Take a look at the picture below. (you may have to turn your head as i couldn't work out how to rotate it it).
As you can see, the DB has seen better days so i am going to replace it with a nice new one with plenty of ways.

I don't get to involved with domestic work as i really only work with industrial installations and bigger stuff. Few questions you guys hopefully will be able to help me with. I will just add that this is a TT System to this house.

1) How far does does the main intake and DB need to be away from the Gas Meter?(As you can see, it is pretty close)

2) I done a Ze on the existing board and was getting a silly reading! Do i need to be looking at installing a new earth rod? If so where is the best place to put it?

3) Choosing a new DB. I was thinking of getting the usual 2 x RCD split boards. Now do i need an RCD Main Switch to feed the Split board (if that makes sense). and if i do does that main switch ideally need to be 100ma?

or

4) can i put a normal DB in with a 100ma main switch and RCBO's to feed each circuit.

I've been a spark for 14years but only ever work on industrial installations and dont know that much about the domestic side of things these days. There are just a few little question im just not sure about when it comes to some of the regs that are involved in domestic installations.

Cheers Guys


Steve



photo.jpg
 
C'mon Biff, you're smarter than that.

eh ? not talkin to me like a pr*** are you ?

Everyone knows that stability has little to do with the size of the Ra value.

so tell me how you measure ground stability then ?
or do you just rely on earth rod resistance like everyone else ?

So is that a requirement or a suggestion? :D

well its an official suggestion , by the IET.

I'm merely pointing out the common misconception that TT systems need 30mA RCD protection and exposing the misguided link in peoples minds between the phrases 'TT' and '30mA'.

at no point in my posts did i state this.
 
eh ? not talkin to me like a pr*** are you ?

Not taking an obnoxious tone with me are you?



so tell me how you measure ground stability then ?
or do you just rely on earth rod resistance like everyone else ?

Personally, 99% of the time I rely on the Ra alone, hence why I would fit 30mA RCDs 99% of the time. Stability however, if needed can be measured over time taking into account different ground conditions, different seasons etc etc...


well its an official suggestion , by the IET.

Not a requirement then?



at no point in my posts did i state this.

I never said or implied that you did?
 
Last edited:
Oh dear, some just never quite understand the workings of decent or crap TT systems, and the measures needed for it's installations protection!! Stability is ''ONLY'' achievable with depth (the deeper the better) when were talking about driven rods!! Anyone thinking of relying on a single up-front 100 or 300mA RCD on a TT system really does need to think again!!
 
Oh dear, some just never quite understand the workings of decent or crap TT systems, and the measures needed for it's installations protection!! Stability is ''ONLY'' achievable with depth (the deeper the better) when were talking about driven rods!! Anyone thinking of relying on a single up-front 100 or 300mA RCD on a TT system really does need to think again!!

Not quite sure who this is aimed at?

Stability is ''ONLY'' achievable with depth

There are a myriad of factors that come into play that will determine how stable a rod is. Yes, I agree, depth is one of the largest, but it's not the 'ONLY' factor. Whack a 3ft rod in the ground in the middle of the desert, it aint deep at all but it will be pretty darn stable! That's not to say it'd be any good mind.
 
Gentlemen, please keep it civil.........thanks!

and whoever started E54 off on RA values and length of rods is getting a ban!!, you have all been warned do not mention TT systems and exporting PME's infront of him, you know what happens!! :lipsrsealed2:
 
Then why would you highlight something like that, that should be a part of every TT system. So what if there is no regulation in your bible, the same bible advocates a numbty 200Ohm Ra for a TT system!!
Can you not think for yourself, does everything have to have a reg attached for you??

An understanding of a TT system coupled with some commonsense, should tell you an S type upfront RCD is a prudent additional protection to any (dual 30mA RCD protected or otherwise) TT system. As i stated before, your comment on the no requirement of a time delayed RCD should not be taken any notice of at all!!

I have no idea why you have decided to have a 'pop' at me all of a sudden? The last time I looked this forum was still UK based (and not in a country with a dictatorship) and as such I am entitled to express my views and opinions? With that in mind I am perfectly entitled to make the comment that I did?

As the Regs are the minimum that we work to, I would once again ask you to highlight where in the Regs it stipulates that the use of a time delayed RCD is mandatory? Maybe you could do it without such vitriol?

BS7671 does not advocate an Ra of 200 ohms. It merely states that an Ra of 200 ohms COULD be unstable. I think anyone with experience of installing a TT system would know it is a totally undesirable figure to work towards and that it should be as low as possible. And I certainly would not disagree that BS7671 is lacking in its information about TT systems (something I think you have stated in other threads before).

It is admirable that you have such knowledge and passion for TT systems and that members of the forum can benefit from that, but being rude and obnoxious; using deliberate inflammatory language and attacking me is not warranted, or appreciated. If you feel so strongly about matters then why not use that knowledge and direct it towards those that write the Regs? Else if my previous post is, in your opinion so poor/dangerous/(insert your own expression of disdain) - then report it to the moderators.
 
Slight error there mate :)

Not all circuits will need 30mA RCD protection.
Hi D Skelton.
In the context I made my post about the original question I believe the OP will need to use 30mA RCD's/RCBO's. I very much doubt he will get an Ra low enough to achieve disconnection times required. I agree that not all circuits in other types of TT system need 30mA RCD's/RCBO's.

On a general note (and not directed at you D Skelton):

Anyhow, as this thread has turned into the usual slanging match, I'm out.
 
I have no idea why you have decided to have a 'pop' at me all of a sudden? The last time I looked this forum was still UK based (and not in a country with a dictatorship) and as such I am entitled to express my views and opinions? With that in mind I am perfectly entitled to make the comment that I did?

As the Regs are the minimum that we work to, I would once again ask you to highlight where in the Regs it stipulates that the use of a time delayed RCD is mandatory? Maybe you could do it without such vitriol?

BS7671 does not advocate an Ra of 200 ohms. It merely states that an Ra of 200 ohms COULD be unstable. I think anyone with experience of installing a TT system would know it is a totally undesirable figure to work towards and that it should be as low as possible. And I certainly would not disagree that BS7671 is lacking in its information about TT systems (something I think you have stated in other threads before).

It is admirable that you have such knowledge and passion for TT systems and that members of the forum can benefit from that, but being rude and obnoxious; using deliberate inflammatory language and attacking me is not warranted, or appreciated. If you feel so strongly about matters then why not use that knowledge and direct it towards those that write the Regs? Else if my previous post is, in your opinion so poor/dangerous/(insert your own expression of disdain) - then report it to the moderators.

Exactly where is the rude, obnoxious, deliberate inflammatory language?? If i wanted to have a pop at you, you would know all about it!! I didn't, ...but it seems you have read differently!!

You can have your say, and state whatever opinion you want too, the same as i do. but why you would advocate not installing an S type RCD on a domestic TT system, is beyond me, and why i included my remarks!! ....It's that simple!!
 
Last edited by a moderator:
Hi D Skelton.
In the context I made my post about the original question I believe the OP will need to use 30mA RCD's/RCBO's. I very much doubt he will get an Ra low enough to achieve disconnection times required. I agree that not all circuits in other types of TT system need 30mA RCD's/RCBO's.

On a general note (and not directed at you D Skelton):

Anyhow, as this thread has turned into the usual slanging match, I'm out.

Apart from mains and distribution sub-main cables etc, i can't think of a single example where a final circuit on any TT system would not require a 30mA RCD type protection. Nothing else is going to trip that circuit out in the disconnection times required on the occurrence of an earth fault...
 
Apart from mains and distribution sub-main cables etc, i can't think of a single example where a final circuit on any TT system would not require a 30mA RCD type protection. Nothing else is going to trip that circuit out in the disconnection times required on the occurrence of an earth fault...

How about a final circuit with a stable Zs below 200 ohms?
 
Apart from mains and distribution sub-main cables etc, i can't think of a single example where a final circuit on any TT system would not require a 30mA RCD type protection. Nothing else is going to trip that circuit out in the disconnection times required on the occurrence of an earth fault...

No reason why a final circuit not including socket outlets or buried cables could not be protected by a 100ma rcd rather than a 30ma rcd on any TT system.
 
No reason why a final circuit not including socket outlets or buried cables could not be protected by a 100ma rcd rather than a 30ma rcd on any TT system.
no reason at all as long as disconnection times are achieved.
 
That was another question i ment to ask earlier as well but forgot. I have no idea why there is a time clock. Economy 7 does spring into mind but i can't see why they would have it at this property.

Anybody got any ideas??????

They dont have any off peak dedicated system like water heater or storage heaters but they most likely have a split bill and duel rate meter, so if they have a time clock on their water heater or washing machine they can benifit from cheap rate for the times the clock is set to.
 

Reply to Domestic DB in the Domestic Electrician Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
715
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
1K
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
3K

Similar threads

  • Question
Thank you so much for that! When I went to do the Ze at the DB, I tripped the RCD in the CU in the house, I understand that's a hard question...
Replies
2
Views
207
You cant just "avoid" the use of RCD's for nuisance tripping... it will depend on how the cable is routed. (ie buried less than 50mm) What has...
Replies
7
Views
380

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top