First Post on here but I need some advice so bare with please!
So I recently got called to a job from a customer who had their consumer unit changed by an "electrician" who fitted a split load rcd board. When the rcds repeatedly tripped he walked away from the job on nothing but MCB and main switch removing both rcds.
I've done plenty of testing on the board today and there are numerous faults and poor readings, such as low L-E IR readings (about 0.4mohms) as well as open end readings on cpc for ring final circuits. Also low N-E IR readings (again about 0.4mohms).
So I explained the scenario to the customer... Who has now told me he doesn't want me to rectify these faults or complete any fault finding as it will cause too much disruption to his house. Testing asides, I've done no work in this house and won't be especially whilst its in the state its in. But asides from just walking away is there anything I can do here to force the situation here slightly?
It really doesn't sit well with me having seen the state of the installation as well as the cr@p test results I got when testing through the board.
However if the customer won't let me continue... Am I at all liable here? And if so what can I do to cover my behind as I've stressed my concerns to the customer and I got nowhere!

Thanks in advance!
 

Reply to Difficult customer! Refusing to allow me to rectify faults. in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
291
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
800
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
831

Similar threads

  • Question
There could also be a completely unsuitable junction box embedded within the wall and tiled over or just cables in choc blocks in old accessory...
Replies
6
Views
981
  • Question
This is a baffling fault I've been fighting with for a couple of weeks now, so I wondered if another set of eyes will help. I installed an EV...
Replies
0
Views
182

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top