Octopus

Been at a place today.......... brand new loft conversion.......... so an additional CU has been fitted for the lights and sockets ......................

Thinking specifically about 314.2 :

[ElectriciansForums.net] Does this comply with 314?


I would say that it doesn't............

Opinions please

and more to the point, this conversion probably cost about ÂŁ45k so using RCBO's wouldn't have been noticed................

The last one I saw was where a new single RCD board had been used for the entire house and loft conversion.............. why do people do this?
 
Because your saying that if the RCD trips then the power and lighting circuits will go off in the loft.Going on that principle then when a dual RCD board trips one of its RCD's then 4-5 circuits go off.Obviously this practice is still accepted as being ok otherwise the powers that be will have told us to fit RCBO's to everything as standard.
 
But is it not that you put downstairs lights on the RCD with the upstairs sockets and visa versa. Enabling that if a trip fault occurs on 1 Circuit you still have lighting ability via the sockets in that area coming from the other RCD, which voids the dual RCD argument.
 
I hope thats not your safe isolation Murdoch lol

What I was doing was in the main house - so not my "safe isolation".

FWIW the "other" CU was an older MK - with a 30Ma main switch!

If it was me I would have taken one of the other lighting circuits out of the old board and put it in the new board, then placed the new lighting circuit in the old board!
 
I was taking mick m8 lol im still training and learning.
But agree on the point of rcbo's as it was a new loft conversion so wouldn't of cost much. Im not to keen on the fact if a fault occurs they will loose both circuits in the loft so I would of either separated them or fitted rcbo's
 
OK, I agree that RCBOs all round is 'best' and minimising inconvenience is a good thing. However, I think that the problem of being plunged into darkness is over-stated. Where I am, you're much more likely to have a power cut than an RCD trip. So, if darkness was a major safety issue, we would be installing emergency lighting to all rooms in domestic premises.
 
Because unless you are going to argue that the Regulation requires every circuit to be individually RCD protected then it doesn't hold water. And that certainly isn't what is demanded by BS7671. Minimising inconvenience is a matter for a risk assessment - nowhere is it suggested that all possible inconvenience must be eradicated. So whilst you are entitled to your own interpretation of the Regulation I wouldn't agree with such an interpretation. If that's what JPEL/64 had wanted then presumably that's what they would have written.
 

Reply to Does this comply with 314? in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
381
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
961
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

  • Question
What I find a little bit interesting is that there was an era of MFT's e.g. Robin, early Kewtech that tried to do non-trip loop tests using D-Lok...
Replies
5
Views
1K
  • Question
If it's buried ducting, have you thought about digging up a section of the buried cable close by, cutting it and pulling in a few extra meters...
Replies
6
Views
817

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top