As suggested, I use clicks

You must take an earth to the light and just over sleave it or into a terminal block, this is so in the future if class 1 used the earth is there.

Supplier is assuming loop in at d/l which is why they say 1.0mm2, therefor 0.75 flex is fine, you are only running 1 d/l per flex.

So to sumarise,

10a MCB
earth to every D/L, terminate in conector
1.5mm2 t+E to a click connector for every D/L
0.75 3core flex from click conector to each D/L
 
A 10A mcb seems a little excessive for this lighting circut. KLIX are a good thought, but you still have the problem of where the cpc is terminated in the fitting - or ecen if it is on a connector block, is there space inside the enclosure of the fitting ?

You would get away with a two core from JB to light fitting - as long as it isn't to long, but more importantly, the JB pops out the ceiling as easily as the light fitting so you can access all connections.
 
Realise this is off the original question but could some one answer if ur testing a light circuit and they happen to be all GU10 type lights wat sort of test r u meant to do as the actual fitting wont hav an earth unless fitting has metal holder????is it just meant to have a n IR test?
 
Realise this is off the original question but could some one answer if ur testing a light circuit and they happen to be all GU10 type lights wat sort of test r u meant to do as the actual fitting wont hav an earth unless fitting has metal holder????is it just meant to have a n IR test?

Take the readings at the termination where the earth is.
 
Take the 1 or 2 ends of this (depending if its loop in loop out)
[ElectriciansForums.net] Downlighters Earth Question
,
then connect them into some of these
[ElectriciansForums.net] Downlighters Earth Question
,
which I ususally house in one of these
[ElectriciansForums.net] Downlighters Earth Question
,
then from your Wago connectors take a short length of this
[ElectriciansForums.net] Downlighters Earth Question



and terminate it to the downlighter, sometimes, dependant of the downlighter, I may use some of these

[ElectriciansForums.net] Downlighters Earth Question
:D
 

Reply to Downlighters Earth Question in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
284
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
786
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
804

Similar threads

In TN-S systems, you shouldn't isolate the neutral in a 4-pole isolator. Connecting neutrals to a dedicated terminal is acceptable and safe...
Replies
4
Views
638
If the shared neutral is lost ,won`t you be getting 400v across both cottages? 2 phase US style but double the Voltage.
Replies
22
Views
3K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top