D

danny124

I done some calculations regarding diversity for max load and also determine my main switch rating for my board....

can someone tell me if i done my calculations right... i have trouble getting my head round this, got my ELECSA assessment coming up, want to make sure im not getting things wrong. Feels like my brain has gone to marmalade...

Supply to workshop will be 16mm 3 core buried, worked out the Current Carru Cap, and Volt drop already....


Circuits needed: 4 Sockets 32amp
2 Florescent Lights 6amp
1 Possible Circuit in future for Planer machine. 32amp


Max demand Load
& Diversity
(With future Circuit):

Onsite Guide Calculations
Possible Planer Circuit 32amp = 32amps
Ring Circuit 40% (32/100x40) = 12.8amps
4ft Florescent Lights (x2)… Likely be 36w each.
72/230 = 0.31amps
66 % of 0.31 amps = 0.20amps

TotalDemand = 45amps


Rule Of Thumbs Calcaulation

Largest Circuit (Planer) = 32amps
40% of Lighting and Ring Circuit = 15.2amps

Total Demand = 47.2amp



Cheers guys....
 
remember that flourescent fittings have a power factor of 1.85 so factor that into your total design current. you need to do it for cable calcs as well.
 
hey scotsparky

Thanks for your reply, and thank you for heads up

Apart from all that, does everything else looks ok to you

Cheers
 
is ther only 1 socket circuit?
If its a workshop then it may be classed as commertial which will affect your lighting demand so go for 100% lighting and 50& sockets.
 
hi mate, its just a little hobby workshop for my grandad, he was a joiner so like to keep himself busy by making things for the house...

basically its.....

ring with 4 double sockets
(possible) radial for the planer but its not likely. (but wanting to add this into calculations just in case
2 florescent IP(protection against sawdust mainly) rated lights for lighting.

With regards to my main switch which for the SWA cable suppling shed. Was going to make it 40amp. Its got a 40amp at moment. But Max demand is about 47amps so was going to go with the 60amp option.

And main switch RCD, on CU in shed, does this also have to be 40. someone told me today it may have to be, but i dont think this guy is right?

What you think.

Have i got a few things wrong here.

Just worring about my assessment, and all the simple things im forgeting...

Thanks for your reply again Sir
 
In>Ib i remember somekinda calc like this , cant really remember it though, but surley if max demand is 47A then the overcurrent protection needs to be 50A?

50A switchfuse, armoured to workshop DB, 63A 30mA main switch and then your breakers, or just a 63A main switch and RCBO's to allow for division of installation BRB pge 39
 
In>Ib i remember somekinda calc like this , cant really remember it though, but surley if max demand is 47A then the overcurrent protection needs to be 50A?

50A switchfuse, armoured to workshop DB, 63A 30mA main switch and then your breakers, or just a 63A main switch and RCBO's to allow for division of installation BRB pge 39
 
jase as its the min switch that is 40 A then the final circuits are seperate MCBs its ok because its backfused. as long as the small busbar in the D.B is covered.
Backfusing is how you get away with taking 25mm tails from 400A busbars to local isolators. remember ithe 3meter rule though.

the formula you remember is Ib>In>Iz
Ib= design current
In = overcurrent rating
Iz = current carrying capacity of cable.
 
Last edited:
"the formula you remember is Ib>In>Iz "
__________________


The 'greater than' symbols should be the other way in the calc Ib<In<Iz (and to be very pedantic should be "less than or equal to"' but I can't find the symbol for that on my keyboard either)


(I now remember it as < looks a bit like an L as in 'Less than')
 
jase as its the min switch that is 40 A then the final circuits are seperate MCBs its ok because its backfused. as long as the small busbar in the D.B is covered.
Backfusing is how you get away with taking 25mm tails from 400A busbars to local isolators. remember ithe 3meter rule though.

the formula you remember is Ib>In>Iz
Ib= design current
In = overcurrent rating
Iz = current carrying capacity of cable.


Backfused?
 
backfufusing means that the supply cable is protected by the upstream device. I cant remember the reg of the top of my head and regs are in van which is in garage after a dopy woman hit me.

basically as the load is protected by an overcurrent device. then supply cable to that overcurrent device if under 3 meters is also protected as long as it is capable of carrying the maxumum load of the device. So if load exeeds protective device rating the device trips thus disconnecting load to supply cable.

It means that on a big busbar chamber then the supplys to the local isolators dont have to be able to take the maximum demand of the busbars.
 
Thinks me got it, so main switch on workshop DB only has to cover max demand of installation, and switchfuse of the submain just has to be big enough to cover the current the submain is carrying,
 

Reply to Diversity and max load in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
361
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
918
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

Thanks little spark. Good point but the drivers I'm considering have a sync and communication between driver function. So (as long as it works)...
Replies
6
Views
595
  • Question
There's a church in a town near me that has solved the heating problem for most days by building what is essentially a large timber and glass...
2
Replies
27
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top