Is it good practice with 230v downlights to connect them to pork pie jbs via a flex, or can the 1.5mm twin and earth just loop in and out ? I've always done it the first way, but I was recently questioned why.
Follow along with the video below to see how to install our site as a web app on your home screen.
Note: This feature may not be available in some browsers.
Discuss Downlights in the Australia area at ElectriciansForums.net
Strictly speaking connecting flex and solid core wires in the same terminal..ie-a JB is bad practice,as the flex may not be properly clamped,particularly if not doubled up....also a JB is designed to be fixed,not stuffed through a hole in the ceiling.
The best way is to use a connector designed for the purpose...like one of these.....Click CT101C Flow Connector 16A Plug-in Connector
That said I've done hundreds with JB's and not had a problem.....
Edit...Murdoch beat me to it!
What is a 'pork pie' junction box
Me too!If the box is not fastened you should use joint boxes with cable clamps, there is a regulation that covers this but I can't remember the number off hand. I use the ashley J501 joint boxes for down lights as it has cable grips, plenty of room for cables inside, fits easily through hole in ceiling. Only down side it is a bit more expensive than the pork pie JBs. Hope this helps.