You can’t run a 2.5mm spur from a 32A 6mm shower.

Not matter what the Zs is. The cable is only rated at max 27A.

So unless you ran it in 6mm, which would be some effort for a 2g socket 😂 then it’s not going to be compliant.

Ah you never said it was in 2.5mm
 
You can’t run a 2.5mm spur from a 32A 6mm shower.

Not matter what the Zs is. The cable is only rated at max 27A.

So unless you ran it in 6mm, which would be some effort for a 2g socket 😂 then it’s not going to be compliant.

That is exactly what my head said at first too.
But....
Overload protection - each appliance and supply cable protected by 13A fuse in plug. OK, two at once would be a bit interesting but unlikely.
(In some circumstances overload protection is allowed downstream - I'd need to read that bit again to comment further.)
Fault protection - it's RCD protected.

It's a truly horrible design but is it actually non-compliant?
 
That is exactly what my head said at first too.
But....
Overload protection - each appliance protected by 13A fuse in plug. OK, two at once would be a bit interesting but unlikely.
(In some circumstances overload protection is allowed downstream - I'd need to read that bit again to comment further.)
Fault protection - it's RCD protected.

It's a truly horrible design but is it actually non-compliant?

What about shower running at same time as someone has plugged a heater in?
 
What about shower running at same time as someone has plugged a heater in?
The breaker and 1st leg of 6mm to shower are correctly matched, so any overload here is dealt with normally by 32A breaker tripping.
Don't get me wrong, I hate it! But I can't immediately see it is unsafe.
 
Im just thinking, if the shower and heater together were above the MCB rating, but not enough to trip it. Just thinking out loud.
As a B32 wouldn't trip at all with a load of ~46 amps, the question is how hot does the 6mm get for the duration of the shower.
It would trip after roughly 15 minutes with a 50A load.
We need someone to plug an EV into the other side of the socket!
But as far as I’m aware a shower has to be a dedicated circuit and nothing else on it.
I agree that angle needs exploring, what requires a dedicated circuit. Appendix 15 comes to mind, but I don't have book here.
 
When I rang NAPIT
Last week NAPIT told me "not to worry" about an RCD taking 0.5 seconds to trip due to a PV system back-feeding and not shutting down very quickly.
There are some good technical people in NAPIT but I find them a bit hit and miss.
 
As a B32 wouldn't trip at all with a load of ~46 amps, the question is how hot does the 6mm get for the duration of the shower.
It would trip after roughly 15 minutes with a 50A load.
We need someone to plug an EV into the other side of the socket!

I agree that angle needs exploring, what requires a dedicated circuit. Appendix 15 comes to mind, but I don't have book here.

I don't think Appendix 15 would cover showers.
 
However, open question to everyone, just what exactly would be wrong with taking a socket outlet off the shower circuit (or anything else such as ufh, or similar); if electrically it had the usual stuff right such as rcd, Zs within limits etc.

General question on people's thoughts about this.
If it is electrically sound then to me the problem it sort of violates the "principle of least surprise" in that you might have a lone socket that is still powered when someone thinks they have isolated the RFC/radials related to that.

Yes, you should never assume and always do your safe isolation tests, but we know that is often missing in any DIY work, etc.

A cooker outlet socket is clearly related to the cooker feed, so no problem there.

The odd radial or conversion from other use has that, but usually there the CU would be labelled with its new use. Yes, you laddie! Stop laughing at the back!!!
 
If NAPIT or any scheme for that matter say it is okay then there is your answer, it probably isn't okay.
I’m not sure you can make a sweeping statement like that.

I’ve not had any issues with NAPIT and always found them to be quite helpful. Even explaining things in detail for me when I ask ‘why’ to help me understand what they’re saying if it’s not immediately obvious.
 

Reply to Dodgy trade pictures for your amusement! - 1 Million Views! in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Hope everyone has had a great Christmas and here’s hoping we all have a better new year coming our way ! Remember our riches aren’t measured by...
    • Friendly
    • Like
Replies
11
Views
578
  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
764
  • Sticky
  • Article
Thanks so much for sharing this with us! I’ll definitely take a look, it seems like there are a lot of useful and interesting products. The idea...
    • Like
Replies
5
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top