Does this setup contravene any regs or is it ok? | Page 10 | on ElectriciansForums
Discuss Does this setup contravene any regs or is it ok? in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net
The Appendix 15 argument.
Appending 15 is informative only, it doesn't matter how many times people claim it is a regulation, it isn't, it's there in black and white (INFORMATIVE).
All the appendixes are informative with the exception of the appendix 1.
The opening text reads "This appendix sets out options for the design of ring and radial final circuits for household and similar premises in accordance with Regulation 433.1"
It sets out the ‘options’ by indicating what can be done and what is acceptable.
Options... it is not the exhaustive list of possibilities that comply with 433.1, if it were some of what we do everyday would be non-compliant (like a 20A DP switch feeding a single socket for an appliance wired in 2.5/1.5mm cable - complies with 433.1.204 but isn't on the diagram in appendix 15).
Where does it say that it’s not exhaustive?
For a ring circuit to comply with the regulations, it must comply with 433.1.204 which defines the acceptable topology of a ring final circuit purely in terms of cable loading. Thus providing the cables are not overloaded in accordance with 433.1.204, a lollipop or ring final circuit will comply.
I’ve said all through this thread ‘loads accepted’ or ‘loads considered’. Lets drop this part as I have accepted this. My argument is not about this, only the make up of a circuit and where it starts.
I have said on numerous occasions that two or more circuits that are lumped together in a protective device is not necessarily electrically unsafe, but just that it doesn’t comply.
Yes Appendix 15 is informative.
It provides us with information.
It’s not the be all and end all, but there is no logical reason why the information provided should be ignored.
(Except of course when it states a Radial starts and finishes at the DB.)
All the appendixes are INFORMATIVE with the exception of app1.
It sets out the 'options' (something that may be chosen) of how to wire a type of circuit. It does not give 'examples' (one of a number of things or a part of something, an instance serving for illustration). If it could be wired like a lollipop it would have a diagrammatical representation of this too!
Where does it say that?
The regs can't possibly show every possible wiring configuration. And they don't need to - a competent electrician does not need to follow a guide covering every option. wiring installations can still comply with the regs even if they aren't specifically drawn in the book!
Where does it say that... it doesn't, but if you take a step back and look at what you're saying I think you might see your talking nonsense because you're saying that the only possibilities for complying with the regulations when constructing a ring final circuit are shown in appendix 15.
If so, explain to me how the example I gave (a 20A DP switch on a ring final supplying a socket outlet in 2.5/1.5mm cable) doesn't comply with the regulations, and I want actual regulation numbers.
If the only answer you can give me is that it's not shown in appendix 15, then you should only ever use double socket outlets on the main ring because that's how appendix 15 shows it... you should never have more than two double socket outlets after a fused spur because that's how appendix 15 shows it.... complete and utter nonsense.
As for the whole two circuits into one OCPD doesn't comply... I think you're wrong, you're not going to change my mind so we'll have to agree to disagree on that.
I have never said that it doesn't and as such I cannot give reg numbers.
App15 states 'the number of socket-outlets supplied from a fused connection unit is dependant upon the load characteristics, having taken diversity into account'. The regs therefore account for more than one socket after a spur.
you are trying to pin the argument down to individual parts of the circuit and my point has always been the proper way the whole circuit is wired and what is acceptable.
This has been a very interesting thread, more so because there has been no outcome. This will run and run i'm sure.
I would stake my pliers on it that the vast majority of inspectors from all schemes, will have the same view as the Stroma man. (And me):).
Brilliant thread!
I agree that it is NOT unsafe (if everything has been taken into consideration). If so it should comply with the regulations. IMO and many others, it's no different than having one cable in the OCPD going to a junction box supplying the two (technically one) circuits.
Having said that I also agree that it is bad practice and should only be done as a last resort.
I have actually had to do this myself on ONE occasion. I needed a way for my new circuit and there was no way the client was going to pay for a new DB. Luckily one of the circuits only had 6x LED GU10 spots on it in the sales room so I just added it to the other sales room lighting circuit which had 600x600 LED panels on it. All loading, switching etc were taken into consideration and I measured the maximum Zs which was fine.
It definitely wasn't my best job but neither was it unsafe. If the circuit had been designed today (with LEDs) they would have been on the same circuit anyway. It was just an old building which was obviously designed when lighting loads were much higher powered.
*awaits loads of abuse*
:D
You can pick up four spaces by replacing the BS 61008 RCDs and using a mix of breakers and RCBO's as required.
Now leave my granny alone, I love her and Catherine Tate studied her for the portrayal of Nan in the series. She had a mouth that made truck drivers blush.
I thought I’d put my input into this thread to rest but I had ten minutes to spare today and this was still bugging me. So I took the opportunity to call the NICEIC technical helpline about it. I have been resurrected!
Their view is that the regulation, although short on specific detail, as a re a lot of the regulations (as it is simetimes very hard to express the intended rule in writing), does in fact intend that each circuit should be connected to only one OCPD. In view of ‘what is classed as a circuit, I specifically asked about lumping circuits together with the view that they both become one circuit, and the view was that they don’t. The circuit is defined as per the wiring was intended and it should comply with BS7671. They would class this as a non compliance.
I asked, if in the event that I found this whilst doing an EICR, would I flag it and if so what would I flag it as. The view was that it should be recorded as a C3 for definite or a C2 if there was a danger of overload or other problems.
This is the NICEIC technical helpline’s view at the time of calling and there are of course other schemes, none of which are necessarily more competent than the NIC or less. (Thought I’d throw that in for balance).
But in the meantime........
I’m am of course, as always, ready to be humbled!
So, if I have an MCB in the CU (above the front door) that is currently supplying the downstairs lighting circuit and the client would like an exterior light by the front door. There are no spare ways in the board.
In this scenario you're saying you can't take a supply from the downstairs lighting MCB without contravening the regs?
Likewise, customer wants a double socket in his garage. CU is in there.
In this scenario you're saying you can't take a spur from the origin of the ring final supplying the downstairs socket circuit without contravening the regs?
If the answer is yes to either of those, it's laughably stupid I'm afraid and is a means by which the NICEIC are encouraging their members to rip off their clients. Sorry, but there is no other way to put it, it's a money making sham sanctioned by an organisation that is supposed to be protecting the clients of it's members. Absolutely laughable and a down right disgrace.
Did they perchance specify which regulations you would be contravening by indulging in such a travesty of wiring?
Reply to Does this setup contravene any regs or is it ok? in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net
  • Locked
Thread closed.
It does seem to me that there's a capacitively coupled voltage to each set of downlights (on the light side of the switch), and when you put the...