Darkwood
Had an emergency call out this morning, a builder who’s installing a drain chopped through the SWA supplying the garden shed. Knocked out half the supply to the street, DNO engineer arrived promptly and changed one of the fuses down the sub station. Circuit isolated and power restored.
In the builder’s defence, the cable wasn’t buried the correct depth and was just beneath the slabs, but you can clearly see where the cable enters the ground so he should have checked prior to cutting.
UPDATE
Just been round to price up repairing this job.
and,
It cost the client an extra days pay with the builder who cut through the cable as he was too traumatised to work for a day…
Bloody builders, You couldn’t make it up.
Is the heavily taped up cpc of the blue/brown T&E disappearing into the ceiling being used as a perm. live/switched live to the fan?
I’ve not untangled it all yet. I’ve got a number of points from this inspection and the list of remedial work keeps growing.
Landlord asked why I was taking light fittings down and sockets off as his last EICR was done in about 30-45 mins and never did any of this, I’ve been here 3hrs so far! 🤔
So I showed him this and said ‘that’s why, along with the fact you have a broken leg of a socket ring somewhere, no earth bond to your gas (meter was moved outside around 2yrs ago he said and it appears it’s never been re-bonded) and there is a socket being spurred off the shower so far. 😂
....and there is a socket being spurred off the shower so far. 😂
Sounds pretty poor.
However, open question to everyone, just what exactly would be wrong with taking a socket outlet off the shower circuit (or anything else such as ufh, or similar); if electrically it had the usual stuff right such as rcd, Zs within limits etc.
General question on people's thoughts about this.
Sounds pretty poor.
It's not unlike a cooker circuit feeding a 13A socket.
Sounds pretty poor.
You can’t run a 2.5mm spur from a 32A 6mm shower.
Not matter what the Zs is. The cable is only rated at max 27A.
So unless you ran it in 6mm, which would be some effort for a 2g socket 😂 then it’s not going to be compliant.
Darkwood,
vjsmarwick,