The regs cannot possibly show every possible circuit. I presume you would class any lollipop ring you come across as unsatisfactory then?
So you make your own up!
Follow along with the video below to see how to install our site as a web app on your home screen.
Note: This feature may not be available in some browsers.
Discuss Does this setup contravene any regs or is it ok? in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net
The regs cannot possibly show every possible circuit. I presume you would class any lollipop ring you come across as unsatisfactory then?
If course! A C3 if I were doing an EICR.
And how can it be a lollipop and also a ring? What would you put under the continuity tests in an EIC?
The Appendix 15 argument.
Appending 15 is informative only, it doesn't matter how many times people claim it is a regulation, it isn't, it's there in black and white (INFORMATIVE).
All the appendixes are informative with the exception of the appendix 1.
The opening text reads "This appendix sets out options for the design of ring and radial final circuits for household and similar premises in accordance with Regulation 433.1"
It sets out the ‘options’ by indicating what can be done and what is acceptable.
Options... it is not the exhaustive list of possibilities that comply with 433.1, if it were some of what we do everyday would be non-compliant (like a 20A DP switch feeding a single socket for an appliance wired in 2.5/1.5mm cable - complies with 433.1.204 but isn't on the diagram in appendix 15).
Where does it say that it’s not exhaustive?
For a ring circuit to comply with the regulations, it must comply with 433.1.204 which defines the acceptable topology of a ring final circuit purely in terms of cable loading. Thus providing the cables are not overloaded in accordance with 433.1.204, a lollipop or ring final circuit will comply.
Appending 15 is informative only, it doesn't matter how many times people claim it is a regulation, it isn't, it's there in black and white (INFORMATIVE).
The opening text reads "This appendix sets out options for the design of ring and radial final circuits for household and similar premises in accordance with Regulation 433.1"
Options... it is not the exhaustive list of possibilities that comply with 433.1,
If so, explain to me how the example I gave (a 20A DP switch on a ring final supplying a socket outlet in 2.5/1.5mm cable) doesn't comply with the regulations, and I want actual regulation numbers.
you should never have more than two double socket outlets after a fused spur because that's how appendix 15 shows it.... complete and utter nonsense.
I would stake my pliers on it that the vast majority of inspectors from all schemes, will have the same view as the Stroma man. (And me).
I'll add it to the list of questions I have for my inspector, see what he says
And we'll have to agree to disagree.... pint? My round