RFC in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
299
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
808
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
855

Similar threads

Yup will do exactly that when I'm back down there. Thanks for the help
Replies
6
Views
378
A picture paints a thousand words so here's an SLD showing my installation and some annotations to show the proposed relocation of the DC...
Replies
12
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top