Hi All,
We have a problem on an installation that is getting worse and I haven't any joy with the supplier.
The system is 16 x Sanyo HIT250, South facing 30 degree (ground mount) zero shading. The system was installed in May this year and worked very well for the first month. Then it started to drop out once or twice a day from midday to 3pm. Now it starts dropping out at about 10am to 4pm and can be over 100times a day.
When I talked to Deihl Germany and gave the fault code they said high grid voltage is the problem. So DNO in to monitor the voltage. One week later and this proved not to be the case and voltage is within guide lines. So back to site and checked resistance and voltage again.
The array is 52mts from the sub main. Underground cable in duct. 10mm 3c SWA. The sub main is wired back to incoming supply 10mm T&E and 6mm T&E. No load on this submain as is now only doing PV system. Possible length of this is 40mts.
When the PV kicks in the AC voltage goes high to 255-257 before dropping out.
We have swapped the inverter for the same model but again it happens on this also so swapped it back again.
We are now looking to install as a temporary trial a 10mm T&E direct off the incomer to the inverter a length of approximately 70mts straight line. Just to see if this helps.
The supply to the property is TNCS and all the incomer is good etc. Tested well and under 0.35 Ze
Anyone any other ideas or things to try.
Thanks
Mark C
We have a problem on an installation that is getting worse and I haven't any joy with the supplier.
The system is 16 x Sanyo HIT250, South facing 30 degree (ground mount) zero shading. The system was installed in May this year and worked very well for the first month. Then it started to drop out once or twice a day from midday to 3pm. Now it starts dropping out at about 10am to 4pm and can be over 100times a day.
When I talked to Deihl Germany and gave the fault code they said high grid voltage is the problem. So DNO in to monitor the voltage. One week later and this proved not to be the case and voltage is within guide lines. So back to site and checked resistance and voltage again.
The array is 52mts from the sub main. Underground cable in duct. 10mm 3c SWA. The sub main is wired back to incoming supply 10mm T&E and 6mm T&E. No load on this submain as is now only doing PV system. Possible length of this is 40mts.
When the PV kicks in the AC voltage goes high to 255-257 before dropping out.
We have swapped the inverter for the same model but again it happens on this also so swapped it back again.
We are now looking to install as a temporary trial a 10mm T&E direct off the incomer to the inverter a length of approximately 70mts straight line. Just to see if this helps.
The supply to the property is TNCS and all the incomer is good etc. Tested well and under 0.35 Ze
Anyone any other ideas or things to try.