OK I'm not very experienced, waiting to register as Competent Person, but I came across this this morning. I was meant to replace some light fittings in the house, and on checking the main earthing and bonding first, this is what I saw, i.e. no main earth conductor only a strange 6mm 6242Y in the earth terminal going to godknowswhere (down under the floor and towards the back of the house), certainly not to the head or supply sheathing. I thought it might be a DIY TT effort but couldn't find the other end of the 6242Y. Bonding was in 6mm from the gas, and water bonding 6mm connected to the gas BS951 clamp. He wasn't happy when I said I wouldn't do the job. I recommended he gets a PIR done to start with, especially as he intends to rent the place out. Ze came out at 707ohms, PFC as less than 1A.