Are you creating a TT system at the garage and workshop? You can get insulated swa glands so you could still terminate straight in to the cu.
What's the issue?
I was under the impression it's perfectly acceptable to use the supply earth where extraneous metal parts don't exist in the out buildingThe issue is normally electricians who lack the knowledge to design a safe and compliant installation
that's correct, but if the supply is PME with extraneous parts in the outbuilding, then the supply cable's cpc must be no less than 10mm to comply as a bonding conductor. ( or a separate 10mm bonding conductor may be used.).I was under the impression it's perfectly acceptable to use the supply earth where extraneous metal parts don't exist in the out building
that's correct, but if the supply is PME with extraneous parts in the outbuilding, then the supply cable's cpc must be no less than 10mm to comply as a bonding conductor. ( or a separate 10mm bonding conductor may be used.).
Yeah, it mentions all this in an ECS guide Tel, I think it's a good few years old now but still valid hence why it hasn't been updated. The 10mm bonding you mentioned in TN-C-S systems might also be accomplished by rodding the outbuilding according to the guide, but I always thought of TTing an install as a last resort rather than a go to.
Where can you get insulated SWA glands from?
Are you creating a TT system at the garage and workshop? You can get insulated swa glands so you could still terminate straight in to the cu.
Look up, CMP products.com
I was under the impression it's perfectly acceptable to use the supply earth where extraneous metal parts don't exist in the out building