I'm not blind, but maybe you could post the correct "maximum length" for metre tails. (After all, I only said I think the maximum is 3 metres as I was not sure.)

There is no maximum length in Bs 7671...but the DNO usually specify a maximum length without an isolator. This varies from 2.5m-5m....check with your DNO.
And it's got nothing to do with mechanical protection.
 
On further inspection, I found that the incoming tails are 16mm and the main earthing conductor is 6mm.

I am going to use the idea of installing a 60a switch fuse which will allow me to continue using the existing tails.

However, is 6mm not a bit small for the main earthing conductor, especially when I will bond gas and water with 10mm?

So my idea is to install a 60a switch fuse, upgrade the main earthing conductor to 10mm and leave existing tails. Then bond water and gas in 10mm. Thoughts?
 
Last edited by a moderator:
Depends on the installation and earthing method.

You will have to work out the necessary csa for earthing and bonding.

By adibiatic equation?

Those calculations always show a lot less than you would actually use.

Surely its acceptable to just upgrade main earth and bonding if 16mm tails are protected by 60a fuse
 
That could be because you actually use a lot more than you actually need.


A lot would agree with you but I don't follow your logic.


The reason for not wanting to replace the tails is that it will be a nightmare as the meter is in a communal hallway. Also the run is about 6 meters so will cost a fortune on cable.
 
That could be because you actually use a lot more than you actually need.


A lot would agree with you but I don't follow your logic.


The reason for not wanting to replace the tails is that it will be a nightmare as the meter is in a communal hallway. Also the run is about 6 meters so will cost a fortune on cable.

But it's not you paying? I don't think cable of that length will cost a fortune, but how big is your fortune?
 
But it's not you paying? I don't think cable of that length will cost a fortune, but how big is your fortune?

The person I'm doing it for does not want to fork out money if its not required. Times are tough.

It will cost approx ÂŁ50 just for the cable.

25mm tails are ÂŁ3 a meter and I need 6 metres of each + 16mm earth.
 
The person I'm doing it for does not want to fork out money if its not required. Times are tough.

It will cost approx ÂŁ50 just for the cable.

25mm tails are ÂŁ3 a meter and I need 6 metres of each + 16mm earth.
I'm afraid these are the type of jobs I walk away from then. If a customer doesn't want it done properly. Pay cheap, pay twice.
At ÂŁ3 per metre for tails, I'd change your wholesaler, and a 100m of 16mm earth is far less than ÂŁ1 per metre
 
16mm tails will happily carry 90A if ref. method C. even more if ref. F, although the osg does not quote a figure for this. if they show no signs of damage, leave 'em be. note on your cert. though that you recommend upgrading to 25mm.
 

Reply to Do tails HAVE to be upgraded? in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
463
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
1K
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
2K

Similar threads

This was posted this week, on topic ....... https://niceic.com/newsletter/omission-of-overload-protection/?dm_i=7G1W,7GCE,K4L2A,WHET,1
Replies
8
Views
744
Ah my mistake - apologies. I have something more or less like this wylex unit and the flappy plastic cover has got a broken pin so won't stay one...
Replies
4
Views
285

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top