danny124
I done some calculations regarding diversity for max load and also determine my main switch rating for my board....
can someone tell me if i done my calculations right... i have trouble getting my head round this, got my ELECSA assessment coming up, want to make sure im not getting things wrong. Feels like my brain has gone to marmalade...
Supply to workshop will be 16mm 3 core buried, worked out the Current Carru Cap, and Volt drop already....
Circuits needed: 4 Sockets 32amp
2 Florescent Lights 6amp
1 Possible Circuit in future for Planer machine. 32amp
Max demand Load
& Diversity
(With future Circuit):
Onsite Guide Calculations
Possible Planer Circuit 32amp = 32amps
Ring Circuit 40% (32/100x40) = 12.8amps
4ft Florescent Lights (x2)… Likely be 36w each.
72/230 = 0.31amps
66 % of 0.31 amps = 0.20amps
TotalDemand = 45amps
Rule Of Thumbs Calcaulation
Largest Circuit (Planer) = 32amps
40% of Lighting and Ring Circuit = 15.2amps
Total Demand = 47.2amp
Cheers guys....
can someone tell me if i done my calculations right... i have trouble getting my head round this, got my ELECSA assessment coming up, want to make sure im not getting things wrong. Feels like my brain has gone to marmalade...
Supply to workshop will be 16mm 3 core buried, worked out the Current Carru Cap, and Volt drop already....
Circuits needed: 4 Sockets 32amp
2 Florescent Lights 6amp
1 Possible Circuit in future for Planer machine. 32amp
Max demand Load
& Diversity
(With future Circuit):
Onsite Guide Calculations
Possible Planer Circuit 32amp = 32amps
Ring Circuit 40% (32/100x40) = 12.8amps
4ft Florescent Lights (x2)… Likely be 36w each.
72/230 = 0.31amps
66 % of 0.31 amps = 0.20amps
TotalDemand = 45amps
Rule Of Thumbs Calcaulation
Largest Circuit (Planer) = 32amps
40% of Lighting and Ring Circuit = 15.2amps
Total Demand = 47.2amp
Cheers guys....