The water pipes enter the house in metal, then there are a few cm's of copper after the stop cock and then plastic. It is hidden behind the kitchen draws (which can be removed to access).

Does this require Main Bonding? The stop cock tests as 0.36Ω to earth, it is TNCS.

I just cant see how fitting a Main Bonding cable achieves anything in this case?
 
I would say no based on niceic advice at tech talk, but I wasn't sure about that advice as the water in the copper and plastic pipes is conductive so a path to earth can penetrate.

Before anyone says anything I know pure water isn't conductive.
 
Having just watched John Ward again
I realise it does need bonding (along with what SL said above). There is the possibility (although ridiculously small) of being in contact with the stop cock and an exposed conductive part at the same time.
 
The water pipes enter the house in metal, then there are a few cm's of copper after the stop cock and then plastic. It is hidden behind the kitchen draws (which can be removed to access).

Does this require Main Bonding? The stop cock tests as 0.36Ω to earth, it is TNCS.

I just cant see how fitting a Main Bonding cable achieves anything in this case?
DRAWER mate
 
Your own test has determined that the incoming pipe is extraneous so needs bonding as per BS7671:2018.

Whether or not it does anything or not is a mute point as BS7671 does not give much wriggle room. Is it extraneous? Yes. Is there an insulating section at the incoming point to the property? No. So it requires bonding whether we like it or not. There is nothing in BS7671 that states the main incoming water pipe needs to be accessible - 544.1.2.
 

Reply to Does this require Main Bonding? in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
As the holiday season approaches, PCBWay is thrilled to announce their Christmas & New Year Promotions! Whether you’re an engineer or an...
Replies
0
Views
541
  • Article
Bloody Hell! Wishing you a speedy recovery and hope (if) anyone else involved is ok. Ivan
    • Friendly
    • Like
Replies
13
Views
988
  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
918

Similar threads

  • Question
Any metalwork connected to the MET could rise in voltage compared to true earth under an open supply neutral fault (on TN-C-S), and that would...
2
Replies
24
Views
2K
  • Question
4-5 hours for 150? no chance, this is 2024, 150 for 2 hours maybe, that said an hour seems pretty quick, not sure he did the job right
2
Replies
23
Views
3K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top