Darkwood
You can’t run a 2.5mm spur from a 32A 6mm shower.
Not matter what the Zs is. The cable is only rated at max 27A.
So unless you ran it in 6mm, which would be some effort for a 2g socket 😂 then it’s not going to be compliant.
Ah you never said it was in 2.5mm
That is exactly what my head said at first too.
But....
Overload protection - each appliance and supply cable protected by 13A fuse in plug. OK, two at once would be a bit interesting but unlikely.
(In some circumstances overload protection is allowed downstream - I'd need to read that bit again to comment further.)
Fault protection - it's RCD protected.
It's a truly horrible design but is it actually non-compliant?
But....
Overload protection - each appliance protected by 13A fuse in plug. OK, two at once would be a bit interesting but unlikely.
What about shower running at same time as someone has plugged a heater in?
Im just thinking, if the shower and heater together were above the MCB rating, but not enough to trip it. Just thinking out loud.
As a B32 wouldn't trip at all with a load of ~46 amps, the question is how hot does the 6mm get for the duration of the shower.
It would trip after roughly 15 minutes with a 50A load.
We need someone to plug an EV into the other side of the socket!
But as far as I’m aware a shower has to be a dedicated circuit and nothing else on it.
I agree that angle needs exploring, what requires a dedicated circuit. Appendix 15 comes to mind, but I don't have book here.
I don't think Appendix 15 would cover showers.
However, open question to everyone, just what exactly would be wrong with taking a socket outlet off the shower circuit (or anything else such as ufh, or similar); if electrically it had the usual stuff right such as rcd, Zs within limits etc.
General question on people's thoughts about this.
If it is electrically sound then to me the problem it sort of violates the "principle of least surprise" in that you might have a lone socket that is still powered when someone thinks they have isolated the RFC/radials related to that.
Yes, you should never assume and always do your safe isolation tests, but we know that is often missing in any DIY work, etc.
A cooker outlet socket is clearly related to the cooker feed, so no problem there.
The odd radial or conversion from other use has that, but usually there the CU would be labelled with its new use. Yes, you laddie! Stop laughing at the back!!!
If NAPIT or any scheme for that matter say it is okay then there is your answer, it probably isn't okay.
I’m not sure you can make a sweeping statement like that.
I’ve not had any issues with NAPIT and always found them to be quite helpful. Even explaining things in detail for me when I ask ‘why’ to help me understand what they’re saying if it’s not immediately obvious.
Darkwood,
mainline,
TrueNAS JBOD Storage Server
